MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Video Scope Inside Dry Valve Satisfy Inspection?

6/8/2026

2 Comments

 
Doing inspections, does looking at the dry valve inside with a camera through, say, a drain (instead of removing the faceplate) and taking pictures satisfy the requirement for the inspections?

Most dry valves
nowadays have automatic resets, and the gaskets on the new faceplates are very, very thin and will not reseal even with the replacement part. FDC inspections also include check valves.

I don’t know why, but when you take the Vic off the check (FDC side), the groove coupling will not seal. So a lot of filing or replacement of the piece must be done. I'm thinking the pipe used was for threading and welding (not recommended for grooving).

Any insight here is appreciated, thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

A Health Hazard for Systems without Backflows?

6/3/2026

7 Comments

 
Are there incidents of actual water health hazards from fire sprinkler systems?

I try to avoid waste. Backflow prevention devices are costly and also make sprinkler systems more expensive by adding friction loss, which can mean larger pipes. The water in most sprinkler systems is the same water as in the domestic system. Yes, the water in a steel pipe sprinkler system will get brown over time, because it picks up iron. Not pretty, but is that iron a health hazard? People buy Iron supplements.

In California the laws are confusing. Health and Safety Code - HSC § 13114.7 states: (b) Automatic fire sprinkler systems described in subdivision (a) shall not require any backflow protection equipment at the service connection other than required by standards for those systems contained in the publication of the National Fire Protection Association entitled “Installation of Sprinkler Systems” (N.F.P.A. Pamphlet No. 13, 1980 edition). and (a) states: (a) For the purposes of this section, the following are definitions of class I and class II systems:

(1) American Water Works Association (A.W.W.A.) Manual No. M-14 class 1—Automatic fire sprinkler systems with direct connection from public water mains only; no pumps, tanks, or reservoirs; no physical connection from other water supplies; no antifreeze or additives of any kind; and all sprinkler drains discharging to the atmosphere or other safe outlets.

(2) American Water Works Association (A.W.W.A.) Manual No. M-14 class 2—Automatic fire sprinkler systems which are the same as class 1, except that booster pumps may be installed in the connections from the street mains.

This makes sense, but unfortunately another section states: 13114.5 The governing body of any city or county may enact ordinances or laws imposing restrictions greater than those imposed by Sections 13113 and 13114. (Added by Stats. 1955, Ch. 1480.) AND many water purveyors, who are not city or county officials simply ignore the law. If you want to use their water, you abide by their demands! No single user wants to take the effort to fight. This can be really expensive, especially when a backflow is imposed on an existing system. The added friction loss can mean the whole system has to be recalculated, and often piping upgraded.

I would like to see the industry help to pass laws to eliminate backflows if they are not accomplishing anything.

Please share any ideas of who and how to help, or any examples if there are actual health issues. Thanks.

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Procedure When No Means of Forward Flow Test?

6/2/2026

9 Comments

 
When Inspectors have an existing sprinkler system without a means to conduct forward flow, what is your process for addressing the test?
​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Will Backflow Dump When Fire Pump Starts?

4/21/2026

6 Comments

 
We have a situation where we need to replace a 40-year-old fire pump where the original RPZ is located downstream of the pump. Our current code requires all BFP's upstream of the pump. We are worried that the RPZ will start dumping every time the pump is started.

Does anyone have experience with this that could lend a recommendation? 

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Run Fire Pump with 5-Year Underground Testing?

2/12/2026

4 Comments

 
For the 5-year Underground and exposed piping flow test NFPA 25 7.3.1 - are you to run the fire pump while recording your static, residual, and GPM's?

Without a fire pump, can I utilize the main drain as long as I can flow enough to have the 10% drop between the static and residual, along with using a pitot or a flow meter at the discharge point of the main drain?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Attic System Pass with Ground-Level Inspection?

1/9/2026

6 Comments

 
Has anyone encountered situations where a dry sprinkler system had incorrect repairs or installations, but still passed inspection because NFPA 25 allows portions of the inspection to be done from ground level—even though the piping is actually located in an attic?

Is this actually acceptable under NFPA 25? What recourse did you have?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Is Easy-Up Canopy, Indoors, NFPA 25 Obstruction?

12/23/2025

12 Comments

 
Would you consider this (Easy Up canopy) an obstruction that can be written up during an NFPA 25 annual inspection?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
12 Comments

Does Manual Standpipe 5-Year Need Fire Dept.?

11/27/2025

4 Comments

 
In a 3-story building with 3 standpipes, one of which is a combination standpipe/riser, and the standpipes are manual wet, with 50 psi.

On a 5-year test, how do I flow 1000 gpm (no pump) at 100 psi?

Do I involve the fire department?

The old hydraulic plates showed 70-50 at 260 flow. Three years later, they are showing 50-40 at 320 flow.

So I cannot pass this, even though the water supply has diminished.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe

4 Comments

Use Bench-Testing for Pressure Reducing FHVs?

11/5/2025

4 Comments

 
Does anyone have experience with bench testing pressure-reducing FHV's?

We have horizontal corridors in a hospital, and having a fire hose and flow noise/water in certain areas is not an option.

NFPA 25 2020 Edition, A.13.5.2.2 allows bench testing (i.e.
 remove the FHV, take it outside to conduct the 5-year test).

Has anyone performed this? What is the procedure, and did the AHJ find it acceptable?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Acceptance Test Req'd for Replaced Controller?

10/10/2025

8 Comments

 
When a new fire pump controller is installed or replaced, is an acceptance test required?

I suppose I know the answer, but I am looking for a code basis. Thank you.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Where to Discharge a Sub-Grade Express Drain?

10/8/2025

7 Comments

 
In sub-grade parking garages, with PRV fire hose valves/floor controls - for testing purposes, would you connect a PRV fire hose valve to the express drain via hose and pump vertically to get to the exterior grade to discharge?

Are there any issues with this method during testing to consider?

PRV floor control would be hard piped to the express drain and utilize the same pathway to the exterior. Then at the bottom of the express drain has a ball valve, acting as an auxiliary drain only. It can discharge to a gravity drain system, whether storm or sanitary, whatever your local AHJ permits.

Or is everyone trying to discharge into a gravity drain at the bottom of the stairs and hoping to not flood anything?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
7 Comments

Does Bulb vs Link Matter for NFPA 25 Testing?

9/2/2025

6 Comments

 
NFPA 25 (2020) notes that standard response sprinklers are to be tested or replaced after 50 years in service, and quick response sprinklers after 20 years in service.

An
issue arose regarding standard response 5mm glass bulb recess sprinklers installed / manufactured in 1990. The heads are RASCO Model F156. The data sheets note standard response.

My understanding is that these sprinklers, being standard response, should have a 15-year service life before testing.

Others in the trade have different opinions (including a manufacturer rep) due to the operating element being a glass bulb.

Prior to contacting the manufacturer, I'd appreciate the
forum's thoughts on whether the glass bulb or the ​fusible link is a determining factor in the required time for sprinkler testing.

Thanks!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

How to Dispose Non-Fluorinated Foam After Test?

8/12/2025

5 Comments

 
How do you dispose of foam after the test (non-fluorinated)?

​No one seems to know what to do with it. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

What is the Existing System's Design Criteria?

8/7/2025

6 Comments

 
This is a backflow preventer retrofit project where I'm trying to figure out what the system's original design criteria was.

I am working with an existing 7,300 sf warehouse area within a larger building, which includes offices and a workshop. It is a marine operation, and the products stored are primarily spare boat parts, propellers, shafts, brackets, housings... large metal objects stored in wood crates or cardboard boxes.

I have determined this to be Class II Commodities, stored no higher than 20'.

I am thinking that, based on NFPA 13-2019, Table 21.4.1.2 and Figure 21.4.1.2(b) curve B, I need a density of 0.3725 gpm/sf over a 2,000 sf area. I would also be required to have a maximum protection area of 100 sf based on Table 10.2.4.2.1(d).

Here's where it gets tricky - the branches are spaced roughly 15' apart, and heads are spaced 8' or more along the branch line. Some are as far apart as 11'-6". The heads are K8.0 solder-type. Because of the K-rating, this shouldn't be a pipe schedule system.

Is anyone aware of an alternative storage protection method that this system may be designed to?

The installation date is 1986. ​Any thoughts would be greatly appreciated. I do not know what density I should be applying to this area in my calculations. Thank you very much!

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Different CPVC Manufacturers for Same System?

7/30/2025

5 Comments

 
Can one type of CPVC (FlameGuard) be connected to an existing but different CPVC manufacturer (BlazeMaster), or vice versa?

Are the solvent cements compatible?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Cause of Major Sprinkler Corrosion in Warehouse?

7/29/2025

12 Comments

 
Looking for education on the cause of major sprinkler corrosion in a warehouse.

A general warehouse with ESFR heads has a serious corrosion problem on approximately 600 sprinklers, with two inadvertent actuations occurring in the past 6 months. The image is of the worst corroded sprinkler. Others are more lightly corroded, each with a green hue.

The actuated heads were sent to UL for evaluation as well as non-fused corroded heads. Tests indicated the heads functioned within normal range, with one head slightly delayed. The manufacturer confirmed the heads are not counterfeit.
Picture
The conditions within the warehouse were unique for approximately 7 years, with very high internal temperatures occurring during the winter months, using once-through heating to ensure forklift exhaust CO ppm levels were kept low.

In addition to elevated temperatures, the warehouse received insect fogging applications as normal practice for stored seed and beans. Fogging has also occurred at other similar warehouses, and no problems have been observed at those locations.

Corrosion is on approximately 15% of all sprinklers in the warehouse building area.

Are there similar experiences with corrosion that is similar to the image?

If so, what was determined to be the primary cause? Heat, chemical, or something else?

All of the corroded sprinklers were replaced with new heads and NFPA guidance was observed for temperature selection near forced air heaters.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

Capped Tee Acceptable for Forward Flow? PRVs?

7/22/2025

8 Comments

 
Recently we encountered a system where the floor control valve assemblies (FCVAs) have pressure reducing valves (PRVs) that are due for their 5-year full-flow testing.

Typically, we would conduct this through a hose valve downstream of the PRV (hooked up to the Drain Riser), but this arrangement does not allow for that. The only means of connecting the FCVA to the Drain Riser would be to shut down the floor, remove the grooved coupling & cap from this tee (clouded in the image below), and then hook up a connection to the Drain Riser. Then, another shutdown would be needed to replace the coupling & cap to return the system to its current configuration.
Picture
When addressing Pressure Reducing Devices, NFPA 13, 2019, 16.9.8.5 states that “Means shall be provided downstream of all pressure reducing valves for flow tests at sprinkler system demand.”

​However, according to NFPA 13 2019, 16.14.5.1, a “means shall be provided” for forward testing of the backflow preventer. This “means”, per 16.14.5.1.1, “shall be serviceable without requiring the owner to modify the system.”

I am unable to find a similar reference that pertains to Pressure Reducing Devices.

Is the capped tee considered “Means” to conduct the testing in this instance, despite requiring 2 shutdowns and “modifications” to the system?

Or is a permanently installed valve required to be considered “Means” to conduct the testing?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

How to Tell Open/Shut for Non-Indicating Valve?

7/9/2025

16 Comments

 
How do I know if these valves are open or closed without using the signage present that says OPEN?

Are these non-indicating valves, or am I missing something? Are these even allowed?

Thanks in advance.

Picture
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments

What is This Sprinkler Pipe Fitting from the 1970s?

7/1/2025

11 Comments

 
I found this fitting from a system installed in the 1970s.

Everyone I work with and I are unfamiliar with it.

Do you recognize it, and does anyone have any technical information available?

It looks like a 2" coupling with a threaded head outlet on the other side. It is a push-connect type fitting. Thanks!
Picture

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Compressor Cycling Repeatedly During Night?

6/6/2025

11 Comments

 
We have a condominium (3 story, 18 units), with an original 20-year-old Gast model 2LAF-12-M200X.

Complaint from the unit sharing an adjacent wall to the sprinkler room. The compressor repeatedly 
turns on and off only during the early morning hours, between 2 and 4 AM.
​
We have monitored and seen nothing but normal activity during the day.

Is this possible?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

"Pipe Schedule System" OK on Hydraulic Placard?

5/30/2025

14 Comments

 
A number of board and care facilities have​ missing hydraulic placards. It's possible they never had them since the sprinkler system was installed before placards were required.

They are now required, and I
wonder if it would be a viable option to survey the system, get pipe diameters and sprinkler counts, and see if they fit within the criteria of the pipe schedule method?

If it does, would there be any issues stating so on the hydraulic placard?

The board and care facilities range from 3 - 16 bedrooms and no more than 2 stories high.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments

Why Flow Switch False Alarm in a Large Facility?

4/16/2025

11 Comments

 
I have a customer who is a large production facility with a 12-inch underground fire loop. There are 14 risers, 2 of which are 4 inch, the rest are 6 inch, with 7 fire hydrants tied in around the exterior.

The issue at hand is that they are getting false alarms on random flow switches. The head scratcher is that the water flows all test fine at around 45-50 seconds. Maintenance is saying that the risers where the alarms happened were cold (indicating water flow) and the other risers were room temperature at the time of activation.

There is a 12-inch double-check backflow preventer at the water entry point.

I'm starting to think
about valve tampering, but I am looking for insight I may not have considered.

​Do you have any tips for what this might be?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Replace Old Sprinklers with Higher K-Factor?

2/12/2025

14 Comments

 
If the fire sprinklers for an entire area or building have to be replaced, such as if they are more than 50 years old, is there any problem or benefit (hydraulically) from increasing the replacement sprinklers to the next higher K-factor (e.g., K5.6 to K8.0 or K8.0 to K11.2), especially for production and storage areas?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments

Use Main Drain for Forward-Flow? What to Test?

2/11/2025

12 Comments

 
Forward Flow Test Confusion... I have an NFPA 13R system built in 2013 that doesn't have any hose connection(s) for forward flow testing. The sprinkler contractor is saying they're unable to conduct the test.

I am attempting to understand the codes around this topic and ran into several questions.

First
, NFPA 25: 2020 NFPA 25 13.7.2.3 states, "Where connections do not permit verification of the forward flow test at the minimum flow rate of system demand, tests shall be conducted at the maximum flow rate possible."

Can someone please explain what this means exactly?

My second question
concerns using the main drain to conduct the forward flow test if it's sized appropriately. A previous Meyer Fire blog post, "Solutions for the Overlooked Forward Flow Test," Option 4, mentioned the 2016 NFPA 13 A8.16.2.4.2, but I cannot find that section in the 2019 version.

Has this method changed somehow?

Can the sprinkler contractor use the main drain as a means to conduct the forward flow test?

If so, what else does the AHJ need to know?

Calcs to prove drain size can flow system demand? Pitot reading?

Thank you for reading and I'd love to find some clarity.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

How Often to Re-Test Loaded Sprinklers?

1/15/2025

10 Comments

 
In NFPA 25-2017 Chapter 5 addresses "Loaded sprinklers." Of course, this has been a "LOADED" question for years and everybody's interruption of what that is whether or not NFPA gives a decent explanation of it.

My question is, we have a customer that we've performed a sprinkler test by removing an X amount of sprinklers and sending it away to a third party lab for testing which samples came back as a pass - but the question has come up asking if sprinklers remain to be loaded the same if not more over the years.

What would be the timeline for re-testing?

Would it follow the 10 year re-test?

Or 5 Year sprinkler testing that NFPA 25 requires for sprinklers in "hazardous" environment areas?

As this plant has over 600 sprinklers and getting up to them and cleaning them every year is not practical, that option is not on the table. See NFPA 25-2017 code for the discussion on it. 

​Thanks for your take.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
<<Previous
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT