Flow Test Reports and the N^1.85 Supply Graph

4/11/2018

 
A few weeks ago I received a call from a sprinkler contractor who needed to provide a water supply graph for a flow test he conducted.

I had a canned sheet I had developed for my own flow tests, but it was a basic graph that showed a curve and didn't match the traditional N^1.85 hydraulic graphs common for water supply curves. Since then I've tinkered and come up with an accurate chart that takes flow test input values, calculates total flow and draws the curve along the N^1.85 chart.

Picture

​The N^1.85 chart is particularly useful for fire suppression systems because the Hazen-Williams formula is based on the relationship that pressure relates to flow to the 1.85th power.

Picture

Take a look at the N1.85 Water Supply Curve tool here and let me know what you think in the comment section below.


Picture
USE THE WATER SUPPLY ANALYSIS TOOL

​When the x-axis, or the hydraulic flow is then scaled to the 1.85th power, hydraulic curves become straight lines which becomes easier to graph and compare. Prior to everyone carrying a computer in their pocket, these graphs were likely much easier to use for summaries and comparisons.

The water supply information is what is provided as part of a two-hydrant flow test. The design input information would be the system demand side and can be used for quick comparisons.

Personally, I only use this setup for flow test reports and water supply comparisons. Fire sprinkler hydraulic calculation software takes care of the graphs and outputs I need after I've completed the hydraulic calculations.

On a side note, I've had several people ask about getting access to all of the tools I've created to use on their own computer with the ability to produce printable output for record keeping. Thanks again to those who asked - these are available now as part of the MeyerFire Toolkit - a collection of all of our quick-hitting tools. The Toolkit is also included as part of MeyerFire University at no additional cost.

Don't get these free weekly articles? Subscribe here.  My goal with creating this website and tools is to support those who want to create great fire protection.
David Reynolds
4/11/2018 09:06:36 am

I am trying to come up with a logarithmic graph form that we can plug in hydrant flow and it plots the curve / with a google map location for the hydrants / forms for fire hydrant insp. (5 year)

John Kallenbach
4/11/2018 12:02:30 pm

I keep getting failed to download chart. Is that just me or are others getting that as well?

Joe Meyer
4/11/2018 04:04:46 pm

Hi John, yes this is not yet available for download. I'll post back here when it is.

Thanks John,

Joe

Gerardo pantoja
4/21/2018 02:57:03 pm

Deseo recibí r información

Daniel
4/11/2018 12:35:37 pm

Thanks for putting this out! I just wanted to confirm that this is a web based tool only (like Ping Fire). My group has been looking to create an excel version for a while but has been running into issues with the N1.85 semi-log scaling. Do you have an excel version available?

Joe Meyer
4/11/2018 04:01:47 pm

Correct, yes this tool is only currently available online similar to Ping Fire.

That being said I'm working on an excel-based downloadable resource with every tool I've created. I hope to have it all ready in the next couple months.

Thanks Daniel!

Brian Harris
4/11/2018 01:42:43 pm

Will this be available for download?

Joe Meyer
4/11/2018 04:03:31 pm

It will be a part of a software package with every tool I've created to date, but I don't have it ready quite yet. Should be posted in the next couple months.

Thanks Brian!

Cindy Gier
4/11/2018 04:05:25 pm

Great tool! We've been working on a KCMO hydrant map with hydrant flow tests -- since the city will no longer give the information out. This form can replace my hand drawn flow test graphs using scanned N1.85 graph paper. Thanks!

John Kallenbach
4/11/2018 04:23:44 pm

The example showed up.. I have a free excel spreadsheet in my group on facebook - non-union fire sprinkler group. Feel free to join.

MICHAEL CHARBONNEAU
4/14/2018 05:58:59 pm

why are flow tests on log graph but fire pump data sheets on regular graph? Since most water flows are from pumps, would they look the same if plotted differently?

Merle Hittle
5/11/2018 09:56:04 am

If I am not mistaken, pump tests not plotted on log graph are actually curves and when plotted on log graph are straight lines like flow tests. I have seen flow test data and pump test data plotted on the same log graph to visually verify boost pressures.

jorge h garcia link
4/23/2018 04:22:33 pm

when you have some calc program for download i'm interested to get one, on the other hand, I use before a software for NFPA 25 pump flow test... very usefull and easy, but unfourtunally does not run on windows 10, jut on XP. Did you Know some software to do that calcs and track the history maintenance.
regards

Jeffrey Wong
4/24/2018 06:20:09 pm

Great tool! Is it possible to change the SI to metric? I'm from that part of the world.

JOE MEYER link
4/26/2018 05:32:25 am

You mean you're from almost any single country on the planet other than the US? We completely missed the boat on metric.

I appreciate the idea, it's in the works and I'll plan to put it up in the next few weeks. Thanks Jeffrey!

John Vergara
5/10/2018 05:21:01 pm

Looks good. Can the units be modified to metric?

JOE MEYER
5/11/2018 06:29:47 am

Yes! The metric version is now available here: https://www.meyerfire.com/blog/fire-suppression-n185-supply-graph-now-in-si

Thanks!

Joe

MEL
5/17/2018 01:25:14 pm

What have all of you been using
to use for hanging from Cold Form Trusses
And for the seismic bracing for Cold Form Shapes

Hanging just the sprinkler pipes?

KEN
7/5/2018 12:21:19 pm

Can you explain in your blog or to me how to adjust for Hydraulic Low gradient. There is nothing on the Web. No one seems to know, and I think my adjustments are too much?
thank you

Edriane Leonard Gabriel
12/20/2018 10:08:57 pm

Hi,

Do you have an example of hydraulic calculation for building construction and space expansion?

I believe that fire protection system design for building construction and expansion are different calculation?

Looking for your fast and positive response.

Thanks.

JOE MEYER
1/5/2019 06:20:10 am

Hi Edraine,

I don't currently have an example calculation - there's some basic starting hydraulic calculations with many of the fire sprinkler hydraulic calculation programs. That being said, each calculation is very specific to the actual design of that system so having an example calculation wouldn't be of any help.

Joe

JUSTIN D STIRLING
1/5/2019 10:32:46 pm

I also have developed my own sheet with a basic graph that shows a curve. Can you provide any guidance on how to adjust the x-axis in Excel to make the N^1.85 chart? Thanks in advance!

Thomas McGrath
1/3/2020 06:51:52 pm

I'm looking for a tutorial explaining how to evaluate hydrant flow tests and manipulate various flow senarios.

Ben Zuerner
8/3/2020 07:55:59 am

never got my access code for the trial

Joe Meyer
8/3/2020 08:01:18 am

Hi Ben,

Sorry the system is giving you trouble. Email me at [email protected] and I'll forward your confirmation email. Thanks!


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT