How to Address Water Hammer with Fire Pump?

11/2/2026

13 Comments

 
Does anyone know if there's a way to determine the water hammer created when a Fire Pump turns on (Hard Start)?

I have an existing facility that's about 60 years old with a lot of buried fire mains serving about 10-15 systems. They are on city water at about 55 psi static, and they want us to install a Diesel Fire Pump. Everything in the facility is Ordinary Hazard Group 2, with no plans to add on or change occupancy down the road.

I've chosen a 1,500 gm diesel fire pump at 49 psi, but the owner is worried about blowing out the underground when the pump kicks on. The churn is 55 psi + the city at static 55 psi + 21% for pump overspeed gives us a maximum of around 133 psi that the pump could ever produce.
Although it's not required, we plan to install a main discharge relief valve. Adding 10 psi more for the jockey pump, we could be up around 143 psi, and the owner is not comfortable with this.

What are some options?

Reduce the pump down to 1,000 GPM, 750 GPM?

Reduce the pump's rated pressure to 35 PSI?

​We would need to adjust the PRV's to relieve at predetermined pressures.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments

Common Fire Pump Header Violate NFPA 20?

10/26/2026

7 Comments

 
What if both main fire pumps discharge into a common header, and the flowmeter/test line is connected to that header?

We had a review comment that the testing arrangement of the pumping system shall be in accordance with NFPA 20 to allow for individual main pump testing without impairing the entire system.

Are we in conflict because of the common header?

​Arrangement attached.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
7 Comments

Double PRV Arrangement for 9-Story Building?

10/14/2026

8 Comments

 
I have a 9-story residential building with 3 levels of parking. The building requires a fire pump. The AHJ limits us to a design pressure of 60 psi regardless of the available water pressure.

In my case, the available pressure is 85 psi static, and I have a 115 psi fire pump with a 134 psi shutoff pressure. Therefore, I need to reduce the pressure to ensure that the system does not exceed 175 psi.

I am planning a double pressure reduction, with the first reducing valve set at 162 psi and the second reducing valve set at 165 psi, with the second valve essentially acting as friction loss only.

Assuming a 5 psi pressure increase per floor, would it be acceptable to supply two basement levels below the pressure-reducing valves and reach 172 psi at those levels?

I have already noticed that PRVs can have up to 10 psi above their set point under static conditions, which would make the pressure exceed the maximum limit of 175 psi. To eliminate this overshoot, I plan to install a 1-inch pressure relief valve set at 165 psi to ensure that the system pressure never exceeds 175 psi. This solution seems ideal, except in the event that the pressure-reducing valve is unable to stabilize the downstream pressure below 165 psi. In that case, both the pressure-reducing valve and the relief valve would remain slightly open, allowing a continuous flow of water. This could cause the jockey pump to start repeatedly in an attempt to maintain system pressure, potentially resulting in premature wear of the pump.

Do you have any advice to help me in my design?

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

FDC Required on Water Storage Tank Near Pump?

9/15/2026

8 Comments

 
Is an FDC required on a water storage tank meant to service a fire pump to a commercial warehouse when there is already an FDC connection on the discharge side of the pump piping?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Actual Rules on Flow Meter for Diesel Fire Pump?

9/11/2026

3 Comments

 
What are the rules when installing a flow meter on a diesel fire pump?

I am seeing recommendations from the manufacturer, such as
5 times the Venturi diameter on the inlet and 2 times the Venturi diameter on the outlet (minimums).

What are the 'hard' rules when it comes to installing a flow meter?

I do not intend to loop it back to the suction side. This is fed from a 10k water tank with a 6-inch tank discharge flange.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Discharge to Tank with Calibrated Nozzle?

9/10/2026

2 Comments

 
Section 5.4 NFPA 20 2019 says that: Fire Pump Test Arrangement. Where the water supply to a fire pump is a tank, a listed flowmeter or a test header discharging back into the tank with a calibrated nozzle(s) arranged for the attachment of a pressure gauge to determine pitot pressure shall be required.

I've never seen this type of test header arrangement before.

We are installing 2 horizontal split-case pumps, each with a flow rate of 1,250 USgpm.

Could you explain how this can be achieved in actuality? 

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Reason for Differences in Flow Test Results?

8/25/2026

13 Comments

 
We are working on a school project that needed a 1,000 gpm fire pump due to three standpipes.

We initially did a hydrant flow test and had a flow of 425 gpm with a static of 55 psi and residual of 50 psi when we started the design
. By the time it went out to bid and the contractor performed their own test,​ they flowed 354 gpm with a static of 55 and a residual of 50.

In the first test, we got 1215 gpm at 20 psi, and 1012 gpm in the second test. They went to turn on the pump and were only getting 368 gpm when the building inlet pressure was at 20 psi.

We re-did the flow test to see what changed so drastically and again got a static of 51 with residual of 46 at 375 gpm, which would give us 1004 gpm at 20 psi.

We have confirmed the two valves between the street and
the building are fully open, and we only have about 50 feet of 8” pipe, so the pressure drop to the building is negligible, especially at 368 gpm.

We are at a loss for what could be causing such a difference in pressure to the building and such a low flow.

​Has anyone ever run into an issue like this or have any suggestions of what else we could check out?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments

Pump & Storage Tank for Sprinklers & Hydrants?

8/6/2026

6 Comments

 
A project we're looking at has a hydrant network that connects to fire sprinkler systems and hydrants. 

What would be the process we'd need to consider for the water supply (fire pump and tank capacities)?

How does the greatest sprinkler system demand (possibly with hose allowance) relate to the hydrant demand? Are they additive? 

Not all buildings could have sprinkler systems in the future, so we're questioning the relationship between sprinklered building system demands and the fire hydrant demand.

Thanks for your input.
​

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Allow Temporary Industrial Pump for Highrise?

7/23/2026

12 Comments

 
I wanted to get your thoughts on temporary fire pumps. We are in warm weather season here in MA, and a building wants to use a temporary fire pump to alleviate a fire detail that is on the building.

If this wasn't a high-rise, I honestly feel more inclined, but being that it is, I am more hesitant.

I wanted to see if others have used them, and if so, what evidence did you bring to AHJs/Fire Depts?

The client shopped around on their own accord and found an industrial end-suction centrifugal pump used for sewage bypass and general construction dewatering, which doesn't seem to be generally used for Fire Protection applications.

Thanks in Advance!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

Should Fire Pump Controller Be NEMA Type 3R?

7/20/2026

6 Comments

 
While NFPA 20 requires a minimum NEMA Type 2 enclosure for fire pump controllers, an alternative view has been expressed that a "NEMA Type 3R" enclosure should be provided where the fire pump room is sprinkler-protected.

The rationale is that activation of the sprinkler system during a fire event may subject the enclosure to water spray similar to rain exposure, for which NEMA Type 3R enclosures are designed to provide protection.

​What is your thought on this?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

How to Connect Two Fire Pumps in Parallel?

5/27/2026

4 Comments

 
I have two sets of fire pumps (electric - diesel), one with a discharge of 1000 gpm and a pressure of 160 psi (11 bar), and the other with a discharge of 750 gpm and a pressure of 115 psi (8 bar).

How are these supposed to be arranged if they're to be connected in parallel?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Is Water Storage Tank Far from Pump a Problem?

5/14/2026

9 Comments

 
Hi, have you encountered cases where the fire pump is more than 100 ft (30 m) away from the water storage tank (underground)?

I know this isn't ideal. What type of pump or setup do you suggest or recommend in this situation?

​Thank you.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Route Diesel Fire Pump Flow Back Into Suction?

5/12/2026

5 Comments

 
I have a DoW project with specifications that require the diesel fire pump flow meter to discharge both into the pump suction and through the test header.

I don't have experience with this setup; in all my previous projects, the diesel fire pump discharged back to the water tank as well as to the test header.

I understand that NFPA 20 allows this arrangement (see attached figure from the 2025 edition), but I'm curious how it works in practice for two main reasons:

1. If we close the tank valve during testing, the pump's suction pipe will receive considerable pressure. Will this repeated pressure adjustment after each test impact the longevity of the soft packing, particularly regarding increased water leakage?

​2. How does a diesel fire pump cool its motor if the heat exchanger water isn't returned to the tank with fresh cool water coming in?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
5 Comments

Water Supply Options for Rural Area with Pond?

5/6/2026

13 Comments

 
I am working on a new building in a rural area that will require sprinkler protection. There is no access to a public water supply, only a 30-100 gpm well on site.

Options for fire suppression water include pumping from a large farm pond 150 feet away or installing
a 15,000-gallon water storage tank with a pump.

Any thoughts on
which option is more feasible and cost-effective​, or any alternatives we're not considering?

This is in a freezing climate. Thank you in advance!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments

Will Backflow Dump When Fire Pump Starts?

4/21/2026

6 Comments

 
We have a situation where we need to replace a 40-year-old fire pump where the original RPZ is located downstream of the pump. Our current code requires all BFP's upstream of the pump. We are worried that the RPZ will start dumping every time the pump is started.

Does anyone have experience with this that could lend a recommendation? 

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

How to Calculate Diesel Fuel Tank Vent Capacity?

4/7/2026

5 Comments

 
I have a plan reviewer requiring calculations (CFH) for a diesel fuel tank because the vent extends further than the UL label is calculated for.

What are the guidelines and how is this calculation performed?

The comment: "
Provide the required emergency vent capacity, in Cubic Feet Per Hour (CFH), for the primary and secondary fuel tank emergency vents. The venting capacity should be indicated on the UL label on fuel tank. The shop drawings don't list the emergency vent capacity. Note: The capacity listed on the UL label is calculated with the vent within 12 inches of the tank body. If the vent is extended above the tank more than 12-inches, additional calculations are required to account for the additional piping and height above the fuel tank. These calculations are required to be computed by a registered engineer."

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Is NFPA 20 10-Diameter Req'mt One Straight Run?

2/23/2026

4 Comments

 
NFPA 20 – Does the 10 pipe diameter suction requirement have to be one continuous straight run?

I’m looking for clarification on the NFPA 20 requirement for 10 pipe diameters of straight pipe on the suction side of a horizontal split‑case fire pump.

NFSA’s Layout Book states: “The length of pipe that needs to be 10 pipe diameters long can be either vertical or horizontal, or some combination of the two, as long as there are no more elbows or tees with a horizontal change in direction in the length of pipe.”

This makes sense—but when I look at NFPA 20’s own figures (specifically the “Right and Wrong Pump Suctions” illustration), one of the “Right” examples shows a 90° elbow dropping directly into a tee located right at the pump suction flange. In that configuration, there is no 10‑diameter straight run at all. My questions: Where in NFPA 20 is it actually stated that the 10 pipe diameters must be a single, continuous straight run of pipe?

NFSA says the 10 diameters can be vertical, horizontal, or a combination, but NFPA 20’s figure seems to show exceptions.

Is NFPA 20’s 10‑diameter rule only triggered by elbows/tees that introduce a horizontal component to the change in direction? (For example, a vertical elbow turning up does not trigger the 10D requirement.)

Is this 10‑diameter rule only applicable to horizontal split‑case pumps?

Or does it apply to all pump types?

​I’m trying to reconcile the NFSA explanation with NFPA 20’s figures and determine whether certain configurations truly require the 10D straight run. Thanks in advance for any clarification.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Route Diesel Pump Relief Discharge to Suction?

2/16/2026

3 Comments

 
For a diesel engine–driven fire pump installation, is it permitted by NFPA 20 to route the PRV discharge piping back to the fire pump suction piping, at a point downstream of the suction control valve, particularly in cases where the fire pump test/meter header discharge is already routed back to the pump suction?
Picture
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Seismic Req'd on Fire Pump Suction & Discharge?

1/27/2026

2 Comments

 
Haven't come across this one before - are the horizontal pipes, both suction and/or discharge from a fire pump, required to be seismically braced?

We have seismic bracing required for the building and a review comment to assess bracing for the fire pump suction and discharge. NFPA 20 and 13 both don't seem to speak to it, but perhaps I am missing something.

What is code required for seismic on these two runs?

Thanks in advance.

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

How to Address Fire Pump with Poor Supply?

1/20/2026

17 Comments

 
We have a disagreement on a fire pump installation. Flow test shows 42 psi static, 10 psi residual at 475 gpm from an 8" municipal main.

The fire sprinkler contractor plotted the water supply curve and says it cannot support the specified 1,000 gpm @ 100 psi pump; they're refusing to certify the fire pump without a suction tank or another resolution.

The mechanical engineer argues the 8" main at 42 psi static should theoretically deliver way more than 1,000 gpm and questions whether the flow test results accurately represent what the pump will actually see at its suction connection.

The steep pressure drop (42 psi to 10 psi in only 475 gpm) seems abnormal for an 8" main.
The area has aging infrastructure and known low-pressure issues.

Looking for the community's input on: (1) 
Is the fire sprinkler contractor correct to base their analysis on residual pressure under flow conditions, or should we be looking at static pressure as the mechanical engineer suggests?

(2) What's the correct NFPA 20 methodology for evaluating water supply adequacy for a fire pump?

(3) When you see such a steep pressure drop in a flow test, what are the typical causes and how would you approach resolving this?

What solutions have worked for others dealing with marginal municipal water supplies?


Thanks in advance.
​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
17 Comments

Fire Pump Test Loop Connect Upstream of OS&Y?

1/14/2026

5 Comments

 
NFPA 20 (2019) Figure A.4.22.1.3(b) provides a typical diagram indicating pipe for fire pump test connections. In this detail the flow meter loop is shown to return to the suction side of the pump and connect between the fire pump and the suction side OS&Y control valve.

I have seen installations over the years
 where this connection is placed on the inlet or city side of the OS&Y. This seems to simplify the loop arrangement. Functionally, it would seem to be similar as you would need the OS&Y open to allow some cooling water to reach the circulation relief valve.

Is there anything in NFPA 20 that would prohibit this arrangement?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Sensing & Air Lines Need Be "Listed for FP?"

1/13/2026

4 Comments

 
In order to use pipe and fittings, they need to be "listed for fire protection service."

Do fire pump sensing lines need to meet this listing?

What about compressed air lines coming from the air compressor to the air maintenance device, do they need to meet this listing?

What about air on the downstream side of the maintenance device?

We're curious on different methods to install these components where some fittings & pipe combinations are listed and some aren't (such as copper pro-press for sensing lines).

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Tolerance in Pump Curve Nameplate vs. Test?

12/17/2025

8 Comments

 
We find that the pressure and flow vary between the nameplate and the shop test curve of the UL-listed fire pump.

What is the allowable tolerance for the difference?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Keep NPSHₐ > NPSHᵣ At All Times Pump Running?

11/24/2025

6 Comments

 
According to NFPA 20, for any pump installation, the NPSH supplied must be at least equal to the NPSH required for the operating conditions specified.

So does the NPSHₐ need to be continuously
maintained at or above the NPSHᵣ during pump operation?

During the operation of the fire pump, the liquid level of the fire water tank will keep dropping, which may lead to a situation where the NPSHₐ is lower than the NPSHᵣ (unless the fire water tank is built at a very high elevation).

​Is this situation permitted?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Standpipe for Scissor Stair Need 500 or 750 gpm?

11/19/2025

4 Comments

 
For scissor stairs having 2 separate standpipe risers (one of them is a combined sprinkler and standpipe system) running 12 floors, how do we size the pump flow rate required?

Can we argue that we can use
a 500GPM pump since the Risers are in close proximity to each other and are within one stairwell, or should we use a 750GPM pump following the NFPA 14 sizing of 500GPM plus 250 GPM per additional riser?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
<<Previous
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT