MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Proper Location to Sample Antifreeze?

2/23/2023

2 Comments

 
What is the proper point in a system to take the antifreeze sample? 

I have taken readings at both outlets at the check valve, unfortunately a contractor is saying to take it at the most remote point. Those locations are either 25-feet in the air, or not installed at all.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments
Dan Wilder
2/23/2023 08:14:36 am

You are both correct per NFPA 25 - 23' Edition
However, system size plays a role. Sounds like a secondary letter of recommendation needs to be sent to add a remote inspection point but read the appendix as this may cause dilution between the upper and lower sections of the pipe which is the intent of the higher testing point.

5.3.4.1 The antifreeze solution shall be tested at its most remote portion and where it interfaces with the wet pipe system.

5.3.4.2 Where antifreeze systems have a capacity larger than 150 gal (568 L), tests at one additional point for every 100 gal (379 L) shall be conducted.

A.5.3.4
Sampling from the top and bottom of the system helps to determine if the solution has settled. Antifreeze solutions are heavier than water. If the antifreeze compound is separating from the water due to poor mixing, it will exhibit a higher concentration in the lower portion of the system than in the upper portion. If the concentration is acceptable near the top, but too low near the water connection, it might mean the system is becoming diluted near the water supply. If the concentration is either too high or too low in both the samples, it might mean the wrong concentration was added to the system.

Reply
Todd E Wyatt
2/23/2023 09:20:49 am

A similar prescriptive requirement for the “test connection(s)” for “Antifreeze systems” is referenced in “2022 NFPA 13 — Standard for the Installation of Sprinkler Systems” which references “2020 NFPA 25 Standard for the Inspection, Testing, and Maintenance of Water-Based Fire Protection Systems.”

REFERENCES
2022 NFPA 13 — Standard for the Installation of Sprinkler Systems
Chapter 8 System Types and Requirements
8.6* Antifreeze Systems.
A.8.6
In cold climates and areas where the potential for freezing of pipes is a concern, options other than antifreeze are available. Such options include installing the pipe in warm spaces, tenting insulation over the piping [as illustrated in Figure A.9.9.1(a) through Figure A.9.9.1(f) of NFPA 13D], listed heat tracing, and the use of dry pipe systems and preaction systems.

ENHANCED CONTENT
Antifreeze systems often are used as subsystems of a wet pipe system. Antifreeze systems are similar to wet systems, but they are not classified as wet systems. These systems are intended to protect small areas that could be exposed to freezing temperatures, such as outside loading docks. Antifreeze systems also are used for larger areas such as freezers, as well as for residential areas that are not protected against freezing temperatures.

Antifreeze systems were once economically more appealing than dry pipe systems for protecting small areas. The reduction in size and cost of certain dry pipe valves, combined with the added expense of backflow preventers and expansion chambers, has made antifreeze systems somewhat less appealing. However, since the hydraulic calculations for an antifreeze system can take the design area reductions of a wet system, there are situations in which the antifreeze system is more economical. Even where a backflow preventer is not required, a larger area protected with a dry pipe system could still provide a more economical option due to the cost of antifreeze for larger systems.

In August 2009, a fire in Truckee, California, brought to light potential problems with the combustibility of antifreeze solutions. In that case, an antifreeze solution was atomized through a discharging sprinkler and exploded, resulting in a fatality. After the Truckee incident, research performed on antifreeze solutions used in sprinkler systems resulted in the issuance of a Tentative Interim Agreement (TIA) by the NFPA Standards Council in August 2012 that prohibited the use of traditional antifreeze solutions in favor of listed solutions that will not ignite. While the original problem was brought to light in a residential occupancy with residential sprinklers, the testing found similar problems in nonresidential commercial applications with standard spray sprinklers.

8.6.3.6*
A drain/test connection shall be installed at the most remote portion of the system.
A.8.6.3.6
Systems are required by NFPA 25 to have the concentration levels checked at the supply inlet to the antifreeze system and at a remote point of the system.
8.6.3.7
For systems with a capacity larger than 150 gal (570 L), an additional test connection shall be provided for every additional 150 gal (570 L).

ENHANCED CONTENT
Checking the concentration level of the antifreeze solution only at the inlet to the system does not necessarily confirm that the solution in the remote portions of the system is at an acceptable level. To facilitate taking a sample, an additional test connection is required at the remote portion of the system. Additional test connections are also required for larger systems. Checking the additional locations is required by NFPA 25, as discussed in A.8.6.3.6.

2020 NFPA 25 Standard for the Inspection, Testing, and Maintenance of Water-Based Fire Protection Systems
Chapter 5 — Sprinkler Systems
5.3.4* Antifreeze Systems.
5.3.4.1
The antifreeze solution shall be tested at its most remote portion and where it interfaces with the wet pipe system.
5.3.4.2
Where antifreeze systems have a capacity larger than 150 gal (568 L), tests at one additional point for every 100 gal (379 L) shall be made.
5.3.4.2.1
If the results indicate an incorrect freeze point at any point in the system, the system shall be drained and refilled with new premixed antifreeze.
5.3.4.2.2
For premixed solutions, the manufacturer’s instructions shall be permitted to be used with regard to the number of test points and the refill procedure.

Chapter 8 Fire Pumps
8.6 Component Replacement Testing Requirements.
There is no “A.8.6.3.6.”

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT