I am working with a company storing Class IIIB liquids in plastic tanks. Tanks range in size from 2000, 3000, to 6100 gallons.
We struggled to find a design that works in NFPA and therefore went with a .40/3,000 from FM DS 7-32; however, now we do not know what to do with the containment requirements. What should the containment duration be? Since they are plastic tanks, I have assumed they would all fail and would essentially need containment around each tank? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
I have a project I'm working on for a data center, and the owner is requesting a Hazard Mitigation Analysis (based on NFPA 855). I'm trying to see if NFPA 855 is applicable since it relates to energy storage systems (ESS).
The end user will have a UPS installed in each rack instead of a central UPS, and each rack will only be 0.55 kWh. FM is also applicable in this case, but FMDS 5-32, Section 2.3.1.4.2 indicates that if your in-rack UPS exceeds 20 kWh, then that pushes the system into an ESS and FMDS 5-33. But, NFPA 855 indicates that if aggregate quantities within the fire area exceed 20 kWh (which we would be for the data hall), then it's defined as an ESS. Is the in-rack UPSs below 20 kWh are actually defined as an ESS or if they're just information technology equipment and NFPA 855 doesn't apply? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have an existing warehouse with ESFR protection. The tenant is adding a rack of rolled carpet in the warehouse. NFPA 13 doesn't cover rolled carpet in rack storage.
FM 8-30 is a guide....I have questions; maybe you all have come across them and can provide some insight. First - Table 1 shows for standard carpet racks over 12' to use K14 QR sprinklers (20 @ 7psi) - this is not ESFR design - can we leave the overhead system as ESFR, or should this area be changed out to provide the 20 @ 7psi sprinklers? Second - Table 1 also states that in-rack sprinklers are needed. Section 2.4.3.1.3 states to balance the in-rack sprinkler system water demand with the ceiling level water demand at the point where the two systems are connected. If you can't get these two to balance, can you install in-rack sprinkler systems independent of the overhead system? If you can, where is the design criteria to do that? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe FM Data Sheet 8-30 Having To Do With Roll Carpet Storage - on Table 1, how many sprinklers on a line do we calculate when we have 30 heads?
NFPA 13 does not cover roll carpet storage, and the NFPA 13 Equivalency Clause allows us to use FM Global. Take a look below, and the only thing I can not figure out is if I am required to discharge 30 K11.2 sprinklers @ 7.0 psi, how many open sprinklers would I calculate on a line? Maybe 7 sprinklers on 4 lines with 2 sprinklers on one line? It has to be in writing somewhere, but I can not find it! Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Does FM Global allow the use of 8k-factor sprinkler heads in HC-3 areas?
The ceiling is only 11 ft. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe How should the new provisions in FMDS 2-0 (2025 Edition) regarding skylights in storage areas (sections 2.5.4.1.7 and 2.5.4.1.8) be correctly interpreted?
I have two cases based on the flowchart from the snippet below. In both scenarios, sprinklers will be required (even in the case highlighted in the green rectangle, which is optional). My question is: Should they be installed at the base of the skylights, at the same level as the surrounding ceiling-level sprinklers (similar to Option 2 for skylight protection in the 2023 edition of FMDS 2-0)? Or should they be installed inside the skylight, close to the highest point of the skylight (similar to Option 1 for skylight protection in the 2023 edition of FMDS 2-0)? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I am working on a project with non-enclosed vertical floor openings, approximately 6-ft by 10-ft. Looking at FMDS (Factory Mutual Data Sheet) 2-0 and NFPA 13, I found similar language that I need help understanding.
FMDS 2-0 2.5.1.7.4.1: A non-enclosed vertical floor opening does not need a combination of draft curtains and closely spaced sprinklers if
(B) seems to contradict (C) as I read it. (B) seems to be describing an area of 400 ft², which leads me to believe I am misunderstanding something. NFPA 13 words it differently, but it still didn’t click. NFPA 13 2022: 9.3.5.4 Large Openings. Closely spaced sprinklers and draft curtains are not required around large openings such as those found in shopping malls, atrium buildings, and similar structures where all adjoining levels and spaces are protected by automatic sprinklers in accordance with this standard and where the openings have all horizontal dimensions between opposite edges of 20 ft (6.1 m) or greater and an area of 1000 ft² (93 m²) or greater. How should the 20-ft horizontal dimension requirement be interpreted, and how does it work together with the 1,000-ft² minimum area requirement without creating a contradiction? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I'm designing an in-rack sprinkler system for an automatic storage retrieval system, up to 30 ft tall. I've designed the system per FM Data Sheet 8-34.
The storage commodities are open-top, non-expanded combustible bins. I referenced Section 2.2.7 since this is a mini-load automatic retrieval system. I'm currently using Figure 39 for the in-rack sprinkler layout. I didn't see anywhere what hose stream allowance to use for in-rack sprinklers only. I currently am using 500 gpm in my design. I attached the FM data sheet 8-34. I based the design from page 85, table 40. Figure 39, unexpanded plastic, 15ft distance between rack sprinklers. Is 500 gpm hose allowance applicable here? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We are currently discussing with the authorities regarding obstructions and their implications subject to FM Global design requirements (FM 2-0, 2021-10).
Specifically, the scenario involves a round duct (2.3 ft / 700 mm in diameter) positioned 12 inches (300 mm) below the sprinkler deflector in a non-storage application. Is it necessary to install sprinklers below the duct in this case? Below is a relevant excerpt from FM 2.0 (2021-10): 2.5.2.5.4.1 Any object up to 4 ft (1.2 m) wide, as measured in the object’s least dimension and in a plane that is parallel to the floor, does not qualify as an obstruction to the sprinkler’s discharge pattern. I would like to clarify whether any object up to 4 feet wide is considered not an obstruction, regardless of the vertical distance from the deflector (or thermal element). Alternatively, must we adhere to the 3 feet (0.9 m) clearance requirement? Your expertise and clarification on this would be greatly appreciated. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have a requirement from a client to use K25.2 sprinklers on a building up to 50-ft in height.
The design criteria that is provided under NFPA 13 is 12 K25.2 sprinklers at 50 psi, but this criteria is not available in Chapter 13 of NFPA 13. Does anyone know where this came from, or whether it's appropriate? It's for up to a 50-ft roof for protection of cartoned, non-expanded Group A plastics. Thank you. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe In-Rack Horizontal Barriers according to FM Global Data Sheet.
Were can I find any details about how to place the horizontal barrier using FM Global Data Sheet 8-9 Scheme 8-9a? In NFPA 13, there is a figure (NFPA 13-2016 Figure 17.1.2.9.4.2(A) ) showing this, but I can´t find any such figure in the Data Sheet. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have an ESFR project with Obstructed Construction and want to be sure we're locating the height of the sprinkler 100% correct. This is an FM-Global project.
We are using K14 ESFR uprights. The bays are 25-ft x 25-ft boxed with W27 beams and contain small bays with W18 beams that are 6'-3" in-between. As far as I can tell, the sprinkler height is compliant as long as the center of the operating element does not exceed 6-inches below the W18 beams, to a maximum of 22-inches below the deck. So 4-inches maximum below the W18 beams is the target. We're using Table 8 in FM Data Sheet 8-9 for the design criteria. Is this approach correct? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe A couple of FM Global questions:
Does FM Global have any requirements for overhead doors? (such as NFPA 13: 8.4.2(3) (2013-2016), 10.3.2(3) (2019)) Does FM Global have any restrictions for private fire service mains under buildings? (such as NFPA 13: 10.4.3 (2013-2016), 6.4.3 (2019)) Can't seem to find relevant material there. Thanks in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe The 2016 and 2019 standards are allowing ESFR designs that the 2022 standard does not.
For example: A warehouse with a ceiling at 35-ft. Group A Unexpanded Exposed on floor probably to 20-ft. Sprinkler design is ESFR, (12) K16.8 pendents @ 52 psi. This was okay in 2016 and 2019, but now, 2022 does not allow for this. Does this mean they completed tests that show this 12@52 K-16.8 WILL NOT work? Is there fire testing to prove this? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Can ESFR Be Used for Extra Hazard Group 2?
ust before I saw that discussion on the forum I was confronted with a nearly finished, similar situation. A new technical plant for manufacturing of large-diameter high voltage cables. Huge amount of PE in the next-to-outer layer, and the sprinkler designer have based the fire protection on ESFR due to ‘’all the plastics’’ and generally large ceiling heights – variation between 40 and 55 feet – and a wish for ‘’maximum flexibility’’, by using table values for UUP for the respective ceiling height. NFPA 13 – 2019 is to be used for the design. The manufacturing process starts with a thin single wire and ends in an obvious UUP commodity. In my mind this is mostly a production risk to be protected with spray sprinklers and density/area calculations, or CMSA-sprinkler parameters where the ceiling height permits it, especially as most of the fire load is moving cables, without automatic stop because the alarm could be undesirable or false. It was said that cables during production would be directed up towards the ceiling, turn and twist on large diameter wheels, and also have large horizontal stretches before they run down into the next machine that may put on a new metal screening or extruding the outer PE layer before PVC or similar outer layer. Obviously a multi-stage production that in the end makes one large cable from 3 or more smaller cables. As I have seen in earlier discussions, the understanding of the text in chapter 23.1.1 saying ‘’ESFR sprinkler shall be permitted to protect : …. Any storage arrangement OH1, OH2, EH1, and EH2 design criteria’’ must be vital for the understanding. I don’t feel the actual situation is a storage arrangement, but if so, what is the target for the wording design criteria? I suspect there will be ‘’longitudinal flue spaces’’ between the cables, transvers flue spaces are not possible. Some places there will be cable(s) in conflict with the minimum 300 mm horizontal distance from a storage suppression sprinkler rule. However, this is the first time I have been presented for a ‘’ceiling only’’ option with 1 or 2 intermediate levels ESFRs having water shields. And (luckily !?) someone had found the FM DS 8-9 Table 17b and put in K 480 storage sprinklers in the part of the manufacturing building with the highest ceiling. Hopefully this is not the only cable manufacturing plant in the world, and I would greatly appreciate other views on this subject. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Is there an FM Global requirement for a minimum safety factor in a hydraulic calculation?
We have a project that is following FM requirements, and the calculation "safety cushion" is coming in at 2 PSI. We have looked through the FM Data Sheets, but cannot find anything to give a minimum criteria. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have sprinklers at an exterior overhang over 100 feet above the floor (ground) it protects. There will not be anything stored directly beneath the overhang.
There is occupiable space above the overhang. It's noncombustible construction; a mid-rise office tower. Questions have been brought up about heat collection, and the effectiveness of sprinkler spray: if there was a fire on the ground level, will enough heat be collected at the overhang 100-ft up in order to operate an intermediate temperature sprinkler that is 286 degrees F? What will happen if there are high winds (common for this area)? And if the sprinklers do discharge, will the water spray droplets evaporate before reaching a proximity of effectiveness? Will a "cooling effect" even happen? The AHJ will allow the sprinklers to be omitted. I'm not seeing anything specific to very high ceilings in NFPA 13 (2016). My question to you all: Where can I find the science to backup their decision? Do you know of any resources where this scenario has been studied, evaluated, or fire-modeled? (FM or non-FM?) Obtaining a PE review is not a desirable option. (I am aware that FM datasheets address this scenario as requiring sprinklers.) Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Would the rack storage of non-encapsulated, Group A, unexpanded plastic commodities, stored in solid plastic containers (totes), be considered cartoned or exposed?
NFPA-13 Section 3.9.1.1 defines cartoned as storage consisting of corrugated cardboard or paperboared containers fully enclosing the commodity. NFPA-13 Section 3.9.1.13 defines Exposed Group A Plastic Commodites as those plastics not in packaging or coverings that absorb water. This leads me to think that any rack storage of Group A unexpanded plastics within solid plastic containers should be considered exposed, as these are not cardboard or paperboard nor does plastic absorb water. Thanks in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe This feels like a silly question, but we have high-piled, non-combustible storage, with open-grate or solid level single/double row permanent racks with Extra Hazard Group 2 overhead system.
I'm trying to identify the actual code verbiage that says nothing is required from an code/NFPA standpoint. The product is metallic car parts with no added materials, just exposed solid metal, no plastic gaskets or spacers, etc. The 2015 IFC is the highest code in my jurisdiction, so starting with that, Chapter 32 is for High-Piled "Combustible" Storage and provides no avenue for code justification. NFPA 13-2013 defines "Noncombustible Material & Automotive Components on Portable Racks" but also gives no criteria for non-combustible storage. FM Global Data Sheet 8-1 actually lists noncombustible as a commodity classification, unlike NFPA 13, but does not provide a criteria stating no coverage. Is this just the simple scenario where code or NFPA standards don't list a requirement or criteria because it just doesn't require anything? Again I feel like it's a silly question given the commodity but I believe the only rules to follow would be obstruction rules and distance from deflector to storage. Thoughts? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Does FM Global design criteria weigh in on whether skylights require protection?
Do they simply adopt the same provisions in NFPA 13 in this regard? Or is there some devation? I can't see any allowance for omission of sprinkler protection for skylights in Data Sheet 2-0. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have a building with FM Approved doors, but I can’t identify the fire resistance rating. We have a fire label but nothing else (see the image). Is there a minimum fire rating for any FM Approved door? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
I have a project with a workshop space that has a ceiling height of 70-feet from floor level.
How do I approach sprinkler selection & system type for this height? Does NFPA 13 have a ceiling height limitation? I see a couple of tables in FM Data Sheets, but is this the only source for protection at these heights? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe NFPA 13 does not allow ESFR protection for shelf or bin box storage. I can see the logic, and this has been in the code for years.
However, FM Data Sheet 8-9 does allow ESFR protection for shelf and bin box. I can protect shelving up to 15-feet with 0.85 over 2,500 sqft but I can't protect it with K25 at 70 psi. Any insights on the logic here? Has testing been done that supports this one way or another? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have a high-piled storage project that falls under both the International Fire Code and FM Global. We are using FM Storage Sprinklers.
Are smoke and heat vents required? Under the International Fire Code Chapter 32, I am directed to Section 910 for smoke and heat vents. Section 910 states that if ESFR sprinklers are used then smoke and heat vents are not required. I have read several definitions for ESFR, and they appear to be essentially the same as FM Storage Sprinklers. My problem is that per the interpretation, if I follow FM Global Data Sheet 8-0 and use Storage Sprinklers, then per IFC Section 910.3 I must have the architect add smoke and heat vents for every 50,000 sqft of the buliding. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I recently investigated some fire doors at one of our older buildings and saw they have an FM Approved label on them instead of a common UL Listing. I'm used to the UL listing label which clearly states the fire rating in minutes or hours. The FM label I saw gives some outdated ASTM standards and references a CABO report but doesn't clearly state the fire rating.
Does anyone have experience with the FM Approved fire door labels? Based on my research, FM stopped approving fire doors a while ago. Thanks in advance. Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe |