MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

How to Address AFFF Leakage in Bladder Tank?

12/31/2019

6 Comments

 
First of all I work at a gas company as a Fire Equipment Maintenance Specialist in Libya. My job is to follow up and assess efficiency of fixed firefighting systems and provide plans for preventative/corrective maintenance/testing based on schedules.

One of our firefighting systems has a foam bladder tank which protects an oil tank and plant operations.

My problem is when we started this project the bladder tank was built out of global standard. The foam concentrate AFFF is stored between the internal tank wall and membrane. Water gets inside the membrane which forces the foam to get out through the rated membrane. 

I know it is wrong and does not produce a perfect foam solution within the specification. When I complained about this case, my manager asked me to provide an opinion based on international standards. 

Is there guidance within NFPA-standards that can help me address this issue?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments

How to Decide on Type of Pre-Action System?

12/30/2019

7 Comments

 
I would like to open up a topic to this amazing forum.

Preaction systems...types, cost, challenges, panel set-ups...I continue to see the vast lack of knowledge amongst the design and management community.

Which type is best? Which is more economical? Which is best for your company to install or to maintain? How does a double interlock system affect design/cost? Can a single interlock system be set up to operate the way you need and at a lower cost? Does the AHJ typically have any special requests?

Knowing these answers could only make everyone's lives easier. Thanks in advance!

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments

Is Pitot the Same As Residual on Flow Test?

12/27/2019

6 Comments

 
Fire hydrant flow test question - is the pitot the same as the residual pressure on a water flow test from a fire hydrant?

Is it possible to know the residual pressure and 'chart out' the flow of the fire hydrant, or is there a way to determine the flow with only the static and residual pressures?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments

What is Maximum Allowed Pressure for CPVC?

12/26/2019

1 Comment

 
What is the maximum working pressure allowed for CPVC?

I understand many manufacturers have 175 psi listings, but I'm wondering if there's anything that's listed for higher pressures. Thanks in advance!

​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
1 Comment

When to Apply Minimum Area for High-Temp?

12/24/2019

4 Comments

 
If I have multiple compounding remote area adjustments, when does the minimum remote area size for high-temperature sprinklers get applied?

For example, if there is a dry system protecting storage starting at 2,500 sqft, which calculation is correct?:

(a) 2,500 sqft x 0.75 (high-temperature reduction) = 1,875 ... rounded up to 2,000 sqft for minimum area, then 2,000 x 1.3 (dry system area increase) = 2,600 sqft.

or

(b) 2,500 sqft x 0.75 (high-temperature reduction) = 1,875 ... 1,875 x 1.3 (dry system area increase) = 2,437 sqft, which is greater than the 2,000 sqft high-temperature minimum.

Thanks in advance!

​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments

Different K-Factors for Res. Sidewall & Pendent?

12/23/2019

4 Comments

 
A three-story dormitory and we have residential-style pendent sprinklers in the corridors with residential sidewall and pendent sprinklers in most of the units. 

By code, are the pendent and sidewall sprinklers required to have the same k-factor?

Residential k-factors jump around a little and I wasn't sure if the requirement (or industry standard) to not mix k-factors would cover different sprinkler orientations too. Thanks in advance!

​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments

Egress from Corridor Through Another Room?

12/20/2019

5 Comments

 
Are there any scenario where the means of egress can be routed from a corridor, through a room, to the exterior? Must all egress corridors discharge to the exterior?

I would assume panic hardware would have to be provided and the room couldn't have a means of being locked, but if a room is relatively low-hazard (like a classroom) could it be used for egress between a corridor and the exterior?

​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments

Is Powder-Coating Facility F-1 or F-2 Occupancy?

12/19/2019

1 Comment

 
What occupancy type would you consider a building being used for powder coating of metal chassis?

The IBC lists F-2 (Low-Hazard Factory Industrial) as the occupancy for metal fabrication and assembly and basically the fabrication or manufacturing of non-combustible materials in which the processes do not involve a significant fire hazard.


Anything not listed as F-2 would be considered F-1 (Moderate-Hazard Factory Industrial).

In this building they bring in the metal chassis, send them through an oven to warm them up, then send them through another booth to standblast them. Then the chassis are powder-coated before going through a final oven to be cured.

In my opinion and past exeprience with powder coating it can be a pretty hazardous activity with explosive hazard and with finely divided particles. I do know the booth is pretty large for powder coating will need to have fire suppression. The big question is would be consider this building F-1 or F-2 requiring fire suppression throughout, as the building is well over 12,000 sqft in area. 

​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
1 Comment

Does Standpipe Riser Need to Be Visible?

12/18/2019

6 Comments

 
Where exactly in the International Fire Code or International Building Code (or NFPA standards) does it state that a standpipe riser must be visible or unobstructed? 

Is there anything that prohibits me from sheetrocking the standpipe riser os installing it inside a wall? Of course the hose outlets will be exposed - but what about the riser?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments

Run Fire Standpipe on Exterior of Building?

12/17/2019

5 Comments

 
Can we run a 6-inch standpipe for a highrise building (24-story) fully on an external wall? The main would come out of the pump room and take branches for each floor from the riser. This new building has a major space shortage and it's not possible to run the pipe within a shaft inside the building. There is no issue of freezing as the temperature does not drop to the freezing point.

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments

Why Does 4-Story Townhouse Require 13R?

12/16/2019

3 Comments

 
Why does a townhouse which is 4-story require an NFPA 13R system?

The IRC is specifically geared toward one-and two-family dwellings up to 3 stories, but the IBC allows 13D systems in R-3, R-4 condition 1 and townhouses (903.3.1.3).

Is there another prevailing code reference that overrules this allowance?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments

Separate New Sprinklered Addition vs. Existing?

12/13/2019

3 Comments

 
We have a non-conforming fraternity building that wants to build a new two-story covered entrance canopy that ties into the existing roof. It is a heavy timber construction and has no concealed spaces. The fire area is already too large, so our interpretation is this would trigger a sprinkler system in the whole building.

A more lenient interpretation might be to only sprinkler the new portion, and potentially add some rated separation between the existing non-sprinklered building and the new sprinklered entry canopy, but I am not aware and I can't find anything about separation between sprinklered and unsprinklered portions of a building. Would this arrangement be permissible by code?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments

Does 2-hr Window Sprinkler Require 2-hr Supply?

12/12/2019

4 Comments

 
High-rise office building, predominantly light hazard occupancy. Water supply is designed for a 30 minute duration (roof mounted gravity water storage tanks).

We need a 1-hour separation between two tenant spaces. The architect has specified a glass partition. As such closely spaced heads are being proposed to achieve an equivalent rating.

Does the water supply now need to be upgraded to provide a 1 hour supply of water?

Similarly, if sprinklers are being used to provide an equivalency rating on a required 2-hour rated partition, does the water supply need to be able to supply 2-hours of demand?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments

Use NFPA 13 or 13R for Mixed Use Hotel Building?

12/11/2019

2 Comments

 
We are converting a 3 story condo building (was designed to NFPA 13R) to a hotel. The ground floor will have a restaurant, a bar, and a spa. The upper floors will remain residential.

Will the addition of these new occupancies change the whole design of the building? Will the upper level residential units be required to be designed to NFPA 13 standards?

This building is in Bermuda if that helps. Thank you in advance for your help!

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
2 Comments

Use Exit Access Stair for Total Travel Distance?

12/10/2019

2 Comments

 
A small core area of a two-story office building has two stairs. One is a traditional enclosed exit stair fire-rated at 1-hour. The other stair is intended to be an "open access stair". The project is under NFPA 101 for means of egress and is sprinkler protected under NFPA 13.

NFPA 101 Chapter 38 New Business Occupancies
   NFPA 101 38.3 Protection
      NFPA 101 38.3.1 Protection of Vertical Openings
         NFPA 101 38.3.1.1 Vertical openings shall be enclosed or protected in accordance with Section 8.6, unless otherwise permitted by any of the following: (4) Exit access stairs in accordance with 38.2.4.6 shall permitted to be unenclosed.

         NFPA 101 38.2.4.6 A single means of egress shall be permitted for a maximum two-story, single-tenant space or building provided that both of the following criteria are met:
            (1) The building is protected throughout by an approved, supervised automatic sprinkler system in accordance with 9.7.1.1(1).
            (2) The total travel to the outside does not exceed 100 ft.

The only way to have an unenclosed stair for this building is if the "total travel to the outside" can include travel through the unenclosed "exit access stair". 

Is it permissible to have one open stair and one enclosed stair with "total travel to the outside" going through the open access stair?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
2 Comments

Draftstop Req'd In Omitted Concealed Spaces?

12/9/2019

2 Comments

 
We have a residential R-2 occupancy, four-story, combustible Type V-B, new construction building with an NFPA 13 system. The floor/ceiling assemblies are built with open-web wood trusses. 

All of the interstitial spaces around these trusses are to be filled with non-combustible insulation, which allows sprinklers to be omitted within them in accordance with NFPA 13-2013 8.15.1.2.7 "concealed spaces filled with noncombustible insulation shall not require sprinkler protection."

The IBC (2015) requires drafstopping in combustible construction to "subdivide floor ceiling assemblies" above an in-line with dwelling unit and sleeping unit separations (IBC 2015 718.3.2). However, an exception exists for buildings equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1 (an NFPA 13 system).

If these spaces omit sprinklers due to non-combustible insulation, is draftstopping still required per the IBC?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
2 Comments

NFPA 13R Use Standard Concealed in Lieu of QR?

12/6/2019

4 Comments

 
Can an NFPA 13R multi-residential apartment building use commercial concealed pendent sprinklers with standard response instead of quick response?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments

What's Your Biggest Frustration with Consultants?

12/5/2019

8 Comments

 
What are your biggest pet peeves with consultants (engineers or designers) in our industry? I'm interested.

Just a little about why I ask -  I work as a consultant and also in our business development. In a backwards way, understanding the pain points only helps guide where I can improve and hopefully help business as well. Thanks in advance for your thoughts!

​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
8 Comments

Type of Sprinkler for Corrosive Environments?

12/4/2019

8 Comments

 
For areas with high water vapor concentrations (such as near showers, steam rooms, etc), what type of sprinkler would perform best? Wax coated? Concealed with gaskets? 

There's many circulated images of corroded sprinklers, but I'm interested in what others feel is current best practice for these areas.

​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
8 Comments

Reminder - You Can Ask Any Question!

12/4/2019

 
Just a friendly reminder to bookmark this page: Submit a Daily Discussion

You can send in any fire-protection-related question, for free. Each day at MeyerFire we review all submitted questions and look at the best one for the community here. It's free and anonymous and our best way of sharing expertise with the latest industry challenges.

​Thanks in advance for submitting your questions!

How to Accommodate Closely-Spaced Sprinklers?

12/3/2019

7 Comments

 
Attached is a sketch of an interesting design issue we’ve been dealing with.

We have a convenience stair connecting multiple floors of an office building. With this, we need to treat the opening as an Atrium opening. So we have told the architect that we need a draft curtain with closely spaced heads.

The sketch attached shows some limitations that we’ve been given.
Picture
My question is, how would you suggest we accomplish the required protection given the constraints of this particular stair?

​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments

Announcing the 2019 PE Prep Series Champions

12/3/2019

 
For those who participated in the 2019 PE Prep Series - we'd like to declare the champs! These point totals are an total of each on-time weekly score.

If you didn't know, we're big on Fire Protection PE Exam prep around here. The PE Prep Series was a series of 20 mini-exams to help simulate the pace of the PE Exam. We tracked weekly scores and are now proud to announce the champions of 2019:
Picture
1st Place Overall (179 points):

NFPA HAS ALL MY MONEY

​2nd Place Overall (175 points):

RYAN ON FIRE

​3rd Place Overall (169 points):

ROUND-TWO


Congratulations to our top three champs (who will have trophies shipped to them) and to all the participants.

Click here to see the final standings on the entire season.

Here's to everyone getting good news on test results in the coming weeks!

Thanks to Top November 2019 Contributors!

12/3/2019

 
Thank you to all forum contributors for November. We're continually seeing an uptick in interest and expertise, and I appreciate your willingness to encourage growth in our industry with your contributions! Here's the top commenters for November 2019:
1. Mike
2. Cliff
3. Randy
​4. Franck
5. NK
6. Matthew K.
​7. On the Clock
8. Paul P.
9. Jesse C.
​10. Doug

Best Place to Find High-Temperature Sprinklers?

12/2/2019

6 Comments

 
Being told I need a sprinkler head that exceeds 350 degrees. Not sure one exists. What are the highest temperature sprinklers on the market and what's the best way to go about finding them?

​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT