|
I am working with a company storing Class IIIB liquids in plastic tanks. Tanks range in size from 2000, 3000, to 6100 gallons.
We struggled to find a design that works in NFPA and therefore went with a .40/3,000 from FM DS 7-32; however, now we do not know what to do with the containment requirements. What should the containment duration be? Since they are plastic tanks, I have assumed they would all fail and would essentially need containment around each tank? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Where in NFPA 13 or 30 does it say ESFR systems cannot protect ignitible liquids?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Our facility is exploring constructing two large (7,200 ft²) facilities for media blasting and coating large steel structures.
The facilities have a ceiling height of approximately 40' and are enclosed via a large roll-up door on one end. The coating systems are categorized as flammable liquids. There has been some internal debate on how to categorize these per the IFC - as "spray rooms," which would require fire suppression, or "spraying spaces," which the IFC does not have a prescriptive requirement for fire suppression. The commentary in the IFC notes that spraying spaces are typically "unenclosed", leading us to lean towards considering these spray rooms, even though they make up the entirety of the building versus a portion of it. We've reached out to some of the local AHJs, who all seem to agree with the spray room determination. However, the builder of the structures has indicated that most of their installations have not required suppression, even when reviewed by the local AHJ. Is categorizing these structures as "spray rooms" the wrong application of the term? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe How do you reconcile NFPA 30, 2021 Edition, Chapter 9 General Storage Requirements which reference NFPA 13, 2019 Edition, and vice versa?
NFPA 30 Section 9.6.1 says that the MAQ is doubled when the building is sprinklered per NFPA 13. NFPA 13 has the Extra Hazard Group 2 occupancy, which covers "substantial amounts of combustible or flammable liquids." The word substantial obviously makes it an engineering judgment for when EH2 should be applied. Hypothetical example: An existing warehouse is sprinklered per NFPA 13 to protect rack storage of Class I-IV commodities and cartoned group A plastics. The owner wants to store a Class III-B liquid in the existing warehouse on the storage racks. They would store more than the baseline MAQ but less than double the MAQ they get for having an NFPA 13 system. In my opinion, this storage arrangement would be out of the scope of NFPA 13, so the double MAQ for sprinklering per NFPA 13 would not apply. I'd require a protection scheme from Chapter 16 of NFPA 30. Do you disagree? What if they only wanted to store under the baseline MAQ amount? Would you require a protection scheme from Chapter 16 of NFPA 30? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe What NFPA Standard(s) apply for two diesel generator tanks?
Two diesel generators (not emergency or standby), outside (but have enclosures) with each diesel tank stored underneath, the tank is rectangular in shape and has ~5,000 gallons of diesel fuel. Looking at the following code path; IMC Chapter 13 for fuel oil piping and storage and IFC Chapter 6--> 605.4 Fuel Oil Storage Systems --> storage above ground in quantities exceeding 660 gallons --> NFPA 31; OR IMC Chapter 9 engine and gas turbine-powered equipment and appliances. Is this approach correct? In reviewing both NFPA 37 and NFPA 31, both seem to be applicable; however, when it comes to "outside aboveground tanks" of this capacity, they both reference NFPA 30 (Section 6.3.3 for NFPA 37 and 7.9.3 for NFPA 31). So here's the main question - is NFPA 30 applicable here? I base this on a few things: 1. NFPA 30 Scope section 1.1.2 item 9 - it says it is NOT applicable to "liquids in fuel tanks of... stationary engines" ; and 2. All the boundary and tank to tank separation requirements throughout chapter 22 are based on the diameter of the tank. This leads me to believe this standard was not written for the type of tanks I have, but instead typical giant circular storage tanks.? Any insight is greatly appreciated. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I don’t often dabble in NFPA 30, so I have some specific questions regarding the protection of flammable and combustible liquids that I am having issues finding straight answers to.
I have a sprinklered general-purpose warehouse that stores flammable liquids in container sizes less than or equal to those indicated in NFPA 30 (2021) Table 12.8.1. The total quantities (MAQs) of these containers are also less than those shown in Table 9.6.1. NFPA 30 (2021) Section 12.8.1 indicates that “The liquid-container combinations listed in Table 12.8.1 shall be permitted to be stored in a general-purpose warehouse without quantity limits if protected in accordance with Chapter 16." An older version of NFPA 30 (2015) Section 12.8.1(1) indicates that if “the applicable provisions of NFPA 13 for 20ft high storage of Class IV commodities based on the storage configuration of the liquids” is used for protecting these containers, no additional protection criteria is required barring the storage arrangements are in line with the rest of the Section 12.8. My questions are as follows (per NFPA 13 -2021): 1. If combustible liquids are stored in amounts under the MAQs stated in Section 9.6.1 (and IFC) are the additional requirements of Section 16 (NFPA 30) required, no matter what? 2. If combustible liquids are stored in container sizes less than or equal to those set forth in Table 12.8.1 (NFPA 30), are the requirements of Section 16 still required? 3. Will the storage of these commodities within liquid storage cabinets negate the requirements set forth by Section 16? The bones of the matter is that I am having a hard time finding a section directly indicating that the requirements of Section 16 are not required. Most if not all sections I can find only indicate that Section 16 is to be used when something is stated. Thank you all ahead of time. As always this forum has always been a wealth of information. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We are providing sprinkler protecting inside a spray/paint booth and its associated exhaust ducts.
The question we have is if the sprinkler(s) inside the exhaust duct require the same protective covering as the heads inside the booth below. Thank you in advance for your input. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe The hot topic of AFFFs and PFOS. Where is the requirement stating foam must be used for fire protection for a diesel generator inside a building?
We're looking to eliminate the need for foam instead of replacing it with "fluorine" free foam. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe What design considerations (if any) need to be taken into account for the new refrigerant changes that are coming up for the HVAC industry (slightly flammable or highly flammable refrigerants)?
Are there any code updates, guidelines reference materials etc. Would this possibly affect hazard classifications? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have a project design for a single room (26'-0" x 14'-6", height of 13'-2"). The room is noncombustible and is solely for the storage of one large metal diesel fuel storage tank in the basement of a hospital. The tank is under 8-ft tall. I have researched NFPA 13, 16, and NFPA 30. I used the tables for sprinkler type and criteria.
My confusion is the amount of storage and the size of the tank. The tables in NFPA 30, starting with Chapter 16.5.2.1, have guidelines for tank sizes up to 60 gallons only. This is a much larger, metal, stationary tank (3,000 gallons). What table or design criteria can be used? K-factors of 8.0 or 11.2 - and 0.30 or 0.40 density? We will be using foam for this project and I just want to be sure that I'm approaching and educating myself for the correct approach without missing or violating limitations within NFPA 30 (or the other standards). Thanks for the help! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Are the requirements for sprinklers in an 'Extraction Booth' the same as a 'spray booth'?
I have a customer looking to add wet pipe coverage to their new 'solvent extraction booth' which appears to be the same as a paint spray booth. The customer is claiming that the AHJ told them that there is no requirement for a separate riser as it's not technically a paint booth. I can't find any supporting documentation of this in any NFPA standard. The closest example I can find is a paint spray booth which appears to require a dedicated riser no matter what. Anybody have any experience with this? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Is there a decision tree, or other wholistic look at what is recommended for fire protection measures for flammable and combustible liquid storage tanks?
Does flashpoint of the liquid impact which system type to pursue? This is specifically for liquid stored in day tanks inside a tank farm, but seeking out guidance here on choosing responsible systems overall. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe What is the proper method for protection of high-piled storage of consumer packaged alcohol with an ABV greater than 20% when stored on racks?
Rack storage will be 30-ft maximum height. I'm assuming plastic and glass containers within cartons. There seems to be a scope gap between NFPA 13 and NFPA 30 here, just wondering what protection methods others might have used. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have two above ground 20,000 gallon (US) PET storage tanks, used for food grade oil, located inside in a manufacturing facility, all above ground. I went through NFPA 30 back and forth, still couldn't find what sort of sprinkler protection do I need for this. Cooking oil is considered a Class IIIB liquid, and all references I could were about all other classes, but IIIB. The only reference to IIIB seems to be in smaller containers, in the rack, but no tank storage mentioned. How do I go about designing protection for the tanks? What about the surrounding area? Thanks in advance.
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have a customer who is building a storage building that includes flammable liquids.
The liquids are Class I-B flammable (as classified under NFPA 30). I understand that there are limits for the quantity that is allowed within one control area. The Maximum Allowable Quantity (MAQ) is 120 gallons, from NFPA 30 tables. The reading can be increased 100% when a sprinkler system is used. So the limit increases to 240 gallons with sprinkler protection. The number can increase even more when stored in approved liquid storage cabinets or safety cans, which I assume the customer would prefer. So the final MAQ becomes 240 gallons x 2 = 480 gallons. The biggest storage room is 2,000 square feet and the customer wants to exceed the MAQ to be above 480 gallons in that storage room. I have understood that exceeding the MAQ is permitted if the building is classified as an H-3 Occupancy (High Hazard). This occupancy applies more restrictive requirements. Is there any numerical value for a new MAQ limit in that case? My current path is as follows: Class I-B liquid storage in Storage occupancy > maximum MAQ exceeded > building re-classified as H-3 Occupancy > but where is the new MAQ? Thanks in advance for your input. I usually design under SFS and CEA standards, and they don't have the same MAQ concept within those standards. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have a situation where we'll have a piece of equipment in one control area that has a closed-use pipe arrangement with oxidizing gases that goes through different control areas. I've gotten conflicting feedback on this. How do you figure the amount of "in-use" for each control area? Here's a sketch of the concept: The equipment that is using the oxygen is on the fourth floor Control Area 2. The tanks that feed it are (2) 200 CF oxygen tanks that are in the second floor Control Area 1.
Which of the following two scenarios is the proper way to tally up the "in-use" quantity for the fourth floor Control Area 2 when comparing against the Maximum Allowable Quantities (MAQs)?
My initial gut reaction was that the second option is correct, but now I’m not sure. My reasoning being that if there is an event in 4th floor control area 2 that causes a leak or something like that, it’s not going to just leak out what is physically within the control area… it’s going to leak out everything in all of the piping, all of the equipment, and all of the hooked up tanks. This is all presuming there are no safety devices to stop this from happening. Assuming my initial gut reaction was correct, is there a way to limit the amount so that it stops at the control area wall? As in: is there a safety device such as an automatic shutoff valve we can put at the wall such that in the event of a leak or other event, the automatic valve will shut off and then we only have to count the amount of gas between the equipment and the shutoff valve? I’ve looked in the IBC and its commentary for more info, but couldn’t find anything helpful. I’ve also reached out to a number of different people and there seems to be a variety of different opinions on it. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have a 300 sq ft control area (1 hour rated) for storage of Class IB flammable liquid. The 2018 IBC Table 307.1 permits 120 gallons (no sprinklers required), but this amount can be doubled if the building is equipped with an NFPA 13 automatic sprinkler system.
Our client would like to store about 165 gallons in the room (3 drums). The building is fully sprinklered. What is the required sprinkler design density for this room? We considered Ordinary Hazard Group 2 (same as lab area it supports) or Extra Hazard Group 2 (only occupancy in NFPA 13 that mentions flammable liquids). If EH2, then the minimum water demand becomes quite large: 0.4 x 2500 + 500 gpm hose = 1500 gpm (Under the 2016 NFPA 13 - Section 23.4.4.2.5). Could you help point us in the right direction? Thanks to all in advance for helping us hunt this down. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I wanted to pose the question on hazardous material storage lockers. We wish to protect the locker in accordance with Chapter 14 of NFPA 30 and have rated it for 4-hours to eliminate the need for fire separation distance to the immediately-adjacent main building as allowed.
The locker will not be structurally attached and will only have flashing connecting the two to keep out the elements, garbage, and animals. The locker will only have people in as necessary to get the liquids out. The main building has a door on the "exterior wall" that opens and "reveals" the 3-hour rated hazardous material locker door, which you have to open to get inside the locker. NFPA 30 2015 handbook Section 14.4.3 denotes that lockers over 1500 sqft should be protected permanent building such as attached buildings or warehouses. Our locker is under the 1500 sqft requirements so therefore I would say we are not a building but a "locker". Therefore, the exterior wall openings allowances of IBC (2015) Table 705.8 would be to the lot line (over 10ft) and not the locker itself (0ft), allowing our client to access the locker from the inside of the main building and not having to go outside to access it from the exterior. I was wondering if anyone has had a similar experience or if we should just call it part of the main building and protect it as such and lose the allowances of Chapter 14. Thanks in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have a customer that has a paint storage facility. All the liquids are Class III-B and stored at a maximum height of 6-ft with a minimum 8-ft aisle.
Does anyone have helpful information/guidance information for designing spill containment and coordinating ventilation requirements for a space like this? I know containment is touched on in NFPA 30 - but I'm looking for some more in-depth guidance to get started. Thanks in advance. We are trying to confirm sprinkler design criteria for a liquor company that has alcohol in boxes and on pallets.
The liquor is 100-proof alcohol. Trucks come in and unload in one area, where these are stacked one-high. Then, they are moved to another area and loaded on a different truck. They are not there for a long period of time. NFPA 13-2013 calls this out as a Class IV for alcohol 100-proof or less. This project being under 12-foot high with high-temperature sprinklers, is the design criteria of 0.30 over 2,000 sqft acceptable? The AHJ uses the 2019 edition of NFPA 13 and we can't find anything in there or in NFPA 30 that is similar, unless I'm missing something. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have a project that has Class III liquids in Non-metallic IBC (Intermediate Bulk Containers).
NFPA 30 Tables 16.5.2.9 and 16.5.2.10 list storage requirements for Class III liquids in Nonmetallic IBCs. Stacked IBCs are limited to two-high (~8 feet), and in racks, only single and double row racks are allowed. Under Section 12.8, these containers may be protected as "high storage of Class IV commodities" through NFPA 13, provided that the volume is limited to 13,750 gal (Class IIIB). Does this mean that under NFPA 13, IBCs can be stacked up to 40-feet with 45-feet ceilings as per Table 23.3.1, or in multiple-row racks up to 40-feet high with 45-feet ceilings as per Table 23.5.1? Or similar configurations as per Chapter 22 (CMSA)? Provided the volume limit is not exceeded, of course. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe NFPA 30 Figure 16.2.5 is used to determine if a material is viscous liquid or not. I am having an issue with a interpretation of the "Weight (percent flammable or combustible liquid)". Is this weight for the liquid only or the liquid plus the container? Example: Total package / container weight = 2.48 grams. The liquid inside is a Class III-A mixture that is 0.78 grams (31.5%). If I go with the entire package Figure 16.2.5 is applicable (less than 50%), but if I am just looking at percent of combustible liquids, all the liquid is combustible.
Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have a question regarding the need to provide electrical classification for a building using Class 1A flammable liquids.
For this building, 4 gallons could be out in use (located anywhere in the building). The MAQ is 10 gallons. I have discussed this with NFPA 30 committee, the manufacturer, and the AHJ (who is a knowledgeable FPE). They have all determined that even if the MAQ is not exceeded, electrical classification is required if a flammable/explosive mixture could be present. The NFPA 30 staff directed me to a provision in NFPA 497, Section 5.5, that if the materials will not reach 25% of the lower flammable limit (LFL), this could be utilized to justify not providing classified electrical fixtures. Does anyone know how to do this calculation, or know of firms that can be hired to do this? I am an FPE and do not know how to perform it, and I have spoken with other FPE’s who also are not aware. The gentleman I spoke with at NFPA 30 agreed it would be by an industrial hygienist or a chemical engineer and not an FPE. But does anyone know any that can be hired for a one-off calculation, or have a place where I could learn how to perform it myself (NFPA reference, SFPE article, course, etc.?). Thank you! Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe Building owner is looking to lease some warehouse space for the storage of hand sanitizer…looking at the MSDS, I see it listed as a Class IB flammable.
Going to NFPA 30 and seeing section 16.5.2.7 would be the most appropriate…which then flips me to section 16.6.1 Scheme A as the Sprinkler arrangement. I have to look to see what design densities are needed for the ceiling spray heads and the in-racks. Is this the correct approach? Is NFPA 30 applicable here? Just wanted to make sure I’m not missing something. Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop July '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
August 2026
PE PREP SERIES |
RSS Feed
