MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

How to Test Waterflow for Dual-Feed System?

2/26/2021

3 Comments

 
Has anyone come across a dual riser (dual-feed) sprinkler system in an office tower, with only a single inspector's test?

What is the proper method of testing each flow switch?

In most cases, only the flow switch nearest the inspector's test will operate in a timely manner. Some inspectors will isolate and test, others believe the system should be tested under normal conditions with both control valves open.

Is the deficiency the lack of a second test connection, or that the flow switch doesn't operate within 90 seconds (or even 5 minutes)? Alternatively, is there no deficiency at all?

​​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
Picture
3 Comments

Use Main Drain Test for Base of Riser Calculation?

2/25/2021

16 Comments

 
Is there a method to use a main drain test to calculate the hydraulic curve at the riser itself?

I haven't done it myself, but using a static pressure at the riser, with a residual pressure at the riser, and then to gather the flow a pitot reading on the main drain discharge to measure how much flow?

If the flow discharge outside was greater than the demand of the system, conceivably a hydraulic calculation could be made with the riser as the source point, and with more accuracy than a hydrant flow test somewhere near the site.

Obviously if a backflow test header or hose valve were supplied, a higher flow could be obtained with a better curve.

I heard this mentioned recently so it's just theory to me, but for small remodels having a setup like this could be far simpler (and potentially more accurate) to know the available water supply at the system.

​​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
16 Comments

Heat Loss on Sprinkler Main in Unheated Space?

2/24/2021

9 Comments

 
In our area, wet standpipe/sprinkler pipe running through unheated parking garages always gets heat tracing and insulation. 

On this current project, the general contractor wants us to run a 4-inch main as high as possible to a 7.5-inch thick post-tensioned concrete deck that has a heated space above it and a 24 deg F 1% design temperature below in the garage. They're looping 14-inches of batt fiberglass with a plastic barrier below it creating an envelope around the pipe.

The general contractor is questioning whether the heat tracing is needed. We've got plenty of experience 'tenting' sprinkler pipe in attics but never under concrete. I've suggested they hire a mechanical engineer to do the calculations.

Does anyone have experience with this situation?

​​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments

Help With Old Glycerin Corrosion on Steel Pipe?

2/23/2021

5 Comments

 
Is anyone having problems with steel pipe corrosion after using the older glycerin?

Three year old condominium complex was an NFPA 13R job. About 75% of the pipe is CPVC with exposed basements installed in steel. We hydo-tested four of the buildings in the winter with the glycerin before the buildings had heat so the builder can insulate and sheetrock. We drained out what we could but did not pull any heads in the basement. We didn't think leaving some trapped glycerin in the steel basement piping would be anything to be concerned about.

The basements have developed pin hole leaks and the odor when draining is putrid! I saw the new UL-listed (Freezemaster) antifreeze states, "includes a corrosion inhibitor package".

Any help/advice is greatly appreciated in stopping this attack on the pipe.

​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments

Clearance Required from Nearest Fire Sprinkler?

2/22/2021

4 Comments

 
I get asked by building owners somewhat frequently - what is the required clearance from a sprinkler?

I understand most typical ordinary storage/miscellaneous storage/office/standard spray sprinklers the clearance is 18-inches.

I also understand ESFR requires 36-inch minimum. I'm trying to understand the big picture and not misspeak. 

What about other sprinklers, like CMDA, CMSA? Is there a rule of thumb across the board?

​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments

Who Provides ITM on Deflagration Vents?

2/19/2021

5 Comments

 
Does anyone have recommendations for who would perform inspection, testing & maintenance  (ITM) on deflagration vents under NFPA 68?

My company is having trouble finding a reputable organization that will take it on. The supplier of the chemical explosion prevention system with has turned down the work. There is a push from some to let our own maintenance handle it, per the checklist in the annex, but I feel that a group with this expertise would be a better fit. Thanks in advance.

​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments

Sprinkler Criteria for Compact Mobile Shelves?

2/18/2021

8 Comments

 
Having trouble getting a good feel for fire sprinkler design criteria for compact, mobile storage shelves. These contain Class I-IV commodities. As I understand it, NFPA 13 only covers light hazard for compact shelving.

The metal shelves have a height of 8-feet, the ceiling height is 26-feet. The room is 3,000 sqft, and the shelves have a footprint within that space of 21 x 30 feet. Any help is appreciated. 

​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
8 Comments

How to Calculate Balcony Sprinklers in NFPA 13R?

2/17/2021

0 Comments

 
We have a four-story project that uses NFPA 13R - 2016 Edition. There are balconies with wood structure that are getting sprinkler protection. The building is in a cold climate.

I'm trying to figure out how to correctly incorporate these balcony sprinklers in the hydraulic calculations while still being efficient in the sprinkler design (there's no fire pump on this and poor city supply).

As I understand it in NFPA 13R, my options are:

(1) NFPA 13R for Dwelling Unit Calculation: use dry-sidewall residential sprinklers (Reliable and Tyco have some) for the balcony. This would then be a 0.05 gpm/sqft calculation over a compartment, up to four sprinklers. 

(2) NFPA 13R for Outside of Dwelling Unit: use dry-sidewall quick response sprinkler for balcony. This would be a 0.10 gpm/sqft calculation for four adjacent sprinklers. The inside sprinklers could still be 0.05 gpm/sqft (per 13R), but the balcony sprinklers need to be 0.10 gpm/sqft (per 13R 7.2.2, 7.2.3).

(3) If the balcony is under 500 sqft and meets a string of conditions, then dry-sidewall quick response sprinklers for the balcony can be for the compartment, up to four sprinklers (per 13R 7.2.3.1). We don't meet this here, because there are large glass slider doors over 50 sqft.

Are there other options here, or is my approach for the first two options appropriate? I could very well be overthinking this. Thanks in advance.

​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
0 Comments

Dampers on Clean Agent Releasing or FA Panel?

2/16/2021

7 Comments

 
We are designing a clean agent system for electrical rooms located within a high-rise building. We are proposing having dedicated clean agent releasing control panels for the electrical rooms, and a separate building Fire Alarm Control Panel.

Is it mandatory to connect fire/smoke dampers (and other shutdown devices) in the electrical room with the clean agent releasing panel, or can these be connected to the building fire alarm system?

Thanks in advance.

​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments

CMDA & ESFR Options for Lumber Storage?

2/15/2021

4 Comments

 
We have a 40-foot tall steel construction building, with lumber strapped and stacked, stored in 20-foot high solid piles.

The building is unheated. The building owner has been told by another fire sprinkler contractor that this will require ESFR sprinklers. The owner would prefer a dry pipe system.

We have researched NFPA 13, 2019 edition. It looks as if Chapters 20 and 21 will allow a dry pipe system for this application using CMDA sprinklers.

Anyone else have experience with a scenario like this? What path would you recommend?

​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments

Is a Jockey Pump Necessary with Small 13R Pump?

2/12/2021

11 Comments

 
We have a small project (13,800 sqft total) which is a four-story, all residential apartment building, using mostly CPVC pipe. The system is under NFPA 13R.

The city supply is very poor, so we will have a fire pump that meets NFPA 20 (as is required by 13R). The pump is an 8-HP, 70 PSI at 75 GPM.

Is a jockey pump necessary with such a small fire pump?

Normally, for our large commercial NFPA 13 projects, a jockey pump is not even a discussion because we don't want the main fire pump (500 - 1,500 gpm) cycling on just to support system maintenance pressure.

For such a small project with a significantly smaller fire pump, is there any harm in not providing a jockey pump?

The question is not based on cost - the pump room is microscopic and we're already having trouble fitting in all the equipment and controllers as is.

Appreciate you all - thanks in advance.

​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
11 Comments

Does Deluge System Use Supply or Demand Calc?

2/11/2021

10 Comments

 
This question pertains to hydraulic calculations at the supply and sprinkler sides of a deluge system:

Our example using rough numbers; the deluge system requires 4,000 gpm based on density requirements through the building. This is the system demand.

Now suppose you have a strong water supply. The water supply actually provides 8,000 gpm based on main capacity testing. This is the system supply.

Now my question is, the pipe is wet up to the deluge valve. There is about 50-feet between the deluge valve and the hazard. It is understood that the system demand is 4,000 gpm, but within the pipe network, is it necessary to size the pipe for a deluge system based on 8,000 gpm on the supply side?

Until the water begins discharging through the deluge nozzles, the 8,000 gpm will be surging through the pipe network to reach the nozzles, correct?

​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments

Sprinkler Clearance from Washer in Small Closet?

2/10/2021

7 Comments

 
Is there a minimum distance clearance required or recommended from the fire sprinkler and the top of a stacked washer dryer in small closet?

What is the reason for the clearance needed?

I heard that 4” is needed for the clearance rather than the standard 18” in a public area.

​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments

Change Elevator Hydraulic Fluid Permanently?

2/9/2021

10 Comments

 
I am building out a space that has been vacant for multiple years. The space has a hydraulic elevator that travels 1 floor. There is a sub that is ushering the elevator contractor through the certificate milestone with all the adjacent trades.

He has proposed to change out the Class III-B hydraulic fluid with a Hydro-Safe or equivalent non-combustible fluid in order to work around the NFPA 13 requirement for a pit sprinkler and pit detection to be installed.

My question is, does swapping the petrol-based fluid to a bio-equivalent have any long-term effects on the pump, pistol, seals, gaskets, etc.?

Also, how do I make sure this is the fluid that remains in use for the life of the certificate?

​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments

Heat Trace or Dry-Pipe System for Loading Dock?

2/8/2021

6 Comments

 
We have a project that includes a 3,500 sqft unheated loading dock. We're in the initial design stages of the project.

Based on your experience would you recommend we specify a heat trace or dry pipe sprinkler system for the loading dock?

​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments

Thanks to Top January 2021 Contributors!

2/8/2021

0 Comments

 
A special thank you to those who helped bring in the new year with great feedback and discussion. Here's the top ten commenters for January 2021:
1. Franck
2. CJ Bonczyk
3. Dan Wilder
​4. Jesse
5. Glenn Berger
6. Casey Milhorn
​7. Mike
8. Pete
9. HJ
​10. Wayne Ammons
0 Comments

Sprinkler Zone Req'd for IT Rooms, Elevators?

2/5/2021

7 Comments

 
We have a project where the Authority Having Jurisdiction (AHJ) is requiring zone control valves and dedicated pipe from the standpipe to any IT rooms and sprinklers in elevator shafts.

As a result, we have three zone controls for each floor: (1) the floor sprinkler system, (2) IT rooms, and (3) any sprinklers in elevator shafts.

Is there a code or standard basis for this requirement, or would it be specific to the AHJ?

We're doing the work either way for this project since the AHJ is requiring it, but I would like to know for future projects. Thanks in advance.

​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments

Software or Calculators for CMDA Sprinklers?

2/4/2021

7 Comments

 
I was wondering if maybe there are some calculators or wizards that guide a selection of CMDA sprinklers for storage applications.

We work with multiple standards (Vds, EN, NFPA) and sometimes it takes a long time to find the right point on the curve out of NFPA 13. It would be great to have a tool to verify that density and multipliers were all chosen properly. Thanks in advance.

​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments

Assembly Exit Allowed Below Grade Level?

2/3/2021

5 Comments

 
We have a building that used to be a business occupancy but the new occupant wants to now use the occupancy as a church (assembly).

The building is not sprinklered and has no fire alarm system. The new occupant load is 279 people.

The problem is the main entrance is on ground level but the second rear exit is below ground level to exit the building. Is the second rear exit below ground level acceptable?

​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments

Why Are Standby Fire Pumps Not Required?

2/2/2021

12 Comments

 
If a fire sprinkler systems is designed for "life safety" purposes, should not a primary and standby fire pump be provided? Why are standby pumps not required to improve reliability for these systems?

​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
12 Comments

Backflow Allowed Before Fire Pump Suction?

2/1/2021

8 Comments

 
We have a building with a double check backflow assembly on the suction side of a fire pump. Normally there is a minimum of 10 pipe diameters of vertical plane pipe just before the suction flange.

Is the double check backflow allowed within that distance?

Are there requirements for the backflow to have flanges vs. grooved connections?

A colleague said the control valve should be OS&Y rather than butterfly on the suction side only. Why would this be the case? I would assume the OS&Y would reduce turbulence better than a butterfly, but wouldn't the checks also cause turbulence?

Thanks in advance.

​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
8 Comments
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT