Greetings. My house was built in 2014 and has a fire sprinkler system with heads rated at 175, orange CPVC pipe throughout the attic, and a riser in the garage.
When I bought the home, pressures on the gauge were typically in the 155 psi range. Recently, they have been spiking to 185 and above. My fire line and domestic line separate early, right after the city meter at the street. I installed a pressure relief valve, 175 psi, on the drain off the riser, and it has been dripping pretty constantly, about 1 drip every 10-20 seconds or so, depending on fluctuations in air temp. When the pressure spikes, it brings it down to 175 pretty quickly. My question is, would you recommend I have a fire professional come out and install a pressure-reducing valve? Is that something that would be installed prior to the riser? Thank you. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments
Do you have to protect the whole attic that has smoke partitions with fire sprinklers if only one area has gas-fueled equipment in it?
Can you just protect the one area that has the fuel-fired equipment in it? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have a 24.5' wide porch that needs to be sprinklered. Can we use a dry sidewall sprinkler?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have an NFPA 13D system covering an ADA house that has two pumps in the basement. I am struggling to understand why the two pumps were installed in parallel.
Would this just be to increase Total Dynamic Head (TDH)? Why would you need to increase TDH on a residential system? Basically, the customer wants the pumps replaced with new ones because they're old, and I guess what my question really boils down to is what info do I need to figure out to replace these pumps with the correct size pump(s) to satisfy system demand? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe My coworker and I are disagreeing about townhomes.
Can each townhouse (3 total) have its own NFPA 13D system? Or do they need to have one total system? Each townhouse has a 1-hr separation in the form of UL U347. I cannot find anything that says they can't each have their own, but he is saying he can't find anything to say they can, to which I have always said if it doesn't say no, then it's usually allowed. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe As an AHJ, I would like to ask what other AHJ's enforce for sprinklers in R-3 Occupancies when home health or Boarding Care businesses open facilities in single-family homes?
Please explain your reasoning as well as thresholds like 5 or more, etc. We're evaluating what our requirements and/or enforcement should be. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Regarding light fixtures as obstructions to sprinkler spray pattern per NFPA 13D - many hanging pendant light bases are slim (1”-2” off ceiling) and do not obstruct or prevent cold solder, but the lighting housing hanging below the base (anywhere from 12”-72”) is to be considered an obstruction?
Are these described hanging pendant lights also to be considered obstructions and to remain 36” away? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Do all wet systems require an FDC?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We are on the AHJ side, and Middle Housing requirements are on their way to increase density and reduce the cost of housing in our area. This will allow existing single-family residences to subdivide their lots, which may have up to four additional dwelling units on a parcel.
In anticipation of this, we are exploring options for residential fire sprinkler requirements beyond our already existing code for these small, ADU (Accessory Dwelling Unit) type structures of 1,000 sqft maximum. We would like to maximize the possibilities of this by making the process as easy and inexpensive as possible. One avenue we are interested in is allowing for P2904 flow through sprinkler systems (Section P2904 of the IRC, prescriptive standard for one- and two-family dwellings) that can be installed by a plumber. We are open to omitting the fire plan review process and possibly even a bucket test, but still inspect for head placement, tenting, etc. What are your thoughts? Has anyone looked at this with any degree of success? We would love to hear any feedback you could provide. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I am preparing an assessment for adding a fire protection sprinkler system to an approximately 9,000 sqft existing single-story building that is a state half-way house for juveniles after being released from detention. Fewer than 16 occupants excluding staff.
The architect has deemed it Group R-3 occupancy (although I wonder if Group R-4 Condition 1 is more appropriate.) IFC 903.3.1.2 permits NFPA 13R throughout Group R, and this meets the three stated conditions for this section. Section 903.1.3 allows NFPA 13D in some applications; the list is separated by semicolons and includes R-3 and R-4 condition 1. However, more square feet of this facility is dedicated to non-residential purposes (meeting rooms, classrooms, kitchen, etc.). This seems counter to the scope of NFPA 13D. Even the IFC commentary mentions the use of 13D, but for one- and two-family dwellings. And I'd prefer an FDC and more than a 10-minute water duration. I'm a sprinkler guy, and not a building code expert. My gut says NFPA 13R is most appropriate (and I will ask the building code official), but what nuance am I missing here? Budget-wise NFPA 13D is way more favorable, but it just doesn't seem right. I'd like to know if both NFPA 13D & NFPA 13R are acceptable options for this type of building. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Question regarding a mechanical closet and/or plenum. We have what I'll call a mechanical closet because it houses an electric AC/heating unit for an apartment using NFPA 13.
The sprinkler designer/contractor is calling it a plenum/small space and is omitting sprinklers. The plans do not show any sprinkler coverage. Is this closet a plenum or small enough space to omit sprinkler protection? Is there code justification for this? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe For NFPA 13D and a single family home of 1,000 sq ft, what is the optimal k-factor I should be considering?
In this particular project, we don't have a city water supply but we do have a good well. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have a project with two existing 900 sqft apartments above a non-sprinklered marine repair garage. Only the apartments are required to be sprinklered.
Can I sprinkler the two apartments per NFPA 13D, or do I have to do per NFPA 13R? I know the definition of dwellings says no more than two dwelling units in 13D. Thank you. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Is there any way to install sidewall sprinklers in a room with sloped ceilings?
Say you had a rectangular room with a ceiling attached directly to the underside of a traditional gable roof with a high ridge peak in the middle. Concealed pendent ceiling sprinklers are often not possible because the space above the ceiling is completely filled with insulation. Can you do sidewalls on the vertical walls near the ceiling high point to protect the room? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe For a single-family home with a 6 in 12 sloped ceiling (roof) that is a combustible wood structure.
Does this need a 1,950 sqft calculation due to the slope, or just two sprinklers as NFPA 13D requires? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Imagine you have a 6-unit, true townhouse-construction building covered by the 2018 IRC under construction. It has an NFPA 13D sprinkler and a one-hour separation between units, but there is one common closet for the sprinkler riser and domestic water main. This closet is accessed only through a door on the exterior and is under the control of the landlord, not the tenant.
What is the code path to require any fire separation between that closet and the dwelling units? There is no dog house off the side. The IRC only seems to call out separation between units, and even if you go into the IBC, it is not apparent. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe For NFPA 13D systems which are "multipurpose" or "flow-through" combination sprinkler and domestic systems, it has been troubling me as a fire code official not knowing the maximum length that a dead-end or arm-over section of pipe can be in order to be deemed safe from contaminating the potable water in a home.
NFPA doesn't seem to weigh in on this, that I know of. What is the maximum length for a dead-end or arm-over section of pipe in a combined sprinkler/domestic system? I've been searching for studies, contacting other AHJs, asking plumbers; but no one can give a definitive answer. From what I understand, there are no documented cases of illness from residential sprinkler systems, but I would rather not rely on this as a way to measure safety. I've seen a few sources say (and show) that water only circulates into the dead end at 1.5 x the diameter of the pipe going across. So if water isn't circulating, it seems like there's a risk for contamination. If contamination is not a risk for whatever reason, why have any maximum at all? I would love to get to the bottom of this and I look forward to hearing from others who have a deeper understanding. Thank you. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I'm reviewing a fire sprinkler system under 2019 NFPA 13D for a single family dwelling. The living room basically has "reverse" ceiling pockets as the pockets are lower than the rest of the ceiling (pockets are at 10'-7", the ceiling is at 12'-1"). They have 2 sprinklers in each of the 3 lower sections of the ceiling but no sprinklers in the higher areas (except for a room to the side but in the same area). It seems off to me to omit sprinklers in the higher area but can't figure out how to apply a code to it. Would you apply the ceiling pocket rule if the higher area exceeds 100 cubic feet or is it fine as designed? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have a 4-story building with Levels 2 through 4 being residential. The first floor is retail and amenities. The 4th floor has vaulted ceilings and is essentially open as a gabled roof deck.
The plan was to use CPVC for all residential floors, and at the top floor to run pipe level and extend sprigs up to catch the peak and higher roof areas. Is this acceptable? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Is it worth installing a nitrogen generator for small residential dry pipe systems with less than 50 gallons?
We have about 175 homes with dry pipe systems in our jurisdiction. Would a nitrogen generator be the best solution for corrosion protection? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Does NFPA 13D require trapped air to be removed in a sprinkler system?
In the 2016 NFPA 13, Section 7.1.5, Air Venting - a single air vent for a sprinkler system, with a connection conforming to 8.16.6, shall be provided in each wet pipe system utilizing metallic pipe. I am using CPVC with anti-freeze in most residential systems. Is there a code requirement for a vent for what I'm doing? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Are hydraulic placards required for NFPA 13D systems?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe What concerns should I have about hanging from old wood? Like very old wood, almost petrified? I'm doing an NFPA 13R job for an old historic building that has been moved. I don't know how old, but it uses full dimension wood. The 2x's look like they measure 2-inches thick.
I'm wondering what hanging to this old dry wood is going to be like? Do they need to predrill? Are screws better? Any ideas appreciated! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Does a fire pump on an NFPA 13D system require backup power?
It seems like it should, but 13D does not say that it has to and does not reference NFPA 20. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe With the use of CPVC, what are the limits to how much can be exposed?
I had thought that we needed to have all of the pipe concealed, and I can't see in code how this is addressed. We have a project with a temperature-controlled and insulated attic (the mechanical engineer has confirmed it will be kept above 40 degrees F year-round) in a warm climate. This is in an NFPA 13R apartment building. Is CPVC allowed to be run exposed through the combustible attic space? The attic is not sprinkler protected (NFPA 13R system, 3-story, apartments, smaller-sized project). Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe |