MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Thrust Block Req'd for Heat-Fused Connections?

7/15/2026

3 Comments

 
Have a question on whether or not thrust blocks are required for heat-fused connections.

Per Section 10.6.3 of NFPA 24, additional restraints are not required for heat-fused connections. Under PPI Chapter 7, for pressure piping systems that are joined by heat fusion, flanges are fully restrained and do not require external joint restraints or thrust blocks.

For the above case, is a pressure thrust block required?

We will use
a concrete pad underneath the hydrant and PIV, but not a pressure thrust block.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Include Hydrants in Fire Pump Total Design Flow?

4/23/2026

4 Comments

 
Does the fire hydrant flow rate need to be included in the total design flow rate?

Assuming a building is only equipped with a standpipe system and a private hydrant system, both supplied by a private fire pump, does the design flow rate of the fire pump still need to account for the fire hydrant flow rate?

In addition, in accordance with NFPA 14‑2024 10.5.3.5.1, when the local fire department can meet the water supply capacity requirements, is the supply main for the standpipe system still required to be arranged in a loop?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Any Fittings or Offsets Allowed Under Building?

2/5/2026

6 Comments

 
Is a fire supply allowed to have any joints, offsets, or fittings underneath the building foundation other than the 90-degree elbow looking up to the flange?

​What's the code or standard basis for allowing or not?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

FDC for Each Building in Private Fire Water Loop?

1/2/2026

10 Comments

 
I'm having trouble finding code citations for this, but if a single-owner site with multiple buildings (like a transportation authority property that has multiple separate buildings) has a dedicated fire water loop serving the sprinkler and hydrant water for the site, can they provide FDCs where the fire water ties into the municipal water, and not provide FDCs for the individual building sprinklers?

Or is each sprinkler system required to have its own FDC?

I would imagine that each building with a sprinkler system would still require an FDC, but I can't really find code language about this specific topic.

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Is Full-Size Water Meter Required on 6" Fire Line?

12/3/2025

8 Comments

 
I have a code official who is requiring a full-size water meter on the fire line preceding double check backflow.

The backflow has a 3/4" meter and
a small check on it with electronic connection capability for the water department. 

Are there any applicable code/standard references that mandate this?

A 6-inch meter on the fire line would run about $15k.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Control Valve Allowed Directly Below Hydrant?

6/27/2025

10 Comments

 
Is the installation form of the control valve for the hydrant correct/allowed as shown?

It is a wet barrel hydrant, and the owner wants to save costs by installing the control valve directly below the hydrant.

​How should the effective coverage area of the fire hydrant be considered?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
10 Comments

Hydrant Spacing & Location for Industrial Plant?

6/20/2025

11 Comments

 
For a newly built steel smelting plant, how should the layout spacing and protection range of private fire hydrants be considered?

I have checked that NFPA 1 states the maximum spacing for "Buildings Other than Detached One- and Two-Family Dwellings" is no more than 500 feet, but NFPA 850 specifies a maximum spacing of 300 feet.

Do both govern?

If so, does the more-restrictive one apply?

What should be the protection range of each hydrant?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Are Separate Fire & Domestic Lines Required?

6/17/2025

7 Comments

 
Do I need a separate 6" fire line to a building sprinkler system, and a second water line for all other uses?

This is for an NFPA 13 system. ​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

NFPA Require 2nd Supply for Seismic Highrises?

6/16/2025

3 Comments

 
The IBC section 403.3.3 requires an automatic on-site secondary water supply for high-rise buildings in seismic zone C or greater.

Does NFPA have a similar requirement for on-site water storage in a seismic zone?

All I can find are the bracing requirements in NFPA 13, but I am not seeing anything in NFPA 101 or NFPA 5000.

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Three Buildings Under One PIV and One FDC?

6/12/2025

10 Comments

 
Our project is a school campus with nine buildings.

The Civil Engineer has designed the underground so that three buildings are controlled from a single PIV and an FDC. Additionally, they want butterfly valves on each fire sprinkler riser.

Does shutting off three buildings become an issue, and is this within the NFPA 13 parameters to dictate this one way or another?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Shared Fire Line Monitored by Only One Building?

3/26/2025

6 Comments

 
Before people say, "Ask the AHJ," I am him; he is me.

I have an applicant who has combined plots of land with a mid-rise and some detached townhouses. A shared fire line supplies the two structures, but only the mid-rise FACP monitors the supply tamper.

The townhouse FACP will not know if the water is off (except for the tampers at the risers within the townhouse).

The buildings are owned by the same ownership. They are arguing they are technically meeting IBC 2015 903.4 "Valves controlling the water supply for automatic sprinkler systems, pumps, tanks, water levels, and temperatures, critical air pressures, and waterflow switches on all sprinkler systems shall be electrically supervised by a listed fire alarm control unit."

It is being monitored, but the fire marshal and I are of the opinion this doesn't provide monitoring for the townhouse and does not meet the intent of the code.

Does anyone have any thoughts on whether a shared line can be monitored by only one building that it serves?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Does a Hydrant Fed From Building Meet Code?

3/4/2025

14 Comments

 
My jurisdiction (I am the AHJ) has had several buildings built with private hydrants supplying the sprinkler system where the main comes into the building, through the RPZ, feeds the sprinkler system/standpipes, and leaves the building and feeds the hydrant(s).
Picture
This has always seemed counterintuitive to me, at best. I feel we are "robbing Peter to pay Paul" and have wondered if this arrangement will adequately supply the sprinkler system when we (FD) pull water from the hydrant and pump it back into the FDC.

Per our state law, private hydrants have to be "protected" with a backflow.

Is this configuration code compliant, and if not, what is a solution?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments

Is Automatic Drain Required for Remote FDC?

1/29/2025

7 Comments

 
In an area subject to freezing, we have a remote FDC that supplies a riser room at the same level. The feed is through underground pipe.

Is the base of the FDC required to have an automatic drain similar to what's at the base of dry barrel fire hydrants?

If not, how are these FDC's typically drained after use?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Drainage for Underground Pipe to Remote FDC?

9/12/2024

8 Comments

 
Is there any particular drainage pipe requirements needed for an FDC that makes a U-loop underground?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Can a 90-degree Elbow Be Beneath a Footing?

9/2/2024

7 Comments

 
Can a fitting (a 90-degree elbow) from a fire ductile iron water line be under the footing, which turns the pipe up into the Fire Pump room?

In other words, the pipe feed comes from a water tank underground, then turns up with a 90 under the building footing and the pipes through the footing.

Is this acceptable?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Fire Hydrant Max Spacing and Distance to Bldgs?

8/16/2024

8 Comments

 
I have a bunch of new houses going in. Some are along an existing street, and some are around a newly formed cul-de-sac.

How do I determine the number of hydrants, how far apart they are, and the maximum distance to any of the homes?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Does Each Building Need Own Isolation Valve?

8/9/2024

12 Comments

 
If I have a fire tap that services multiple buildings, is it required to have a service valve outside the building on each line?

Does each building need to be capable of being isolated in case of service needs without interrupting others?

As it is, if one building needs work done to the #1 valve on the backflow then the other buildings will have to lose water during repair.

Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

Thrust Block Volume Much Greater than Shape?

8/7/2024

6 Comments

 
MeyerFire has a great thrust block calculator that appears to match NFPA 13’s annex/appendix exactly.
https://www.meyerfire.com/blog/a-new-thrust-block-calculator-part-i
 
How can the thrust block volume fit within the dimensions of the thrust block?
 
The default entries, for example, give a thrust block volume of 57.8 ft³ (NFPA 13 Equation A.6.6.1c), a base height of 2.2 ft, and a base width of 4.27 ft.  This meets the bearing area required by the equations.
 
NFPA 13, Figure A.6.6.1(b) gives the angle between the base of the thrust block and the pipe as 45°. This makes the thrust block a pyramid shape but ends with a pipe instead of coming to a tip. The Figure shows both vertical and horizontal angles as 45°, but that wouldn’t work unless the height and width are equal.  If 45° is the minimum angle, then the width of 4.27 ft would control the distance from the base of the pyramid to the pipe. If each side has a 45° angle, this distance would be half the width or 2.135 ft.  These dimensions can be used with the pyramid volume formula to give another method to check the thrust block volume.
 
The pyramid formula is V = L*W*H/3, which gives a volume of 6.7 ft³.  This is very different from the NFPA equation result.   Even if the thrust block was poured as a cube, its volume would be V = L*W*H, which is 20 ft³ -- still much smaller than the NFPA value. – I am counting the tip of the pyramid, which is part of the pipe, not the thrust block. It would be more accurate to exclude the tip, lowering the required volume slightly, but it would be harder to calculate.
 
If the pyramid were 57.8 ft³ with a bearing area of 2.2 ft by 4.27 ft, then it would need a distance from the pipe of 18 feet.
 
I think there is something wrong with Equation A.6.6.1c in NFPA 13.  It doesn’t make sense that it cancels the thrust force with the weight of the fill material. If you could use some incredibly dense fill material (pretend fantasy fill that is 8670 lb/ft³), then the thrust block volume would be 1 ft³ by that formula, but how is that small thrust block volume going to transfer the thrust forces onto a large enough soil surface? 
Picture
The weight of the thrust block material should not be related to calculating the volume of fill material required.
 
Another issue I see with the equation is that it is suddenly using T = P*A*sin(theta) while all previous formulas were using T = P*A*sin(theta/2). 

Why did the angle change for this formula?

Thanks in advance for any insight you could shed on the difference in volume versus shape with the NFPA formulas.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Does Pipe Under Walkway Need Depth of Cover?

5/29/2024

9 Comments

 
We have a scenario where the fire riser will be installed after the building is completed.

If the pipe is located below the pedestrian walkway area, is this required to comply with NFPA 13, 2022, (6.4.2.2.2 In locations where freezing is not a factor, the depth of cover shall not be less than 30 in. (750 mm) below grade to prevent mechanical damage. [24:10.4.2.2.2])?

See the attached sketch. If yes, what is the possible solution?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
9 Comments

Is a 4"-6" Discharge OK for Sprinklers & Hydrants?

5/17/2024

4 Comments

 
Can a 4" pump with 4"-6" discharge fitting be used on a private 10" combination line (fire suppression and hydrants)?

NFPA 24 Section 13.1 states that no line less than 6" shall service a hydrant. But does the fact that NFPA 20 Section 4.16 allows the 4"-6" discharge fitting as part of the pump assembly overrule this?

Thanks in advance.

​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Maximum Length from Hydrant to Water Main?

5/3/2024

7 Comments

 
Hi all, what is the maximum length of the connection from the hydrant to the fire water main?

​NFPA 24 mentions that the minimum size is 6" but couldn't find anything related to the pipe length. Thanks


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Limit for Length and Size for Underground Loops?

4/26/2024

11 Comments

 
Typically when I work on campus/multi-building systems, I am using a single underground main and splitting off to each building. Since you don't have to consider a multiple building fire problem, we have typically worked on the hydraulically most-remote building for underground sizing and use wall PIVs to offer individual building shutoffs, with FDCs on the individual buildings.

I'm getting challenged on "what allows this in code?" It's mostly a question of - where is the limit on how long a loop can be?

I'm looking at this from a sprinkler design perspective and whether each individual building's sprinkler system is able to perform hydraulically.

Is the limit for the length/layout/sizing of a campus underground loop simply the more demanding of Fire Flow or sprinkler system feeds?

Is there a code basis for this?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

When is PIV Not Subject to Mechanical Damage?

3/8/2024

8 Comments

 
According to NFPA 13 2022 Section 16.9.8.2 it is to our discretion what we consider a location " where they are not subject to mechanical damage?

When installing a Post Indicator Valve, what do you consider "not subject to mechanical damage?"

Where is the line drawn, so to speak?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Why is Fire Pump Pulling the Underground Dry?

3/6/2024

19 Comments

 
Had a review comment come back and needed to clarify.

I have a 14-inch city main with an 8-inch tap to a backflow in a pit. It then runs to four hydrants, and then turns into the building supplying a fire pump.

The flow test at the hydrant near the tap (#1 on image below) was 49 psi static, 47 psi residual at 920 gpm.

The flow test at a hydrant nearest the building (#2 on image below) was 49 psi static, 39 psi residual at 750 gpm.
Picture
The 95 psi @ 1,500 gpm pump in the building is running the underground dry. The plot curve shows 20 psi at 2,100 gpm, however the pump rep said he barely got 500 gpm at 9 pitot and had to shut it down as the gauges went below 20 psi and air was starting to come out of the 2-1/2" hose valves.

This is a mystery to us - we have five different flow tests all ranging from 750 gpm to 1,060 gpm at 40-32 psi residual.

Why would the pump be pulling the underground so low?

They checked all the valves and rebuilt the backflow in the pit. Water meter is good as well (per the utility department). Looking for suggestions. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
19 Comments

Can Floating Dock with Hose Valves Use PVC?

3/1/2024

13 Comments

 
Can a floating dock standpipe with hose valves in the ocean be ran with PVC pipe?

NFPA 307 doesn’t go into detail about materials used but reverts back to NFPA 20, 22 and 24. This is in Florida. The AHJ wants it full of water so I have to issues, it’s too heavy to mount on the side of the dock, it’s not very big and it will be in the water or very close with high tide, so corrosion is inevitable.

Is there anything stating Schedule 40 or 80 PVC is listed or acceptable for such use?


​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe​
13 Comments
<<Previous
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT