MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Main Drain, Placards at Each Floor Control Valve?

5/27/2024

4 Comments

 
Consider a multi-story building with floor control valves (FCV) at each level.

Is a main drain test required to be performed at each of the floor control valves and tagged at startup?

Is a hydraulic placard required at each floor control valve? If so, is the base of riser pressure to be the pressure at floor control valve or at the base of riser in the sprinkler riser room?

Is it allowable to hang each of the floor's hydraulic placard together at the main riser in the sprinkler riser room?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Glenn Berger
5/27/2024 08:24:37 am

"Main Drain" is located at the building's sprinkler system main riser. As such this test is only required at this one point. The drains at each floor control valve shall still be operated.

Hydraulic Placard located at each floor - Yes - The water pressure indicated shall be carefully documented for if it is a the floor control valve connection or at the base of the riser.

Your question did not state that each floor had the same layout, occupancy, or any type of configuration.

Is it "allowable to hang each of the floor's hydraulic placard together" - I seen it both ways and preferred that they be hanged in both locations to properly allow system information to be present especially if it is out of the public reach.

Reply
Jack G
5/27/2024 07:34:08 pm

For my own preferences I do a printed vinyl sticker at each floor control valve with machine print.
Standpipe valve number with flows and pressure(s)— top of standpipe in vinyl and metal.
And then do everything again in metal at the pump.
I like to sell a 5 year after I install, but if working for a contractor the owner usually buys that out.
For some reason your signs seem to disappear, a couple years down the road when you get the inspection back. Also furnish a thumb drive for owner.

Reply
Matthew Mueller
5/28/2024 08:12:30 am

The question of placard placement is an important question, and one that has been interpreted in different ways. We recently asked the NFSA's "Expert Of the Day" this very question and their response was as follows: "No, the data plate does not need to be at each control valve if they are not different design criteria. NFPA 13, 2019 Section 28.5.2 States that the sign shall be placed at the alarm, dry, preaction, or deluge valve supplying the corresponding hydraulically designed area. If the entire mall is fed from the same watersupply and the design criteria is the same throughout, only the main riser would require the sign. Note that the 2022 edition of NFPA 13 requires a dataplate at all system risers. A riser is defined as aboveground horizontal or vertical pipe between the water supply and mains, cross or feed that contains a control valve, gauge, drain and alarm device.

We are using this interpretation to reduce the sheer number of inspection deficiencies that were being reported if they were required at each valve even if the design is the same throughout.

Reply
Dan Wilder
5/28/2024 08:44:27 am

13-22' Ed. - Every drain valve as there is no allowance to only test a single valve for Acceptance Testing 29.2.3.4

25-23' Ed. - A single main drain test is required only, additional testing of every drain valve is not required unless it has a maintenance issue.
13.2.2.1 /13.2.2.2-

13'-22 Ed. 29.4.2 (newer section) - Hydraulic placard located at every system riser/floor control valve assembly unless the AHJ allows an alternate location.

25'-23 ed. 5.2.5 requires that the placard is installed and legible (assumed that its location is per NFPA 13 so depending on that edition, it may or may not be clear as to specific locations).

I would say that the BOR location is the control valve for that system or floor. Standpipe would be at the main control valve (not the isolation valves) that feeds the system

Where to hang the sign is called out to be at the control valve (29.4.2 section above, or at least the valve that coincides with the hydraulic area), again unless the AHJ allows an alternate location.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT