MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Annual Inspection for Single Room Sprinkler?

12/16/2024

1 Comment

 
Is an annual sprinkler inspection required for a storage room with a height of less than 12' and a room size totaling 100 square feet with a single sprinkler head installed?

I have been looking in NFPA 13 and 25 but I'm not sure I'm looking in the right direction for this ruling. Please help, thanks!

​Moderator's Note: So sorry crew, missed the post yesterday so following up with two today. Thanks!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
1 Comment

Any 5-Year Testing for Manual Wet Standpipe?

12/4/2024

3 Comments

 
What is involved in a 5 year inspection/test for a manual wet standpipe?

I see in NFPA 25, 2017 edition that manual wet standpipes are not required to be flow tested or hydrotested when part of the sprinkler system.

So my question again is are there any specific requirements for 5 year testing for manual wet standpipes?

​Thank you all!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Hydrostatic Test Req'd for Adding Few Sprinklers?

12/2/2024

14 Comments

 
Is a hydrostatic test required for adding two new sprinklers to an existing system?

For this, assume it can be isolated, and the local jurisdiction refers to NFPA 13 - 2016 Edition.

This is the most referenced code outside of the obstruction rule, and is the most common I've seen interpreted differently amongst professionals.

Reference Chapter 25, Section 25.2. What is your "threshold" for triggering a hydrostatic test?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments

20-Year Sprinkler Testing for Renovated Building?

11/22/2024

10 Comments

 
Per 5.3.1.1.1.3, NFPA 25, 2014 Edition, states that sprinklers manufactured using fast-response elements that have been in service for 20 years shall be replaced or representative samples shall be tested and then retested at 10-year intervals."

What is the common practice for doing a
20-year sprinkler test sample on a multistory office building built 20 years ago that has undergone numerous tenant renovations, where sprinklers have been replaced and added throughout the years?

My thoughts would be that maybe the common areas would have original sprinklers, but what would be the best way to approach this?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

5-Year Required for 1.5" Class II PRVs in NFPA 25?

11/12/2024

3 Comments

 
In NFPA 25 (2013), Table 13.1.1.2 directs us to the Testing requirements for Pressure-Reducing "Hose connections," with a frequency of 5 years.

Does this apply solely to 2.5-inch PRV Hose Valve outlets, or does it include the 1.5-inch PRV Hose Valve outlets on Class II (and Class III) systems as well?

Can't seem to find specifics on that. Thank you.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

How to Fix a Flowswitch that Cycles?

10/8/2024

6 Comments

 
We have an instance of "flowswitch cycling" on a new wet-pipe system. The RPZ backflow is thought to be causing the flow switch to fluctuate and, therefore, not get us the flow alarm in a timely manner or at all.

We have opened the manual high point air vent and flowed for several minutes with no success.

Has anyone had this
or found a solution to it?

Potter has a technical bulletin on this but does not go into detail about how to resolve it.

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
6 Comments

What is Best Practice for Testing Forward-Flow?

10/7/2024

9 Comments

 
Regarding forward-flow testing, I have read that a main drain (if sized appropriately) can be used in place of other means. This was in the 2016 NFPA 13 A.8.16.2.4.2, but I cannot locate it in the 2019 version.

With that, what is the best practice for testing at the time of system acceptance?

Without being able to use a hose monster, is the main drain test sufficient to ensure the backflow fully opens?

Other than hydraulic calculations, how is it proven that we have an acceptable result?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

What is "Significant" Water Delivery Delay Time?

9/30/2024

6 Comments

 
NFPA 25 states that a 3-year full flow test for a dry sprinkler system should show no significant delay in water delivery time from previous tests.

What is considered a significant delay?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Concern with Draining Standpipes Back to Tank?

9/3/2024

4 Comments

 
We're designing a small footprint high rise with 2 stairs/standpipes, and 3" drains in the stairs for floor control valve drains and testing/verifying hose valves.

Primary water is supplied from a vertical turbine pump and tank. Local codes don’t allow direct outdoor drains so it’s either into the tank or into large hub drains.

Owner is very ‘green’ and looking for ways to reduce water usage.  We’ve already got the fire pump test flows back into the tank.  We’re considering flowing the stair’s drains into a hub with a bypass into the tank -- hub for system draining, tank for PRV and flow switch testing. 


Is it advisable or preferable to run these stair drains back into the tank?

​Concerns include flowing black, stinky water into the tank and possibly adding pipe scale into the tank


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Installer/Operators: Do Automatic Air Vents Leak?

8/26/2024

11 Comments

 
Can any installers or maintainers provide insights into automatic air vents in fire sprinkler systems?

In your experience, do these vents ever leak water while operating?

Trying to understand why specifications often require these vents to be piped to the exterior. Although manufacturers claim that only air is released, I’m curious if they occasionally sputter or drip water and whether this has caused maintenance issues.

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Re-Evaluate Supply with Replacement Fire Pump?

8/23/2024

9 Comments

 
We have a number of apartment buildings, 4-5 stories in height, with fire pumps serving the standpipes coming towards their end-of-life.

Is there a code requirement to re-evaluate the water supply when replacing a pump in a like-for-like scenario?

​Of course, this building has no existing fire protection records or placards to reference. Thanks!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Horizontal Drum Drip an Impairment in NFPA 25?

8/2/2024

9 Comments

 
I recently observed an existing drum drip assembly installed in a horizontal orientation at a low point of a dry system. Although I would never design or install a drum drip in this fashion, I do not see any specific language in NFPA 13 regarding the installation orientation of a drum drip. General knowledge and understanding tell me it must be installed vertically. The only language I can use to identify the acceptable installation orientation is manufacturer cut sheets for pre-assembled drum drip assemblies.

Has anyone come across this in the past?

Would you consider this an "impairment" if conducting an NFPA 25 quarterly inspection?

​I look forward to hearing everyone's input.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Company License to Perform Testing, Inspection?

7/11/2024

10 Comments

 
Can a company who is licensed in the installation of fire sprinkler systems perform the acceptance testing of the system or does that company need to be licensed to perform testing and inspections?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

When Does Exterior Pipe Rust Get a Red Tag?

7/1/2024

3 Comments

 
When should a red tag be issued for exterior rust on a sprinkler system?

The rust has heavy flaking especially around the weld-o-lets. NFPA 25 leaves a vague interpretation and I just need something a little more concrete to make sure we are covering ourselves. Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

5-Year Hydro (NFPA 25) Apply to Steel with CPVC?

6/4/2024

10 Comments

 
Per NFPA 25 there needs to be a hydrostatic test of fire department connection pipe every 5 years. It does specify pipe material that are exempt (CPVC).

Should I recommend a hydrostatic test of the 2-inch FDC feed if the pipe is walled in and connected to the CPVCc before and after the check valve?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Main Drain, Placards at Each Floor Control Valve?

5/27/2024

4 Comments

 
Consider a multi-story building with floor control valves (FCV) at each level.

Is a main drain test required to be performed at each of the floor control valves and tagged at startup?

Is a hydraulic placard required at each floor control valve? If so, is the base of riser pressure to be the pressure at floor control valve or at the base of riser in the sprinkler riser room?

Is it allowable to hang each of the floor's hydraulic placard together at the main riser in the sprinkler riser room?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Fire Pump On or Off During Main Drain Test?

5/24/2024

10 Comments

 
When conducting main drain test on a sprinkler system with a fire pump, should the pump be on or off?

AHJ generally wants the pump to be on in this area. Thanks.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Forward Flow Still Required with Fire Pump Test?

3/28/2024

4 Comments

 
Would we still be required to conduct a forward flow test if we have a fire pump downstream and it's tested annually?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Why Would Fire Pump Over-Perform at 150%?

2/5/2024

19 Comments

 
I have a unique quandary that I haven't run into before. We have an overperforming fire pump.

It was factory tested, we have a factory performance curve of 68 psi churn, 52 psi at 500 gpm (100%), and 35 psi at 750 gpm (150%).

Once it was field installed, we were 1-3 psi over on Churn, 50%, and 100%, but +10 psi on the 150%. We had a net pressure of 45 psi at the 150% test when, based on the factory curve, the net should have been 35 psi. 

We checked the nameplate for the match, nameplate for the expected pressure at 150%; they all match. The supply for the test in the field got pretty low (about 25 psi suction at 150% flow). 

The only unique thing I can see about this setup is that we have a very tight room and had to meet a military spec to flow through the flowmeter and both run outside as well as back to the recirculation. As a result, the path from the pump discharge to the outside has to navigate through nine (9) elbows in order to get enough clearance upstream and downstream for the flowmeter in this very tiny pump room.

Could a test header with that many bends be affecting the net pressure on the 150% test? 

Is this considered a failure?

As this is military, it'll be by the book and I'm concerned that an overperforming pump might set up future tests for failure if I can't identify why it would be overperforming at the 150%. 

Thanks in advance!

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
19 Comments

Dry Sprinkler System Affected by Freezing Temp?

2/1/2024

9 Comments

 
Would a dry fire suppression system be affected by freezing temperatures?

I work at a facility that had a glass sprinkler break, no contact or anything, and of course the water came out as it should.

We've had freezing temps for the last few days, but where it broke was in an 74 degree room, so not frozen.

Any ideas on why this would have happened?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Allowed to Run 4 Diesel Pumps Simultaneously?

1/26/2024

15 Comments

 
We have a project and have gotten into an internal debate. The project has four diesel fire pumps in one pump house. 

During testing, are we allowed to run all four at the same time?

Or do we need to run each separately as we do normally to reduce the chance of blowing out a main?

Anyone have insight on this?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
15 Comments

Deluge Full-Flow Test Count for 5-Year Internal?

12/7/2023

9 Comments

 
Does the requirement under NFPA 25, Chapter 14 for a 5-year internal pipe inspection apply if the system is an open sprinkler/nozzle deluge system?

The system is flowed annually and I believe that this full flow should meet the requirement in lieu of a 5-year internal pipe inspection. 

Am I correct?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Hydrostatic Test In Lieu of Dry Pneumatic Test?

12/5/2023

8 Comments

 
For the acceptance testing of a dry pipe sprinkler system, is a 24-hour 40 psi pneumatic test required, or will the 200 psi hydrostatic test alone suffice?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

FDC Used for Forward-Flow and as Drain Outlet?

11/20/2023

13 Comments

 
A fire department connection can be used with a bypass to facilitate a forward flow test of the backflow preventer as described in NFPA 25 Annex A.

Is there anything prohibiting the FDC from being used as a drain outlet, as well?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments

Cause for Low Res. Pressure in a Main Drain Test?

10/31/2023

11 Comments

 
What would cause a 10% reduction in the full flow residual pressure from the current main drain test, when compared to the original acceptance test or previously performed tests?

If the original acceptance test or previously performed test information is not available, then the residual pressure on the current main drain test must be within 5 PSI of the design/demand pressure.

What would cause a decrease over time?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
<<Previous
Forward>>
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT