MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Exterior Window Allowed on Fire-Rated Stair?

7/8/2026

9 Comments

 
Is a window allowed in the exterior wall of a fire rated egress stair enclosure?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Do Condo Unit Doors Need Self-Closing Hinges?

12/22/2025

7 Comments

 
I have a 10-story condo building with 70 units. Each floor has 7 units, and the unit doors open to an open-atmosphere walkway with two exit stairwells at each end.

Do each unit door that swings into the unit need self-closing hinges?

​Thanks in advance for your help or guidance with this.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

How is 10% of Area Used in Accessory Occupancy?

9/1/2025

1 Comment

 
My question is about small assembly occupancies and the total area of accessory occupancies per floor, with the 2021 IBC being the governing code. A small assembly occupancy can be considered part of the overall building occupancy if it is less than 750 sq ft and is accessory to that other occupancy (Section 303.1.2(2)).

My confusion comes when applying 508.2.3, which says that aggregate accessory occupancies cannot exceed 10% of the floor area.

Is the small assembly occupancy still considered accessory, or is it part of the overall occupancy?

Two scenarios have come up recently with multiple architects having differing interpretations. Assume the main occupancy is R-2.

1) Multiple small assembly occupancies scattered throughout the floor, that when added together, make up more than 10% of the floor area.

Is the 10% in aggregate or is it per small assembly occupancy?

One line of thought is that 303.1.2(2) is applied to each small assembly occupancy, meaning that they're all considered R-2.

2) A small assembly occupancy that is less than 10% of the floor area, but other accessory occupancies (storage for example) push the total accessory area over 10%.

Does the small assembly occupancy not contribute to the 10% since it's considered part of the overall occupancy?

Or does the small assembly occupancy + the storage occupancy need to be under 10%?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
1 Comment

Use Armored Cable for Controller to Pump?

7/31/2025

5 Comments

 
Is it permitted to install fire pump cables, from the controller panel to the motor, through a cable tray using armored cables, at a height of about 4 inches (10 cm) above the finished floor level?

Are there any code or standard requirements that affect this?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

FA & Occupancy Type for a Trailer Near Building?

7/28/2025

4 Comments

 
We have a project where there is one large building that has many different activities throughout. There is also a trailer that is not connected to the building by walkway or anything except some plumbing for what I believe is a restroom.

This trailer is maybe 2-4 feet away from the larger main building, and the activity being done in the area closest to this trailer is woodworking/carpentry.

I am trying to determine how the trailer should be classified to determine the requirements for a fire alarm system. I have gone back and forth between NFPA 101 and the IBC, but I am either overthinking or underthinking the scenario.

I would just like to ensure I understand the criteria correctly because these two buildings do not share exit access or an exit, but may share an exit discharge.

Would it be correct to classify the trailer as an existing business occupancy and look at Chapter 39 of NFPA 101?

If I arrive there and look at Section 39.3.4.1, it appears that the three criteria listed there, which the trailer would not meet, result in a fire alarm system not being required.

This does not sound correct but I could not piece together why. A

ny help would be much appreciated! Thanks!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Egress Speed for NFPA 2001 Egress Time Study?

4/9/2025

6 Comments

 
NFPA 2001, Standard on Clean Agent Fire Extinguishing Systems now require an egress time study to show that the design limits exposure to halocarbon agents is no longer than 5 minutes, like FK-5-1-12 (NOVEC 1230), HFC-227ea (FM 200).

This comes from 2018 Edition Section 1.5.14, 2020 Edition Section 4.3.4, and 2022 Edition Section 4.3.4.

Exposure time for inert gas agents will depend on the oxygen levels within the space or room. Concentration below 43 percent shall be permitted where exposure is no longer than 5 minutes. Concentration between 43 and 52 percent shall be permitted where exposure is no longer than 3 minutes.

The annex of NFPA 2001 tells us to review the NFPA Handbook and the SFPE Handbook for more information.

Is anyone doing these calculations, and if so, what exit flow, movement speed, and reaction time would you consider appropriate for spaces using these systems?

​Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Can "Refuge Area" Include Area Open to Outside?

3/27/2025

3 Comments

 
We're looking at "refuge areas" per 2024 IBC (not to be confused with "areas of refuge" in NFPA 101) within smoke compartments to satisfy the requirements for smoke barriers in Group I-1, Condition 2 in the IBC.

Can the "refuge area" be calculated to include portions of the floor/smoke compartment that are open to the exterior of the building?

For example, an occupant load of 80 persons receiving care on the fifth floor of a Group I-1, Condition 2 occupancy would require a minimum of two (2) smoke compartments to be provided (420.6).

Each smoke compartment must be provided with a refuge area sized to accommodate 15 sqft/care recipient plus 6 sqft/other occupant and "areas or spaces permitted to be included in the calculation of the refuge area are corridors, lounge or dining areas and other low-hazard areas" (420.6.1).

If each side of the smoke compartment is provided with an exterior lounge/amenity area, may this be used as the "refuge area" to meet the minimum required square footage?

Picture
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Is Large Circulation Space a 'Corridor' in NFPA 101?

2/13/2025

6 Comments

 
Subject: Two story convenience opening separation from corridors.

NFPA 101 (2021 edition) Section 8.6.9.1 permits convenience openings for two adjacent stories. But, these convenience openings shall be separated from corridors (requirement #3) and
further states that separation should be by a smoke partition (requirement #5).

How do you define a corridor versus an open floor area or lobby per NFPA 101, since no definitions are given within the code?

Jurisdiction is required to follow NFPA 1 and NFPA 101.

For example, a building has a large assembly space on the second floor. All doors from the assembly space lead to a ~40'-0" wide circulation space (+200'-0" long in the other direction). To reach the building exit stair, occupants from the assembly room must traverse the 40'-0" wide circulation space. Within this circulation space is a ~20'-0" x 40'-0" vertical opening that connects the 1st and 2nd floor.

Should this circulation space be considered a corridor
, and should the vertical opening be prohibited from being classified as a convenience opening without a smoke partition separating from the corridor?

Or is the 2nd floor space to be considered an open floor area, with exits immediately accessible in different directions (NFPA 101 7.5.1.1.1) and not consider it a corridor?

​The width of the circulation space seems too wide to be defined as a corridor but NFPA only provides minimum width requirements for corridors, and no maximum width for a space to be considered a corridor as far as I can determine.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
6 Comments

Are Pictogram Exit Signs IBC & IFC Compliant?

10/23/2024

6 Comments

 
As many/most of us know, there's an internationally standardized pictogram (symbol) for exit signs that's common in many countries worldwide. However, it's not yet common in the US, likely due to what appears to be a misconception that the IBC/IFC only allows "EXIT" lettering.

IBC/IFC Section 1013.5 requires internally illuminated exit signs to be listed to UL 924. (There's a different section on externally-illuminated exit signs, 1013.6.1, that specifies "EXIT" lettering, however, the vast majority of exit signs are internally-illuminated and therefore not subject to anything under 1013.6 due to that section's scope clause.)

UL 924 was revised a while back to allow the internationally standardized pictogram, including in lieu of "EXIT" lettering. (see section 42 of UL 924) Therefore, my impression is that a UL-listed internally-illuminated exit sign that uses the internationally-standardized pictogram complies with the IBC/IFC. (There are such products currently on the market.)

Are UL-listed internally-illuminated exit signs using the pictogram in compliance with IBC/IFC?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
6 Comments

Why is 90-Minute Door Allowed in 2-Hr Barrier?

10/21/2024

7 Comments

 
Does anyone know the historical context of why a 90-minute door is permitted on a 2-hour barrier?

Why the 30-minute difference?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Window Sprinkler at Ext. Area Assisted Rescue?

10/10/2024

6 Comments

 
The 2018 IBC, Section 1009.7 for Exterior Area for Assisted Rescue (EAAR) requires exterior walls within 10 feet to be rated 1-hour for exposure to fire from the inside.

​When a window is located within 10 feet of the EAAR, can it be protected with a window sprinkler system?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Occupancy for 2 Sleep Rooms in Office Building?

10/9/2024

12 Comments

 
What occupancy would you classify two sleeping rooms in an office building (otherwise B Occupancy)?

The area of the two rooms is 400 sf, and the area of the offices is 6,870 sf.

Will the rooms be R-2? Does the building need sprinklers as a result?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

When Does Common Path Stop for Wide Areas?

10/3/2024

6 Comments

 
I understand the definition of the "Common Path" from Section 3.3.49 in NFPA 101, but within the examples it is up to the point when you reach a corridor and have the two exit alternatives.

In a case like the one in the image shown below, the orange area is very wide, or open space, up to where they would measure the common travel distance.

At what point does the path of common travel stop in a scenario like this?

​What is that threshold?

Picture
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Exit Stair Required to Have Solid Treads/Risers?

8/22/2024

8 Comments

 
In NFPA 101, is a solid riser and a solid tread required for an Exit Stair?

See the image below that is metal tread but wouldn't have solid risers. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
8 Comments

Corridor with a Non-Exit Door at End a Dead-End?

6/18/2024

7 Comments

 
We have a sprinkler protected facility where we have a corridor that exceeds 50-ft in length.

At the end of the corridor is a door that leads to the apparatus bay. It's not a means of egress leading to an exit (higher hazard on the other side). The required means of egress are at other locations in the facility.

Is this considered a dead end corridor under NFPA 101?

In all the examples I've found on the topic, the end is truly dead-end with no means of exiting.

What's your take on this? 

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Address FA & FP for Fixed Airplane Inside Facility?

6/14/2024

10 Comments

 
We have an airline opening a training facility in our jurisdiction. The building is fully sprinklered and has a fire alarm.

They wish to install a static airplane fuselage for training airplane cabin personnel. This would be a functioning fuselage with standard airplane doors with ramps.

Has anyone had an experience with this?

This is a fully sprinklered building so our thinking is the fuselage needs sprinkler coverage inside. Is this correct?

This building has a fire alarm system so our thinking is the fuselage needs notification devices. Is this correct?

The fuselage doors do not meet the code requirement for egress doors (locks, swing, etc), how is this addressed?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Handrails Required on Roof Due to Standpipe?

6/22/2023

11 Comments

 
Is it a requirement to have a 42-inch handrail on the edge of the building, due to the standpipe hose connections and this needing to be accessible for the fire department use?

​If it's required, it seems that handrails could apply under IBC 2018 Section 1015.6.
Picture
Thanks in advance.

​​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Does EIFS Trigger Sprinklers on Exterior Corridor?

6/14/2023

8 Comments

 
We have a multistory hotel building with the rooms opening to an exterior corridor. There is Exterior Insulation Finish System (EIFS) along the walls of the exterior corridor.

NFPA 13 (2022), Section 9.2.3.3 allows omission of sprinklers from exterior exit corridors where the exterior wall of the corridor is at least 50% open and where the corridor is entirely of noncombustible construction.

It seems from research that EIFS is considered combustible and would require sprinkler protection along the exterior corridor.

Has anyone done more research on this or has this come up before for other projects with EIFS in the exterior corridors and ultimately required sprinkler protection?

​Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Does Stair Structure Have to be Fire-Rated?

6/8/2023

7 Comments

 
If a stair structure is supporting the fire barriers that enclose the exit enclosure, does the stair structure have to be fire rated as well?

Looking specifically at IBC 2018 Section 707.5.1 and NFPA 101 (2018) Section 7.1.3.2.

If there is a fire inside a stair, the means of egress is no longer usable and at that point are you protecting the interior of the building from the fire inside the exit enclosure?

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Treat Wellness Room as Residential Occupancy?

5/15/2023

17 Comments

 
A lot of office buildings and public transit depot buildings are being designed with "quiet" or "wellness" rooms for tired employees to take a break and "rest," leading a lot of AHJs to ask if these rooms are R occupancies.

The designed use is not a sleeping room and many clients "prohibit" sleeping but everyone agrees that it could be used as a sleeping room.

Typically they're size for 1-5 people and have lounge chairs (no beds) so they fall under the accessory use category to the rest of the building. For example, assume a multi-story office building where each floor has one of these rooms, less than 500 square feet, no beds just chairs, room is entirely open inside.

How would you treat these rooms and how would you address the requirements for corridors in the building assuming its a sprinklered building?

​Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
17 Comments

Does Egress Apply to Car-Stacking Garage?

4/25/2023

8 Comments

 
Is there an egress requirement for a garage structure that only houses the car stacker, with 10 bays and 3 levels?

What would a code path be for or against such a requirement?

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe

8 Comments

Feature Stair Subject to Means of Egress Reqm'ts?

1/31/2023

4 Comments

 
I understand that Chapter 7 of NFPA 101 applies to stairs on the means of egress.

However, in the case of a feature stair, does the same dimensional requirements and handrails on both sides still apply?

In theory, should a person be on the feature stair when the fire alarm activates, they would need to traverse the stair to escape and it therefore forms part of the means of egress?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Requirements for Two-Way Door Swing?

12/21/2022

10 Comments

 
​In the corridors of an apartment building (wrap) there are fire doors that are double-egress pairs that are left-hand-reverse by left-hand reverse which follows the natural traffic pattern within the corridor.
Picture
However, there are also several right-hand-reverse by right-hand-reverse in the same corridor.

Is there a requirement one way or another on which direction these are supposed to be?

​I informed the project manager that the egress needs to follow the natural traffic pattern. I was curious about the different flow patterns of the doors so I researched the code but was unable to locate anything in the code regarding whether it was code or not, except for the AHJ. The county where I live also agreed with me but if someone out there knows if this is code please respond.

​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Does Every Occupant Need Access to All 3 Exits?

12/16/2022

7 Comments

 
A business occupancy we're working on has 550 occupants, and requires three means of egress per Section 7.4.1.2 (NFPA 101, 2018 Edition).

Section 7.5.1.1.1 indicates that egress shall be arranged such that each occupant has access to not less than two means of egress.

When the three means of egress are required per Section 7.4.1.2, does access to all three means of egress need to be provided to each occupant?

Or will providing access for each occupant to a minimum of two means of egress satisfy the code requirement?

​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Is a Knob on an Exit One or Two Operations?

12/14/2022

4 Comments

 
NFPA 101, Section 39.2.2.2.2* Door Locking to Prevent Unwanted Entry. Where approved, doors, other than those complying with 39.2.11.2, shall be permitted to be locked to prevent unwanted entry provided that all of the following conditions are met:
  1. The locking means shall be capable of being engaged without opening the door.
  2. The unlocking and unlatching operation from the egress side of the door shall be accomplished without the use of a key, tool, or special knowledge or effort.
  3. Egress shall require not more than one releasing operation.
​Question on Item (3) above: Is a knob on a (exit) door considered a 'one releasing operation' or two releasing operations (i.e., turning the knob to unlatch and push it to open the door)?

​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
<<Previous
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT