MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Duration for Secondary Containment in FM?

7/27/2026

4 Comments

 
I am working with a company storing Class IIIB liquids in plastic tanks. Tanks range in size from 2000, 3000, to 6100 gallons. 

We struggled to find a design that works in NFPA and therefore went with a .40/3,000 from FM DS 7-32; however, now we do not know what to do with the containment requirements. 

What should the containment duration be? 

Since they are plastic tanks, I have assumed they would all fail and would essentially need containment around each tank? 

​Thanks in advance. 


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Use AR-SFFF in Lieu of AFFF With NFPA 409?

7/24/2026

6 Comments

 
We are designing foam system for an aircraft hangar in accordance with NFPA 409. 

Is it acceptable to use AR-SFFF instead of AFFF with discharge density of 0.16 gpm/ft² (6.5 L/min/m²)?

AR-SFFF is not specifically mentioned in NFPA 409. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Spray Nozzles Spaced for Entire Oil Tank Wall?

6/23/2026

5 Comments

 
When a water spray system is installed for outdoor vertical fixed-roof oil storage tanks, is every point on the tank exterior wall required to be within the coverage of water spray nozzles?

Or is it sufficient to arrange a ring of nozzles around the exterior wall, so that the sprayed water flows down the tank wall by gravity to achieve effective suppression?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Extinguishers Type, Size for ASRS with Group A?

6/10/2026

2 Comments

 
The project consists of storing Group A plastics, Cartoned Unexpanded Plastics, in an ASRS (Automated Storage and Retrieval System).

The ESFR system has been designed accordingly.

What type and size of fire extinguishers are required for the space?

​Any direction and guidance is appreciated.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

UFC 3-601-02/NFPA 2001 Clean Agent Inspection?

5/8/2026

2 Comments

 
Clean agent system inspections for Department of Defense (DoD) buildings require UFC 3-601-02.

Should NFPA 2001 inspection requirements also be included?

Looks as if the UFC 3-601-02 guidelines are more stringent than NFPA 2001, correct?

Trying to sort this out, thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Adjust Oxygen Cylinders to NTP for MAQ Limits?

3/9/2026

4 Comments

 
I’m working on a fire protection assessment for a facility that stores multiple oxygen cylinders, and I need to verify whether the stored quantity exceeds the Maximum Allowable Quantity (MAQ) per control area per the IBC/IFC.

The facility has a mix of oxygen cylinders in different sizes, and I’m trying to determine the correct method to calculate the aggregate oxidizing gas quantity.

My main question is: When calculating total oxygen gas quantity, is it correct to standardize the volume to NTP (Normal Temperature and Pressure) before comparing with IFC/IBC MAQ limits?

Or should the calculation simply use the manufacturer’s stated gas content (e.g., cubic meters or SCF at normal conditions)?

The reason I’m asking is that if I convert pressurized gas to NTP volume, even a single “standard” 40-liter cylinder at 140 bar would exceed the MAQ for oxidizing gases and potentially classify the space as a High-Hazard Occupancy (H-2/H-3).

​I want to confirm whether this interpretation is correct, or if the code expects the use of the manufacturer’s rated gas quantity instead of a full expansion-to-NTP calculation. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Hose Allowance Req'd for Foam/Water Deluge?

2/26/2026

4 Comments

 
Is a hose stream allowance required for foam/water deluge system, in either NFPA 13 or NFPA 16?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Intrinsically Safe Pneumatic Mixer in Paint Booth?

12/24/2025

6 Comments

 
For a Paint Booth, mixing paint is taking place inside the space (1 gallon), and all applicable code items are in place, such as ventilation and sprinkler system (etc.).

If the mixer is pneumatic, is it required to be intrinsically safe?

Looking for code or standard reference guidance either way. Thanks in advance!

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

How to Dispose Non-Fluorinated Foam After Test?

8/12/2025

5 Comments

 
How do you dispose of foam after the test (non-fluorinated)?

​No one seems to know what to do with it. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Shutdown CRAC Units with FM200 Activation?

7/8/2025

5 Comments

 
I have an IT room with FM-200 under the raised floor and a pre-action sprinkler system at the ceiling. Contractors are replacing CRAC units.

Should the CRAC units be connected to the suppression system to shutdown upon activation of the FM200 system?

I have done 2 days of research with no answer. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Why Different IG-541 Concentrations by Brand?

7/2/2025

3 Comments

 
Why do the minimum design extinguishing concentrations for IG-541 vary among different manufacturers, while those for FM-200 remain consistent?

Additionally, the certification reports only indicate Class A and Class B fires, with no mention of Class C.

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Life Expectancy of a Clean Agent System?

6/25/2025

5 Comments

 
What is estimate life expectancy of a clean agent system before complete replacement?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Type of Fire Protection for Existing Server Room?

5/26/2025

8 Comments

 
We have an old server room. The server room is split into two side-by-side rooms separated by a wood stud wall with sheet rock covering. One server room side is approximately 15'x30'. The other side is approximately 30'x30'.

The ceiling is a 2 ' x2' square ceiling tile with insulation above. Above the ceiling is open to the warehouse.

The floating floor is suspended approximately 12". Wires for the servers are under the floating floor resembles a bird's nest. The wires also protrude through all four walls at various locations, but mainly between the floating floor and the concrete floor. The old sprinkler system needs upgrading.

We are thinking of a clean agent system, but the cost would be monumental. Moving the server room to a different location would also be cost-prohibitive. Both server rooms would require doors, walls, and ceiling modifications including rewiring all the server equipment for a clean agent system. We have a large amount of server equipment.

Does anyone have fire protection system(s) suggestion?

Does anyone have reference material for suggestions on installing different systems to provide to upper management?

What is the best method for providing a cost estimate for various types of systems?

Also, has anyone had luck with the misting system in server rooms?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Egress Speed for NFPA 2001 Egress Time Study?

4/9/2025

6 Comments

 
NFPA 2001, Standard on Clean Agent Fire Extinguishing Systems now require an egress time study to show that the design limits exposure to halocarbon agents is no longer than 5 minutes, like FK-5-1-12 (NOVEC 1230), HFC-227ea (FM 200).

This comes from 2018 Edition Section 1.5.14, 2020 Edition Section 4.3.4, and 2022 Edition Section 4.3.4.

Exposure time for inert gas agents will depend on the oxygen levels within the space or room. Concentration below 43 percent shall be permitted where exposure is no longer than 5 minutes. Concentration between 43 and 52 percent shall be permitted where exposure is no longer than 3 minutes.

The annex of NFPA 2001 tells us to review the NFPA Handbook and the SFPE Handbook for more information.

Is anyone doing these calculations, and if so, what exit flow, movement speed, and reaction time would you consider appropriate for spaces using these systems?

​Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Fire Protection for Dry Rooms for Batteries?

3/11/2025

4 Comments

 
How would you recommend protecting a dry room for battery operations, such as battery testing or packaging?

I've been designing these with dry systems but was curious if there are any codes to omit sprinklers, or if anyone uses clean agent systems?

If you use something alternatively, why do you go that direction?

Moderator's Note: Dry Rooms for batteries have less moisture to avoid corrosion and any chemical reaction for the batteries, which would degrade or reduce performance. Very low moisture is the key for a dry room for batteries.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Replacement Recommendation for NOVEC 1230?

2/26/2025

12 Comments

 
Where are we with the newest clean agents?

I'm running into an interesting scenario where the discussion of the phasing out by 3M of the NOVEC 1230 agent is coming up. I mentioned the competitors to NOVEC 1230 that we're aware of - FK-5-1-12 but they are interested in the next-gen stuff because they don't want to have to redo anything in the near future.

Does anyone have any experience with the Fluoro-K or any other newer, lesser used in the past but now have to look into agents?

I'm aware of Victaulic's Vortex and CO
₂ options, but I'm asking about chemical agents. I look forward to hearing your thoughts and experience.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

Difference of "Spray Room" vs "Spray Area?"

2/7/2025

5 Comments

 
Our facility is exploring constructing two large (7,200 ft²) facilities for media blasting and coating large steel structures.

The facilities have a ceiling height of approximately 40' and are enclosed via a large roll-up door on one end. The coating systems are categorized as flammable liquids.

There has been some internal debate on how to categorize these per the IFC - as "spray rooms
," which would require fire suppression, or "spraying spaces," which the IFC does not have a prescriptive requirement for fire suppression.

The commentary in the IFC notes that spraying spaces are typically "unenclosed", leading us to lean towards considering these spray rooms, even though they make up the entirety of the building versus a portion of it.

We've reached out to some of the local AHJs, who all seem to agree with the spray room determination. However, the builder of the structures has indicated that most of their installations have not required suppression, even when reviewed by the local AHJ.

​Is categorizing these structures as "spray rooms" the wrong application of the term?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

How to Address Control Areas in Old Buildings?

1/27/2025

8 Comments

 
We are a large metropolitan area with multiple universities that have been operating for decades with high levels of hazardous materials. They want to have separated control areas, but their building construction does not meet current requirements.

On one side we can only enforce the code that these were built to, which was BOCA or even no building code at the time, but on the other hand, there is a reason why control areas came about in the first place.

As they cannot easily upgrade the structure to meet 2-hr requirements, I am planning on just using equivalent level of safety through sprinkler protection and other factors, but was wondering if anyone had experience doing enforcement like this?

Is NFPA 45 enforceable here?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Does NFPA 30, 31, 37 Apply to Diesel Generators?

12/6/2024

6 Comments

 
What NFPA Standard(s) apply for two diesel generator tanks?

Two diesel generators (not emergency or standby), outside (but
have enclosures) with each diesel tank stored underneath, the tank is rectangular in shape and has ~5,000 gallons of diesel fuel.

Looking at the following code path; IMC Chapter 13 for fuel oil piping and storage and IFC Chapter 6--> 605.4 Fuel Oil Storage Systems --> storage above ground in quantities exceeding 660 gallons --> NFPA 31; OR IMC Chapter 9 engine and gas turbine-powered equipment and appliances.

Is this approach correct?

In reviewing both NFPA 37 and NFPA 31, both seem to be applicable
; however, when it comes to "outside aboveground tanks" of this capacity, they both reference NFPA 30 (Section 6.3.3 for NFPA 37 and 7.9.3 for NFPA 31).

So here's the main question - is NFPA 30 applicable here?

I base this on a few things:

1. NFPA 30 Scope section 1.1.2 item 9 - it says it is NOT applicable to "liquids in fuel tanks of... stationary engines" ; and
2. All the boundary and tank to tank separation requirements throughout chapter 22 are based on the diameter of the tank.

This leads me to believe this standard was not written for the type of tanks I have, but instead typical giant circular storage tanks.?

Any insight is greatly appreciated.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Radiation Affect Oxygen Concentration Level?

12/5/2024

2 Comments

 
I have 10+ years of experience in the design, specification, installation, commissioning and operation of oxygen reduction systems. ORS are designed to prevent fires from occurring.

The experimental work undertaken by Xin and Khan, FM Global etc is all concerned with fire suppression, using substantial fires (up to 33 kW) combusting in ambient conditions, and then trying to suppress the resultant fire.

There is a substantial variation in limiting oxygen concentration (LOC) with variation in the received level of radiation at the precombusted surface, which means that the LOC is not a fixed value.

Is there a recognition of the impact of the received level of radiation upon the LOC in the fire engineering community?

​Is there any data or study to back it up?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Does NFPA 30 Chapter 16 Apply if Under MAQ?

11/7/2024

9 Comments

 
I don’t often dabble in NFPA 30, so I have some specific questions regarding the protection of flammable and combustible liquids that I am having issues finding straight answers to.

I have a sprinklered general-purpose warehouse that stores flammable liquids in container sizes less than or equal to those indicated in NFPA 30 (2021) Table 12.8.1. The total quantities (MAQs) of these containers are also less than those shown in Table 9.6.1.

NFPA 30 (2021) Section 12.8.1 indicates that “The liquid-container combinations listed in Table 12.8.1 shall be permitted to be stored in a general-purpose warehouse without quantity limits if protected in accordance with Chapter 16."

An older version of NFPA 30 (2015) Section 12.8.1(1) indicates that if “the applicable provisions of NFPA 13 for 20ft high storage of Class IV commodities based on the storage configuration of the liquids” is used for protecting these containers, no additional protection criteria is required barring the storage arrangements are in line with the rest of the Section 12.8.

My questions are as follows (per NFPA 13 -2021):

1. If combustible liquids are stored in amounts under the MAQs stated in Section 9.6.1 (and IFC) are the additional requirements of Section 16 (NFPA 30) required, no matter what?

2. If combustible liquids are stored in container sizes less than or equal to those set forth in Table 12.8.1 (NFPA 30), are the requirements of Section 16 still required?

3. Will the storage of these commodities within liquid storage cabinets negate the requirements set forth by Section 16?

The bones of the matter is that I am having a hard time finding a section directly indicating that the requirements of Section 16 are not required. Most if not all sections I can find only indicate that Section 16 is to be used when something is stated.

​Thank you all ahead of time. As always this forum has always been a wealth of information.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

NFPA 30B Classification for Aerosol Spray Cans?

9/27/2024

3 Comments

 
How would you classify metallic spray cans containing aerosol Category 3, where 20.1% of the contents by mass are flammable (specifically, propane-2-ol, isopropyl alcohol, or isopropanol). The product Flash point exceeds 61 (23 – 60) °C (estimated value).

How should I define and handle this product under NFPA 30B?

Is it defined as Aerosol Level 3?

Thank you!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Area Per Unit of A vs. Floor Area Per Extinguisher?

9/23/2024

7 Comments

 
I have never quite understood the difference between the maximum floor area per unit of A and the maximum floor area per extinguisher in NFPA 10 Table 6.2.1.1.

If you are only permitted 6,000 sqft for a 2A (3,000 x 2) how does the 11,250 sqft limitation come into play?

Regardless
, with a 75-ft travel distance maximum, you rarely get anywhere near these limits, but I wonder if anyone knows more. Thanks in advance!

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Fire Suppression for Wood-Fired Pizza Oven?

8/19/2024

11 Comments

 
What are the requirements for fire suppression for a wood-fired pizza oven in a commercial application?

Does a wood-fired pizza oven require anything special, like a Type I hood would? 

If it does require some level of suppression - what's commonly provided? A high-temperature sprinkler on the adjacent fire sprinkler system, a feed from domestic water, or something else?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

How to Best Protect Room w/ Oxygen Cylinders?

8/12/2024

16 Comments

 
Is there a preferred method of protecting a room with the sole purpose of storing oxygen cylinders?

FM-200, NOVEC, IG, water mist?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
16 Comments
<<Previous
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT