Label Needed for NFPA 25 Gauge Re-Calibration?

1/30/2023

15 Comments

 
Section 5.3.2.1 of NFPA 25, Gauges shall be replaced or tested every five years by comparison with a calibrated gauge.

Is it required for us to provide a sticker on the gauge to indicate it has been re-calibrated by the 3rd party, or will a sharpie inscription on the glass of the gauge be sufficient to meet this requirement?

​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
15 Comments
Alex
1/30/2023 05:51:08 am

In short, I've seen gauges labeled by sharpie and small labels on the back of the gauge. As far as I am aware, both are acceptable. NFPA 25 is silent on the labeling methods. It tosses the requirement back to the manufacture. Code sections below.

Thanks


NFPA 25 (2020) 8.3.3.5.1 Gauges ,transducers, and other devices used for measurement during the test shall bear a label with the latest date of calibration.

3.2.1 Approved. Acceptable to the AHJ

A.3.2.1 Approved. ..... The authority having jurisdiction may also refer to the listings or labeling practices of an organization that is concerned with product evaluations and is thus in a position to determine compliance with appropriate standards for the current production of listed items.

Reply
Dan Wilder
1/30/2023 07:12:31 am

As I deal with inspectors & insurance agents requesting calibration paperwork on our pump test/flow testing gear....if a company I was paying did the calibration and marked sharpie on the gauge, it would be the last time I would use that company. If it is written on, it's typically for an installation date, some PSI number to indicate high/normal/low PSI (air gauges I see this on a lot), or other basic info.

You should not be providing anything on the gauge....that (should) fall onto the 3rd party to complete the calibration and provide the passing paperwork.

The company we use (National Calibration Inc.) provides a small metal sticker with a gauge number, date of inspection, and date of expiration. The paperwork includes (last I saw) a pic of the gauge (front & back with the passed calibration sticker), information on the calibration equipment & tech, results of the testing and all the company info for ISO certifications.

When not defined or clear within NFPA, Merriam-Webster definitions apply. Those definitions are also pretty grey in this case so I guess it comes down to what the AHJ is accepting of.

Reply
Dan Wilder
1/30/2023 11:03:41 am

Point of clarification, we do this for liquid filled gauges. Standard air/water gauges are just a replace and typically less costly going that route.

Reply
Anthony
1/30/2023 07:21:51 am

I'm of the opinion that if the gauge is even inspected that's a win. Dan's method would be best but I'll take a sharpie any day of the week.

Reply
Patrick Spillane
1/30/2023 08:30:54 am

The gauge does not have to be calibrated, just compared to a calibrated gauge. If it is calibrated, then a label should be provided by the calibration company. If just compared, then common practice is just to have a sharpie with the date of comparison.

NFPA 25 (2017) 13.2.7.2* Gauges shall be replaced every 5 years or tested every 5 years by comparison with a calibrated gauge.

Reply
Greg
1/30/2023 08:37:49 am

As an AHJ inspector, I would be thrilled with either, as this requirement gets ignored the majority of the time.

There seems to some confusion with the process, though. The idea is to install a test gauge on the three way valve, and compare it to the in-service gauge. You are not paying a gauge calibration company to test the riser gauge. You pay them to calibrate your test gauge, which is then typically labeled with a sticker including the test date, expiration date, and technician signature. Riser gauges are cheap, and sending them out would not be cost effective. When I was in the field we just replaced them at customer request most times.

Reply
Randy Kimbro
1/30/2023 08:51:51 am

As an AHJ this annoys me to no end. Gauges are cheap … replace them. We never accept a Sharpie marker date. Unscrupulous business owners just write a new date on them to save a few dollars. With NFPA silent on this, if the gauge is verified against another gauge per NFPA, we require the sprinkler inspection company to attach one of their inspection tags to each gauge and write a notation on the tag that it was verified, the date, and the technician number.

Reply
Ray Jackson link
1/30/2023 09:07:32 am

As Randy said, it is extremely less to simply replace the gauge. Gauges are not that expensive. Change them out and be on your way to the next problem.

Reply
Anon
1/30/2023 11:17:12 am

...Back in the day that's how I've got some of the coolest old gauges in my collection. It's good to be friendly with fitters.

Mike M link
1/30/2023 01:23:12 pm

Agree with Randy, our AHJ also accepts a sprinkler company inspection tag with appropriate information on each gauge.

Reply
Glenn Berger
1/30/2023 09:24:48 am

I would never trust a sharpie marking on any gauge. Like others have said, gauges are cheap and should be replaced.

Reply
Eric R
1/30/2023 09:53:44 am

Up till very recently I was in the "just replace them" boat, but we are currently going through the due diligence process to see if switching over to checking the gauges may be workable for us. Throwing away gauges that are only 5 years old seems pretty damn wasteful, especially when the standard for these gauges is so forgiving at 3% accuracy variance.

There are stickers you can buy that you can write the date of the inspection on, and stick to the back or upper rim of the gauge without obstructing the viewport.

One of the main reasons we are considering the switch is to get our field NICET guys more comfortable with handling NIST calibrated gauges. The need to use them on fire pump, standpipe, and hydrant testing is critical, so having an avenue for techs to get comfortable handling (these gauges and certs are expensive!) them could be extremely beneficial.

Also it creates less garbage in a landfill which we should all strive to do anyways.

Reply
Randy Kimbro
1/30/2023 10:27:39 am

I like the thought of being less wasteful but, and there is always a but, if YOU can buy those stickers, what stops a business owner from buying them and just slapping them on to save a few $$?

Reply
Anthony
1/30/2023 12:12:58 pm

The pain threshold for ordering those stickers is higher than just doing the inspection and buying the gauge. I'd expect someone to have fake heads (just cover plates) before they bothered going thought all that nonsense over a gauge.

Mark Harris
1/31/2023 06:41:11 pm

If a gauge is marked with a sharpie or sticker there would be or should be inspection paperwork supporting what was done. Owner should not be able to fake that. One thing I don't see talked about above is how do you "tag" a replacement gauge so the five year time starts over again?

Inspectors need to document their work and owners need to maintain records of their properties. We have come a long way in 30 years since NFPA 25 was introduced.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT