MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

How to Verify Flow for Underground Flush Test?

7/31/2020

9 Comments

 
Many sprinkler systems in our area (I'm a fire marshal) have aboveground pipe installed by a fire sprinkler installer and the underground installed by an underground pipe contractor. NFPA 24 requires a minimum flow rate from underground pipe in order to remove rock and debris from the underground pipe.

Many of the underground contractors simply open up the pipe and wait until there's consistent clear water and/or stop hearing the rocks ping around. There's no measurements taken for the underground flushing and when I ask for them to verify the flow rate I get blank stares.

Is there a way to tell just by static pressure in the area if opening up the pipe flange is enough flow to satisfy the underground flushing? Or is there a measurement I should be seeing to verify the flow rate? 

Thanks in advance.

​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments

Recommendations for FPE E&O Insurance?

7/30/2020

1 Comment

 
​E&O insurance; Many recognized brand names cover fire sprinkler layout, which is a re-branding of basic liability coverage for sprinkler installation contractors. The same policies will in most cases cover fire protection engineering design in instances of design-build contracts.

Does anyone know of a good underwriter of E&O policies exclusively for Fire Protection Engineering? One that is affordable, and also has a good claims payment history, S&P rating?

​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
1 Comment

Hazard Class of Recycling Plastic Solid Storage?

7/29/2020

3 Comments

 
We're designing a fire sprinkler system for plastic (Group A material, unexpanded polyethylene) recycling site. We are designing only for the depot area. There are raw materials stored as solid blocks up to ...We've raw material stored as solid blocks up to 12 feet (3.6 meters).

I am thinking this should be considered rack storage under NFPA 13 Section 16.2.1.2 (2016 Edition) for Protection Criteria for Rack Storage of Class I Through Class IV Commodities Stored Up to 12-ft (3.7m) in Height.

Am I wrong considering this? Note that compacted material will have a lower combustion propagation velocity than generic goods. Any ideas? Thanks in advance.

​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments

Sprinkler System Required for Dental Office?

7/28/2020

3 Comments

 
We have a new 3,300 square foot dental facility that is single story with a basement. Is a fire sprinkler system required?

​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments

Quick Response Reduction for Ordinary Hazard?

7/27/2020

9 Comments

 
NFPA 13 (2010 Edition) 21.23 Cleanrooms: 21.23.1.1 Automatic sprinklers for cleanrooms or clean zones shall be hydraulically designed for a density of .20 gpm/sqft over a design area of 3000 sqft.We have a wet pipe system utilizing quick-response sprinklers.

With an ordinary hazard density (.20 gpm/sqft) would I be allowed to use the quick-response design area reduction in Chapter 11?

​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments

PE Prep Series: Week 8 Leaderboard

7/27/2020

 
This week is the eighth of our 2020 PE Prep Series - it's 20-weeks worth of mini Fire Protection PE Exams. 

Each week we'll post the leaderboard here with the results of that week's exams. To see full leadership board and more details, visit the PE Prep Series page here.
Picture
The Leaderboard lists the top total scores for the most recent three weekly exams for PE Prep Series participants. 
See the entire scoreboard here.
Picture
Want to join in? It's not too late - the PE Prep Series is the ultimate PE Prep tool. It's a series of 1-hour, 10-question simulated PE Exams offered weekly with solutions immediately following each exam. Learn more here. ​​​​Every week of the series is retroactive so you can still test yourself with past week exams.

Hydraulic Calculations Required for Each Zone?

7/24/2020

13 Comments

 
I need an answer for a simple question. I am working on a large airport project expansion. I have a structure of 4 levels with 70+ sprinkler zones.

Is there an NFPA standard requirement stating that each area requires a hydraulic calculation on each system?

Each system is not prototypical.

​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
13 Comments

Standard(s) for Deluge Transformer Protection?

7/23/2020

5 Comments

 
Good morning, I have a project with a 60MVA outdoor transformer. We have a deluge valve system with wet pilot trim. 

Is there a standard requirement for protecting the transformer regarding k-factor, coverage area, and distances for a sprinkler/nozzle from the transformer?  

​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments

Code Requirements for Fire Door Pins & Plugs?

7/22/2020

0 Comments

 
Does anyone have much experience with fire pins/plugs as part of a fire door?

I came across some during a project to replace fire doors. There's a male and female component but ultimately a pin/plug is released at high temperature and goes into a hole to secure a pair of fire rated double doors.

My question is: are the pins just a substitute for a lower latch or is there some special code or regulatory driver for them?

​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
0 Comments

Quick-Response Reduction Apply to Preaction?

7/21/2020

5 Comments

 
I have a question that stems from NFPA 318 (Protection of Semiconductor Fabrication Facilities), Chapter 11, Section 11.1.4.2.


11.1.4.2* Automatic sprinklers for cleanrooms or clean zones shall be installed in accordance with NFPA 13, and shall be
hydraulically designed for a density of 8.15 L/min·m2 (0.20 gpm/ft2) over a design area of 278.8 m2 (3000 ft2).

For a clean room 11.1.4.2 mentions 0.20 gpm/sqft density over 3,000 sqft design area. We're considering quick-response standard-spray sprinkler coverage under section 11.1.4.4. The client is requiring a double-interlock pre-action system, so under NFPA 13 11.2.3.2.5 the remote area must be increased by 30% without revising the density. 

Can we omit the 30% increase in sprinkler operation under NFPA 13 11.2.3.2.3 since we are using quick response sprinklers?

​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments

Fire Pump Type with Underground Storage Tank?

7/20/2020

12 Comments

 
I’m working in the construction of 4-star hotel. The water storage tank is underground made from concrete and the pump room is located above the water tank. The designer specified the fire pumps to be vertical split-case type! In order to follow code, I proposed to install vertical turbine pumps instead of the specified vertical-split case.

The supervisor Engineer is insisting to follow the specification of the fire pump and pushing me to create an underground pump room in order to install the specified pump set.

Any recommendations to avoid this directive?

I have a bad flooding experiences with this this type of subgrade pump rooms.

​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
12 Comments

PE Prep Series: Week 7 Leaderboard

7/20/2020

0 Comments

 
This week is the seventh of our 2020 PE Prep Series - it's 20-weeks worth of mini Fire Protection PE Exams. 

Each week we'll post the leaderboard here with the results of that week's exams. To see full leadership board and more details, visit the PE Prep Series page here.

Please Note: The solution for Problem #7 of Week 7 used the Total Heat Release Rate to find the height of the flame tip. This is incorrect; the convective portion of the heat release rate (assumed to be 70% of the total heat release rate) should be used to calculate flame tip height. Those who answered "c" have been credited as having this problem correct:
Picture
The Leaderboard lists the top total scores for the most recent three weekly exams for PE Prep Series participants. 
See the entire scoreboard here
Picture
Want to join in? It's not too late - the PE Prep Series is the ultimate PE Prep tool. It's a series of 1-hour, 10-question simulated PE Exams offered weekly with solutions immediately following each exam. Learn more here. ​​​​Every week of the series is retroactive so you can still test yourself with past week exams.
0 Comments

One Sprinkler System if Each Floor is 52,000 sqft?

7/17/2020

5 Comments

 
​A parking garage has multiple levels covered by a dry system.

If the floor area of each level is equal to 52,000sf, is it acceptable to protect all levels with one dry system riser?

I am referencing the NFPA 13-2016 Handbook Sections 8.2 and its accompanying explanations. Thanks.

​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments

What is the Fire Rating for an FM Approved Door?

7/16/2020

2 Comments

 
I recently investigated some fire doors at one of our older buildings and saw they have an FM Approved label on them instead of a common UL Listing. I'm used to the UL listing label which clearly states the fire rating in minutes or hours. The FM label I saw gives some outdated ASTM standards and references a CABO report but doesn't clearly state the fire rating.

Does anyone have experience with the FM Approved fire door labels?

Based on my research, FM stopped approving fire doors a while ago. Thanks in advance.

​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
2 Comments

Preference for Gate Valves vs. Butterfly Valves?

7/15/2020

9 Comments

 
Indicating valve (Butterfly vs Gate Valve) Requirement in Fire Water Mains:

NFPA 24, Section A.3.3.17.1 (Edition 2019), suggests to use OS&Y gate valves, butterfly valves, and underground gate valves with post indicators.

I understand that any type of valve are acceptable to use and I've seen frequent use of butterfly and gate valves in underground main. OS&Y requirement is quite clear.

Based on my understanding, butterfly valves are less prone to corrosion and ferritic buildup when compared to gate valves due to its body design.

My understand is that gate valves, due to buildup, might be prevented from closing and would require an entire systems or section of a system to do any maintenance. Yet, direct-buried gate valves are still preferred for underground mains and I'm not sure why.

The cost difference does is not enough in my case to use gate valves specially for 8", 10" 14" or higher sizes.

Is there some reason for gate valve preferences over butterfly valves?

If a butterfly is used I could possibly see a pit being required for maintenance, but NFPA standards do not address pit requirements for a butterfly valve.

Is there any other consideration would be helpful to consider when using butterfly vs gate valves, for underground or even aboveground applications?

Any suggestions would be much appreciated.

​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments

Sprinkler Main Larger than Underground Size OK?

7/14/2020

15 Comments

 
Have a situation I've never crossed before: we have a very small building that's getting expanded. Originally the sprinkler contractor gave two options for the general contractor to price their underground fire sprinkler service - (1) is to provide a 2-1/2" main, the other (2) is to provide fire barriers in certain areas with automatic door closers to allow the room design method be used, and bring in a 2" underground.

I completely recognize that small underground pipe is not good practice and limits the future potential of the building. We recommended a 4-inch underground, but the increased cost for tap fees and underground pricing added $10-15,000 to the job which the owner adamantly refused.

We were given notice to proceed with 2-1/2" underground and thus provided a 2-1/2" riser and 2-1/2" mains. 

The GC gave a different direction for the underground and pulled 2" underground and is providing fire barriers and automatic door closers.

We've recalculated using the room design method and everything still works with the 2" underground, but the 2-1/2" riser and 2-1/2" main is already ordered and on the way to the jobsite.

Does NFPA 13 have any restriction against having a larger riser or main size than the underground?

Because of the change in building construction, we only need a 2" riser and 2" main but will instead already have prefabricated 2-1/2" in both. My thought is to have a permanent placard clearly affixed to the riser showing the situation and clearly identify on as-builts the methodology used.

​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
15 Comments

Are Natural Smoke Vents Obstructed for Stage?

7/13/2020

2 Comments

 
We have an auditorium with a stage area. The stage area is fully sprinklered and provided with four natural smoke vents at the roof.

Below the smoke vents at a depth of almost 10-feet (3 meters) there is structural steel frame (provided for structural stability) arranged with narrow gap of only about 1-inch (30 mm) and obstructing all the smoke vents. We understand this steel frames will deflect the smoke plume and affect the performance of smoke vents.

Is there a standard/code reference regarding how to include this obstruction in the calculations and to prove to AHJ that the smoke vents would still be sufficient?

Thanks in advance.

​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
2 Comments

PE Prep Series: Week 6 Leaderboard

7/13/2020

 
This week is the sixth of our 2020 PE Prep Series - it's 20-weeks worth of mini Fire Protection PE Exams. 

Each week we'll post the leaderboard here with the results of that week's exams. To see full leadership board and more details, visit the PE Prep Series page here.
Picture
The Leaderboard lists the top total scores for the most recent three weekly exams for PE Prep Series participants. 
See the entire scoreboard here
Picture
Want to join in? It's not too late - the PE Prep Series is the ultimate PE Prep tool. It's a series of 1-hour, 10-question simulated PE Exams offered weekly with solutions immediately following each exam. Learn more here. ​​​​Every week of the series is retroactive so you can still test yourself with past week exams.

Why Does a Hydrant Need a Control Valve?

7/10/2020

9 Comments

 
NFPA 24, Section 7.1.1.2 (2016 Edition), states that control valve shall be installed in each hydrant connection.

What is the purpose of this control valve, other than facilitating maintenance?

Would this be considered a "control valve" per NFPA 24 3.3.3, and does this have to be a post-indicating type valve?
Picture
​Common hydrant arrangement for illustration purposes.
Based on my limited understanding, this control valve is just a post-indicator valve/isolation valve which is for shutoff when there is an impairment downstream. I'm trying to get a better understanding of its purpose. Thanks in advance.

​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments

Mall Hose Connections Considered a Standpipe?

7/9/2020

2 Comments

 
I have a covered mall under 30' tall that requires hose valve connections in accordance with the International Building Code, Section 905.3.3.

Do these hose valve connections count as a standpipe that requires a monitored isolation valve as per NFPA 14 6.3.2?

​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
2 Comments

Duct Detectors Shut Only Associated Damper or All Dampers? How Should they be Controlled?

7/8/2020

7 Comments

 
Should return air duct smoke detectors associated with a fan system close only the associated damper and shutdown the fan or close all dampers on the system (including supply return spill and outside air)?

How should outside air and spill air fire smoke dampers be controlled? Should these to be controlled by fire alarm?

Thanks in advance.

​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe


7 Comments

How to Calc Ordinary Hazard Residential Areas?

7/7/2020

4 Comments

 
When performing hydraulic calcs for NFPA 13 residential occupancies, what is the best approach to address small Ordinary Hazard rooms, such as janitor's closets or laundry rooms located on an otherwise-residential floor?

Room design is not always an option due to the prerequisites listed in NFPA 13, but area/density seems excessive when the calculation method given for residential occupancies is the 4 most demanding adjacent heads.

A 1,500 square foot area seems to go well beyond this approach, defeating the purpose of the residential design method. Other than room design, is there a justifiable code basis for calculating only the heads in the most demanding ordinary hazard room on such a floor?

​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments

Dry System in a Wet System Count as Own Area?

7/6/2020

5 Comments

 
We are having a discussion in our office; we are doing a 14,000 square foot addition. The existing riser has 2 systems that are approximately 40,000 square foot each. On the middle of one of the systems there is a dry system for the loading dock.

Does the dry system count as its own system or is it included in the 40,000 square feet for purposes of a total system area?

​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments

PE Prep Series: Week 5 Leaderboard

7/6/2020

 
This week is the third of our 2020 PE Prep Series - it's 20-weeks worth of mini Fire Protection PE Exams. 

Each week we'll post the leaderboard here with the results of that week's exams. To see full leadership board and more details, visit the PE Prep Series page here.
​
Picture
The Leaderboard lists the top total scores for the most recent three weekly exams for PE Prep Series participants. 
See the entire scoreboard here
Picture
Want to join in? It's not too late - the PE Prep Series is the ultimate PE Prep tool. It's a series of 1-hour, 10-question simulated PE Exams offered weekly with solutions immediately following each exam. Learn more here. ​​​​Every week of the series is retroactive so you can still test yourself with past week exams

Remote Area by Coverage Along Floor or Slope?

7/3/2020

9 Comments

 
I am working on a project with an attic. The pitch of the attic is 12:12 and the structure is combustible construction. The area is being used as a mechanical room so the fire sprinkler layout will be Ordinary Hazard Group 1 and a wet system will protect the space since the temperature will be maintained above 40ºF. Standard spray sprinklers are being utilized because Attic sprinklers are only listed for Light Hazard use.

Using a quick response area reduction, the remote area will be 1,500ft² (OH1) x 1.3 (30% pitch increase) x 0.6 (40% quick response decrease) = 1,170ft².

Since the sprinklers are spaced along the 12:12 pitch, the floor area in plan view is substantially less than the square footage being protected along this steep slope which picks up a ton of sprinklers when I draw my remote area based on the floor. I can't find any guidance in NFPA 13 about remote area on a slope besides the typical 1.2 x √RA split between sprinklers.

Should the 1,170ft² remote area be measured based on the coverage of the sprinkler along the slope (as the protection is spaced) or should the remote area be based on the floor even though it picks up way more sprinklers than 1,170ft² of actual coverage based on the slope?

​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
9 Comments
<<Previous
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT