Can an auxiliary drain for a dry system be mounted on the side of pipe?
We've debated it recently after finding a situation where the auxiliary drains were mounted on the side of the pipe. I've been unable to find proper documentation concerning the orientation for the auxiliary drain. I did find the 5-gallon rule for wet systems, however, I was unable to find a specific reference for a dry system. Thanks in advance! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
Dan Wilder
10/30/2023 08:07:33 am
13-22'
Reply
Casey Milhorn
10/30/2023 10:08:09 am
See below for sections from NFPA 13, 2016 ed.
Reply
RYAN HINSON
10/30/2023 10:34:17 am
It is my opinion that complete drainage required per NFPA 13 (2022) Section 16.10, can only be achieved where the drain comes off the bottom of the lowest portion of the trapped system section.
Reply
Anthony
10/30/2023 01:14:11 pm
There is no specific provision requiring a drain be at the bottom of the pipe. However, it is strongly implied throughout NFPA 13 with phrases such as "completely drained." I would also sy its industry best practice.