How to Replace XL Pipe with Push Fit Fittings?

7/27/2023

15 Comments

 
​We have a remodel project with XL pipe and push fit fittings.

​When there is a leak in the fit fitting what product or method can be used to change the pipe to schedule 10 with grooved fittings?

Can XL be grooved?

Is a roustabout approved for XL?

There is virtually no information on the internet regarding XL except for notable failures with the material.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe

Additional References:
  • XL/BLT Galvanized and Black Lightwall Threadable Pipe
  • XL/BLT - M-COAT Galvanized and Black Lightwall Threadable Pipe
15 Comments
Pete H
7/27/2023 06:59:21 am

XL Can be grooved according to one guy on the eng-tips forum (and he seems to suggest it as he says threaded xl pipe has always caused problems). https://www.eng-tips.com/viewthread.cfm?qid=456367

That said, the same thread on that forum noted it seemed like all information about xl pipe has been scrubbed from the internet.

Reply
Ricky B
7/27/2023 08:07:24 am

I have a copy of the original tech data sheet for Allied XL - let me know how to send it to you.

Reply
Moderator (Joe Meyer)
7/27/2023 08:10:29 am

If you'd like to post it - email me at [email protected] and I can post it at the bottom of the comments. If you'd like to only forward onto the original poster, email me and I can get it forwarded.

Thanks Ricky!

Reply
Edward
7/27/2023 08:37:36 am

Please post it. It would be good information for all!

Moderator
7/27/2023 09:09:42 am

Links are provided below the original question. Thanks!

Bill Harvey
7/27/2023 08:12:22 am

I'd appreciate it if you could send mr the cuts.

thank you

bill harvey
nova fire protection

Reply
Glenn Berger
7/27/2023 08:38:55 am

Victaulic (and others) have "clamp-type" fittings that are perfect for your application.

Reply
Bill Harvey
7/27/2023 10:13:07 am

I thought so too but Victaulic informed me it isn't listed for fire protection

Reply
Vinnie
7/27/2023 08:39:12 am

In my experience (did a ton of service work replacing slip fittings & XL) you have to demo all the way back to the thread/groove connection. Once you put an in-air groover on the branch line and start moving things around up there you're going to cause leaks all over that branch line from those old slip fittings.

Reply
Dan Wilder
7/27/2023 08:43:13 am

Can it be grooved, yes, slowly assuming the pipe isn't already egg'd. Is a Vic 99 (or similar) push fitting allowed, also yes with the right end prep on the pipe BUT Sch 5 pipe, pending size, does not carry the minimum 175PSI pressure rating for 2½" and larger pipe (for Vic 99 anyways) so double check the working pressure of the fitting planned to be used.

In our experience, we try to get the replacement to use as little new piping as possible, but movement of existing fittings typically creates more leaks that need to be replaced. Most times we are going back to the main and using a mech tee for a new outlet and just installing all new piping.

Would love a copy as well, mine is lost on a USB somewhere...

Reply
Jesse
7/27/2023 09:05:01 am

To reiterate what Dan said and emphasize SLOWLY. We have had nothing but trouble with XL

Reply
Jim McHugh link
7/27/2023 08:44:29 am

You way want to look at Viega MegaPRESS as they have variations of the fitting that are approved for fire sprinkler piping on SCH 5 to SCH40.

Reply
Daniel Cieslinski
7/28/2023 06:50:44 am

are these UL /FM approved

Reply
Dan Wilder
7/28/2023 07:58:15 am

MegaPress (Steel), yes. Both UL & FM pending fitting type and size.

ProPress (Copper) did lose its listing/approvals at the beginning of the year due to just not getting renewed, not due to any issues that I am aware, (just a fiscal reason I think, but we sure bought enough of it I thought...)

Chris
7/31/2023 08:03:21 am

Are you sure it is XL pipe and not "poz-lock"? I would groove XL pipe without worry, but XL pipe was typically installed with threaded connections. But that poz-lock stuff was even thinner and used push together fittings, if it is that stuff you are SOL IMO. You'd have to demo back to the something you could groove or thread.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT