I recently read in a DoD specification for a fire alarm mass notification system that it was required that I perform a voltage drop calculation for my notification circuits that utilizes the end voltage of the battery test load and duration as the starting voltage of the voltage drop (v-drop) calc.
Typically, I just use the 20.4 V (85%) as the starting voltage for V-drops. I honestly have no idea how to calculate the end voltage of a battery bank after a prescribed loading period. I did some digging online and came across Peukert's Law (which could be helpful), and in the battery manufacturer data it provides max load capacities for an array of durations: 5 minutes to 20 hrs, and gives the end voltage per cell of these specific scenarios, but it appears to be a dubious proposition to extrapolate or interpolate values from the tables. For instance, the table tells me that for 5 minutes a 120 Ah battery can discharge at 313.2 A and have a remaining voltage of 1.7 V/cell (which is 10.2 V/batt and 20.4 V/sys), but it does not tell me what the voltage drop would be for a much smaller load over this duration. Does anyone know how to use these tables in order to estimate the ending battery voltage, let's say after a period of 48 hours under 1 A, and a successive period of 15 minutes at 18 A, utilizing a set of batteries that are 12v and 120AH? The battery tables mentioned above can be found in the product literature for Power Sonic PS-121200 batteries. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments
An existing building needs to replace its fire alarm system because the current system cannot support elevator recall, which is required for the new elevator they need to install. In Massachusetts, the IEBC states that when a fire alarm system is replaced, heat detectors will be installed if the building is not fully sprinklered.
Should the building include providing low-frequency sounders inside the units to ensure adequate audibility at the pillow? I have heard mixed interpretations from other AHJs. The attachment shows the code citation. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Hello everyone, I am testing a Hikvision HF-C108 Conventional Fire Alarm Control Panel and would appreciate some advice from anyone who has worked with this model. My goal is to monitor the panel remotely over the Internet from different locations and mobile devices.
Current situation:
Has anyone successfully monitored this panel via LAN/WAN or mobile application? Any guidance, manuals, software names, or real-world experience would be greatly appreciated. Thank you. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe When conducting a fire alarm test, I noticed the strobes on the 3-story barracks walkways on the exterior do not strobe in unison, but they do in unison per floor. Is this a concern?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We've been called back for service work to a recent voice fire alarm system installation, where we found that the elementary school is using the voice fire alarm system as their public address system (announcements, etc).
Is there anything codewise that prohibits this? On one hand, it should allow the system to possibly become more reliable since they'll report outages right away; I'm mostly just concerned with less trained staff using fire alarm equipment and having messages come from speakers labeled as "FIRE ALARM." What are your thoughts on this? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe With POTS lines going away very soon, I'm seeing many companies switch to a "POTS in a Box."
Do these meet the NFPA 72 code requirements? I can't find much information about these devices. One thing I am finding is that they do not appear to be UL-listed. At what point does NFPA 72 stop regulating the communication method? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I'm seeking clarification on where in code it dictates the need for a strobe device in the bathroom of a R-1 occupancy type (for the number of sleeping units required to have visual devices from IFC Table 907.5.2.3.2).
IFC 2024 Section 907.5.2.3.2 states "Habitable spaces in dwelling units and sleeping units" ... shall be provided with visible alarm notification. The definition of "habitable space" from Chapter 3 is "A space in a building for living, sleeping, eating, or cooking. Bathrooms, toilet rooms, closets, halls, storage or utility spaces, and similar areas are NOT considered habitable spaces". The 2010 ADA Standards for Accessible Design, Section 702.1, states that alarms in guest rooms required to provide communication features shall comply with Sections 4-3 and 4-4 of NFPA 72 (1999 edition) or Sections 7.4 and 7.5 of NFPA 72 (2002 edition). Neither of these sections mandates a strobe in the bathroom. I would like some context on when this became an industry standard (if it has) and where the code reference driving it comes from. Thanks in advance!!! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Where in NFPA-72 OR 13 does it discuss the location of control panels for pre-action systems?
Is there any guidance? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe How do people do elevator recall during dust-producing construction/tenant fit-outs?
I have heard smoke detectors being replaced with temporary heat detectors. I have heard bag the smoke detectors (but keep it live) and install an adjacent heat detector so that flames could melt the plastic bag. How have people done this? Before people say ask the AHJ, I am an AHJ, and I am trying to keep my constituents safe and am waffling back and forth. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe With the lithium ion battery problem, why not develop or use detection which sounds alarm if a hazard is developing?
Is that already a path people are recommending? Are there methods that already pick up on this? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe What are the applicable requirements for speaker placement in high-rise Group R-2 buildings equipped with fire alarm or emergency voice/alarm communication systems, specifically regarding speakers inside dwelling or sleeping units?
What practices have you been applying or enforcing in these areas? Industry feedback suggests inconsistent approaches: some designs include speakers within bedrooms and living rooms, while others install speakers only in the corridors and rely on in-unit smoke-detector sounder bases for occupant notification, expecting residents to move into the corridor to hear prerecorded or live voice messages. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We are completing a buildout for a spec suite; the shell warehouse building was just constructed and has a fire sprinkler supervising panel.
The fire department is saying we have to tie the duct detector into the fire alarm panel. This building does not have fire alarm, only sprinkler monitoring. Are they correct in saying we have to tie in the duct detector? Thank you! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe How do you coordinate what dialing out method with the client/telecom group, etc.?
A new fire alarm system, let's say a college building, for example, what do you typically see? Does the college have its own monitoring station? Do you dial out signals via cellular or internet, or both? Do dial-out signals go to both the college monitoring station (say, a life safety office) and a central monitoring station? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Can an outside horn and strobe be used for a general alarm, or just for water flow only?
I can't find anything specific in NFPA 72, 2016 edition. Is it more of an AHJ call? I can understand where it could be a nuisance if used for general alarm notification. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe We have a project where there is one large building that has many different activities throughout. There is also a trailer that is not connected to the building by walkway or anything except some plumbing for what I believe is a restroom.
This trailer is maybe 2-4 feet away from the larger main building, and the activity being done in the area closest to this trailer is woodworking/carpentry. I am trying to determine how the trailer should be classified to determine the requirements for a fire alarm system. I have gone back and forth between NFPA 101 and the IBC, but I am either overthinking or underthinking the scenario. I would just like to ensure I understand the criteria correctly because these two buildings do not share exit access or an exit, but may share an exit discharge. Would it be correct to classify the trailer as an existing business occupancy and look at Chapter 39 of NFPA 101? If I arrive there and look at Section 39.3.4.1, it appears that the three criteria listed there, which the trailer would not meet, result in a fire alarm system not being required. This does not sound correct but I could not piece together why. A ny help would be much appreciated! Thanks! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe For an apartment building (highrise), we have a situation here where a child with autism is has intense panic whenever there’s a fire alarm, including false alarms and testing.
We are planning to disconnect the smoke detector sounders from their flat and let the sounders from the common area notify them in case of a fire scenario. Is this allowed by code? Would it be allowed if permitted by AHJ? Would NFPA 72 or 101 address this specifically, or are there means of alternative approaches for a situation like this? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe I have an IT room with FM-200 under the raised floor and a pre-action sprinkler system at the ceiling. Contractors are replacing CRAC units.
Should the CRAC units be connected to the suppression system to shutdown upon activation of the FM200 system? I have done 2 days of research with no answer. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe How do you place fire alarm bells?
Do you just place them normally as you would place wall-mounted horns? Dealing with an old building, an existing system, but not that old fire alarm system that uses alarm bells instead of horns or speakers. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Do dual electrical feeds from two separate sources (same service provider, two different substations) with a UPS storage battery system that will support full load for 4+ hours meet the requirements for fire alarm secondary power?
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe In reference to the 2025 edition of NFPA 72, Table 14.4.3.2, Item 17(7)(a), it is stated that "manufacturer’s published instructions that ensure smoke entry from the protected area, through the vents, or into the sensing chamber" may be used, which appears to include self-testing smoke detectors such as the Honeywell self-test series.
These detectors introduce a small quantity of smoke or aerosol into the sensing chamber as part of a built-in functional test sequence. It is my understanding that this self-testing technology may fulfill the requirement for a functional test that traditionally uses an aerosol can to verify smoke entry and detector response during both initial acceptance and annual testing. Further, Section 14.4.4.2 states that “If automatic testing is performed at least weekly by a remotely monitored fire alarm control unit specifically listed for the application, the manual testing frequency shall be permitted to be extended to annually in accordance with Table 14.4.3.2.” However, this section does not explicitly clarify whether this weekly automatic testing relates to the smoke detector’s functional test, sensitivity test, or both. With that context, I would like to get clarification on the following points: Does NFPA 72 (2025) permit the use of self-test smoke detectors that introduce a small amount of test smoke into the sensing chamber to fully satisfy the functional testing requirements (including smoke entry testing) for both initial acceptance and annual testing per Table 14.4.3.2? If an approved self-test detector performs an automatic internal functional test that verifies smoke entry into the sensing chamber and provides results to a remotely monitored fire alarm control unit, does NFPA 72 still require a manual smoke entry test (e.g., aerosol can) for annual testing purposes? Does the reference in Section 14.4.4.2 to “automatic testing performed at least weekly” apply to functional testing, sensitivity testing, or both? And is there any mandate elsewhere in NFPA 72 requiring weekly testing of smoke detectors? Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe For cycle tracks within a road tunnel, what requirements exist for the bicycle tracks within the tunnels?
I have not been able to find any fire or life safety requirements for cycle tracks within road tunnels (exit separation, fire suppression, detection, and emergency communication system requirements) in any codes or standards. Any suggestions on where I could go to or any research papers that I could refer? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Does a Sauna room require fire alarm notification?
Is there any code requirement on this one way or another? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe Before people say, "Ask the AHJ," I am him; he is me.
I have an applicant who has combined plots of land with a mid-rise and some detached townhouses. A shared fire line supplies the two structures, but only the mid-rise FACP monitors the supply tamper. The townhouse FACP will not know if the water is off (except for the tampers at the risers within the townhouse). The buildings are owned by the same ownership. They are arguing they are technically meeting IBC 2015 903.4 "Valves controlling the water supply for automatic sprinkler systems, pumps, tanks, water levels, and temperatures, critical air pressures, and waterflow switches on all sprinkler systems shall be electrically supervised by a listed fire alarm control unit." It is being monitored, but the fire marshal and I are of the opinion this doesn't provide monitoring for the townhouse and does not meet the intent of the code. Does anyone have any thoughts on whether a shared line can be monitored by only one building that it serves? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe My company is hiring a contractor to install our central station headend equipment (servers and software).
I would like to include the testing requirements in the statement of work. I looked through NFPA 72-19 Chapters 14 and 26, as well as other chapters and codes. I do not see the requirements for central station headend testing. I think the subscribers will need to ping the central station with the date, emergency code, building, etc. Does code require a minimum amount of information the subscribers must send to the Central Station? If so, could you tell me the required subscriber information that needs to be sent to the central station or provide the location in code for the information to be sent to the central station from the subscribers? I don't see any requirements or criteria for testing, and I want to be sure we're conducting this appropriately. Thanks in advance. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe If a duct detector is installed, and the mechanical unit has a capacity of less than 2,000 CFM, it is required by code for the duct detector to be connected to the fire alarm panel?
Alternatively, removing the detectors can be considered in this situation. Looking for relevant code and standard basis. We're under the 2021 IFC, 2021 IBC, and 2019 NFPA 72. Thank you! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe |