Does the requirement under NFPA 25, Chapter 14 for a 5-year internal pipe inspection apply if the system is an open sprinkler/nozzle deluge system?
The system is flowed annually and I believe that this full flow should meet the requirement in lieu of a 5-year internal pipe inspection. Am I correct? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Glenn Berger
12/7/2023 08:11:52 am
The comment states that the system is "flowed annually."
Reply
Jesse
12/7/2023 08:28:59 am
I've seen a lot of deluge systems, but I think all of them had a test manifold and didn't flow the entire system. I think an internal pipe inspection is needed
Reply
Peter
12/7/2023 08:44:26 am
NFPA 25 13.4.4.2.4 requires a full flow test to include discharge water through the sprinklers or nozzles, primarily to observe any issues with spray patterns and obstructions.
Reply
12/7/2023 08:46:03 am
NFPA requires a full flow test annually (with exceptions that extend this to no more than 3 years) and are to include pressure readings at the most remote nozzle or sprinkler to determine if there's been deterioration of the water supply. If this is how the tests are performed, I would agree with you. The only exception to the requirement for internal inspections however is for nonmetallic piping. I'd be interested to know if the committee has discussed this.
Reply
Eric R
12/7/2023 11:47:21 am
I can see how this could be questioned, because at least for foam deluge systems you can do the reverse and use an internal pipe inspection performed per chapter 14 in lieu of performing the nozzle flow test per chapter 11.
Reply
Peter
12/7/2023 12:03:41 pm
Eric,
Reply
Eric R
12/7/2023 12:18:47 pm
Totally agree Peter, just wanted to point out the only place I could think of in the code where the two test types cross paths.
Dave
12/7/2023 11:58:03 am
Regarding IPE, it is worth noting that for the 2014 edition of NFPA #25 “The concept of internal inspection was modified to an internal assessment concept, in which a performance-based assessment frequency is explicitly addressed.”
Reply
sean
12/31/2023 06:59:10 pm
you still need to make sure that pipe has not be compromised and with nothing inside you have no leaks to let you know early