One fundamental aspect of fluid movement is thrust force, which is created when a flow path bends, tees, wyes, dead ends, or reduces. In order to counter the unbalanced forces that are created at these locations, the pipe and fittings must be mechanically restrained from separating, welded together, or otherwise fixed from movement.
Push-On Underground Joints One popular method of preventing pipe separation for underground pipe is gasketed push-on joints for underground pipe that do not have special locking devices, but permit pipe to be installed in any direction and at any point along the path. Role of Thrust Blocks In order to prevent the internal pressure from forcing the pipe and fittings to separate, blocking (or "thrust blocks") provide stability and allow the surrounding soil to accept the thrust force from the pipe assembly. Soil conditions vary in its ability to handle forces. Thrust blocks allow a narrow point force to be spread and distributed across larger areas of soil down to a pressure that the soil can bear.
Thrust blocks take the point force created from the change in direction of the water (static and dynamic)
and distribute that force to the soil. The Calculator The tool below is an early part of a larger effort to determine the thrust block detailing. In the coming weeks, I would like to add block height, width, volume and visualizations to detail the parameters. Don't see the tool below? Click here. For those who work routinely with thrust block and their calculations under NFPA 13, what else could I add to this tool to be more useful? Comment here or email me at jdmeyer@meyerfire.com if you have any ideas. The Toolkit - Launches Next Week The long-awaited Toolkit launches next week - complete with this and other tools in a downloadable software package. Be the office hero with quick and printable tools, as well as access to the Sprinkler Database and the ability to post questions to users on the Daily Discussion forum. Look out for news regarding the launch next week. Get More Like This If you don't already subscribe to these articles & resources, you can do so, for free, here: 1/24/2019 03:49:49 am
Dear Sir/Madam,
James Smith
2/1/2019 01:11:11 pm
A total weight of the thrust block would be nice to see, instead of calculating by hand after the results.
Christopher Davis
2/12/2019 08:21:23 am
What degree would I use for a Tee fitting or dead end?
salman
7/4/2019 01:56:01 am
i would like to know how to check the foc is => to 1.5
JOE
7/8/2019 01:17:28 pm
Salman,
Ihab Said Sorour
2/24/2020 03:51:25 am
I need two download this documnets
Joe Meyer
2/24/2020 08:49:06 am
Ihab - you can get a license for this tool and all the others at www.meyerfire.com/toolkit. Hope this helps!
Josh
6/12/2020 05:02:24 pm
The calculator doesn't provide for all elements in NFPA 13 or NFPA 24.
Joe Meyer
6/16/2020 05:45:00 am
Josh, thanks for reaching out about this. NFPA 13 jumps back and forth between interior and outside pipe diameters depending on the calculation. I'll review this in detail and update the tool here shortly. Comments are closed.
|
ALL-ACCESSSUBSCRIBEGet Free Articles via Email:
+ Get calculators, tools, resources and articles
+ Get our PDF Flowchart for Canopy & Overhang Requirements instantly + No spam
+ Unsubscribe anytime AUTHORJoe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About FILTERS
All
ARCHIVES
March 2024
|