Fire Pump On or Off During Main Drain Test?

5/24/2024

10 Comments

 
When conducting main drain test on a sprinkler system with a fire pump, should the pump be on or off?

AHJ generally wants the pump to be on in this area. Thanks.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Dan Wilder
5/24/2024 07:51:27 am

The test should be done at the main drain closest to the supply/source with the pump off. NFPA 25 says "for each water supply lead-in". It would be near impossible to decern a water supply degradation instead of a pump degradation, or a combination of both, with the pump running based only on a main drain test.

13.2.2* Main Drain Test.
A main drain test shall be conducted annually for each water supply lead-in to a building water-based fire protection system to determine whether there has been a change in the condition of the water supply.

13.2.2.1 also allows a single main drain test for buildings with multiple systems per water supply lead-in.

This is also reinforced by looking at Table 5.1.1.2 for the summary of sprinkler systems with no frequency provided and referencing Chapter 13.

Reply
Glenn Berger
5/24/2024 08:15:32 am

Depends -

Is the water supply to the sprinkler system solely dependent on the fire pump? Or can the municipal's water supply the sprinkler system without the fire pump operating?

Reply
Derek G.
5/24/2024 08:34:52 am

Agree with Dan here. It should be off, but as an AHJ and former fitter, I would also capture the numbers with it on.....it doesn't hurt to have both sets of values.

Reply
Jack G
5/24/2024 09:16:28 am

The fire pump should be off.
The main drain test is used to determine degradation in the incoming water supply.
A separate test —— fire pump test — is used to determine changes or degradation of the fire pump.

Reply
Franck
5/24/2024 09:18:28 am

If you are talking about the 2 in. drain test, it should be done with the pump on.
I always did it that way (and was trained to do it that way) for more than 30 years as an insurance loss prevention engineer (for every survey).

The purpose of this test is to drop the pressure at the ACV very quickly and check if the fire pump starts and if the pressure is coming back to the required value (as per previous tests).
If not, this means that you have partial obstruction between the fire pump and the ACV.
If you do this test with the pump off, the the pressure will drop, but will not come back up (you just drop the pressure in the system with no way to compensate). This means that you will have no idea on possible obstruction on the line.

To check possible pump degradation, you will check it anyway with the annual flow test of the pump.

Reply
Franck
5/24/2024 09:21:38 am

By "on", I mean "pump in automatic mode". But the pump is not running when you start the 2" drain test. You start the pump by pulling down the pressure in the system.

I understand "off" in your question by "pump in non-automatic mode".

Reply
Steve Cooper
5/24/2024 09:41:00 am

With the fire pump off, would make sense per code, but your AHJ could just want extra values and tests. Many AHJs we work with like to ask for much more than NFPA requires.

Reply
Matthew Mueller
5/28/2024 07:45:41 am

This was something that was taught to me early on and was a significant change to how my company, and most companies in our area had been doing this test. The fire pump is an integral part of the designed water supply. In addition, all tests required by NFPA 25 are required to be performed with the fire pump in "on" (automatic) unless impairment procedures are followed.

NFPA 25, 2023 Ed.:
4.4 Water Supply Status.
During inspection, testing, and maintenance, water supplies, including fire pumps, shall remain in service unless under constant attendance by qualified personnel or unless impairment procedures in Chapter 15 are followed.

Excerpt from NFPA 25 Handbook, 2023 Ed.

Testing Procedure for 13.2.2
Main Drain Test

Purpose

The purpose of conducting a main drain test is to determine the adequacy of the connected water supply and to detect significant reductions that might adversely impact the system operation by comparing the results of the current test to a previous baseline test pressure. The test does not provide absolute assurance of an unobstructed waterflow or fully opened valves, but it provides a reasonable check against gross changes in the water supply conditions. This testing is required for each water supply lead-in to the building. Where a single lead-in supplies multiple risers, a single main drain test is acceptable, except that additional main drain tests must be conducted so that every system backflow preventer and/or pressure-reducing valve is exercised. These additional tests would be necessary for situations such as those that include individual floor control valves equipped with pressure-reducing valves.

Tools/Equipment

No special tools are required.

Procedure Steps

Systems Supplied by a Fire Pump

1.
Prior to any testing, notify the fire department and/or the alarm monitoring company, as well as the facility representatives, that testing is going to be conducted.

2.
The pressure gauge readings collected on the suction side of the fire pump during the annual fire pump test can be used for comparison purposes at a common flow rate in lieu of conducting a separate annual main drain test.

a.
During the annual fire pump test, record the static pressure (no flow) reading on the pressure gauge on the suction side of the fire pump.

b.
During the rated flow (or other common flow rate) of the annual fire pump test, allow the pressure to stabilize and then record the residual pressure reading on the pressure gauge on the suction side of the fire pump.

3.
Where the sole supply of water to the fire pump is through a backflow preventer and/or pressure-reducing valve requiring a quarterly main drain test, the test should be conducted in accordance with the following procedure with the fire pump in the operating position.

a.
Check the area surrounding the main drain outlet to ensure that there are no obvious conditions that would prevent water from being discharged safely or cause direct damage in the immediate vicinity. Where the discharge of water is to an area subject to potential freezing conditions, the facility representative should be advised of the potential for icing conditions.

b.
On systems where the main drain is connected to an alarm valve or other arrangement where the flow of water from the main drain will result in the activation of an alarm device or water motor gong, the shutoff valve (where equipped) in the connection to the alarm sensing line should be closed to avoid unnecessary sounding of the alarm.

c.
Record the static pressure (no flow) reading on the pressure gauge on the suction side of the fire pump.

d.
Open the main drain valve slowly until it has reached the fully open position, initiating the fire pump operation. Allow the pressure to stabilize, then record the residual pressure reading on the pressure gauge on the suction side of the fire pump.

e.
Slowly close the main drain valve to avoid water hammer, record the time for the pressure to stabilize, and record the return static pressure reading on the pressure gauge on the suction side of the fire pump.

f.
Allow the fire pump to operate for 10 minutes for an electric fire pump or 30 minutes for a diesel fire pump, followed by a shutdown of the fire pump and restoration of automatic operating condition.

g.
Return any shutoff valves in alarm sensing lines that were closed during Step 3b to the normal operating position.

4.
Upon completion of all testing, notify the fire department and/or the alarm monitoring company, as well as the facility representatives, that testing is complete. Reset the fire alarm system as necessary.

Reply
Jay
5/29/2024 03:45:40 pm

I agree with #2.....there is no need to do a main drain test on a system with a fire pump because the suction pressures from the annual pump tests can be compared to identify a reduced water supply

Reply
Matt G
8/15/2024 04:35:28 pm

That is not entirely correct Jay. Facilities that have fire pumps in stand alone pump houses that feed underground piping that supply the sprinkler risers in the main building(s) certainly need main drain tests completed. This is to ensure no isolation valves are shut / partially shut or major deterioration / blockage of the underground supply piping.

As to pump running versus not running for main drain tests, I have heard it argued both ways. My company performs them with the fire pump off, unless fed by a storage tank. We drop the system pressures to the city pressure to do so properly.




Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT