MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

What Safety Factor to Use for Fire Flow?

1/7/2026

12 Comments

 
In the absence of a code-mandated requirement, what safety factor ​should we apply when evaluating fire flow, if you apply one at all?

I am currently working on a building that has a code-required fire flow of 2,000 gpm at 20 psi. Using the MeyerFire Toolkit to evaluate the water supply, I found
that the available fire flow is 2,004 gpm at 20 psi.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
12 Comments

What Fire Flow Method is Actually Used?

12/12/2025

13 Comments

 
The International Fire Code, Appendix B, describes one method for determining Fire Flow (water available at the site for manual firefighting via hydrants). 

However, Appendix B is not enforceable unless it's specifically adopted.

The 2024 IFC Section 507.3 simply states, "Fire-flow requirements for buildings or portions of buildings and facilities shall be determined by an approved method."

Is Appendix B the only method actually used in practice in North America?

If not, what alternative methods do you see adopted, or does your jurisdiction adopt?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments

Tie Tenant Duct-Detectors to Building Fire Alarm?

10/27/2025

6 Comments

 
Good morning, I am in Florida and use the Florida Fire Prevention Code 8th Edition, which references NFPA 1 and 101 (2021), NFPA 72 (2019), NFPA 96 (2021), and NFPA 17A (2021).

I have a mixed occupancy strip mall that is fully sprinklered and has a fire alarm that was initially installed to monitor the sprinklers only.

One tenant upgraded the panel to accommodate a full fire alarm for their unit.

A different tenant, mercantile class C, in the strip mall has installed a hood and hood suppression system along with duct detectors for their upgraded AC system. The ducts serve only their unit and do not cross demising walls or serve other units.

My interpretation is that the duct detectors and hood suppression systems must be tied into the building's fire alarm.

Is this correct?

Another question, would this tenant then need to upgrade their unit to include pulls and notification appliances?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

NFPA Requirements for Campus-Style Fire Pump?

10/15/2025

8 Comments

 
Does NFPA provide guidance on campus-style fire pump design?

Can I provide two water services (one from each building) and serve out to two buildings?

NFPA 20 4.9 implies that campus-style designs are acceptable, but I am not seeing any code lines referencing any further requirements for such a design.

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Hydrant Spacing & Location for Industrial Plant?

6/20/2025

11 Comments

 
For a newly built steel smelting plant, how should the layout spacing and protection range of private fire hydrants be considered?

I have checked that NFPA 1 states the maximum spacing for "Buildings Other than Detached One- and Two-Family Dwellings" is no more than 500 feet, but NFPA 850 specifies a maximum spacing of 300 feet.

Do both govern?

If so, does the more-restrictive one apply?

What should be the protection range of each hydrant?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

NFPA Require 2nd Supply for Seismic Highrises?

6/16/2025

3 Comments

 
The IBC section 403.3.3 requires an automatic on-site secondary water supply for high-rise buildings in seismic zone C or greater.

Does NFPA have a similar requirement for on-site water storage in a seismic zone?

All I can find are the bracing requirements in NFPA 13, but I am not seeing anything in NFPA 101 or NFPA 5000.

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Fire Flow for an Outdoor Lumberyard?

6/10/2025

6 Comments

 
Where can I find guidance for fire flow for an outdoor lumberyard?

The IBC, Appendix B and C are for Buildings. It specifically says: "This appendix does not apply to structures other than buildings."

Is there anything in the FM data sheets, or elsewhere?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Is Large Circulation Space a 'Corridor' in NFPA 101?

2/13/2025

6 Comments

 
Subject: Two story convenience opening separation from corridors.

NFPA 101 (2021 edition) Section 8.6.9.1 permits convenience openings for two adjacent stories. But, these convenience openings shall be separated from corridors (requirement #3) and
further states that separation should be by a smoke partition (requirement #5).

How do you define a corridor versus an open floor area or lobby per NFPA 101, since no definitions are given within the code?

Jurisdiction is required to follow NFPA 1 and NFPA 101.

For example, a building has a large assembly space on the second floor. All doors from the assembly space lead to a ~40'-0" wide circulation space (+200'-0" long in the other direction). To reach the building exit stair, occupants from the assembly room must traverse the 40'-0" wide circulation space. Within this circulation space is a ~20'-0" x 40'-0" vertical opening that connects the 1st and 2nd floor.

Should this circulation space be considered a corridor
, and should the vertical opening be prohibited from being classified as a convenience opening without a smoke partition separating from the corridor?

Or is the 2nd floor space to be considered an open floor area, with exits immediately accessible in different directions (NFPA 101 7.5.1.1.1) and not consider it a corridor?

​The width of the circulation space seems too wide to be defined as a corridor but NFPA only provides minimum width requirements for corridors, and no maximum width for a space to be considered a corridor as far as I can determine.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
6 Comments

Use Many (8) Water Storage Tanks in Lieu of One?

12/23/2024

17 Comments

 
I work for a local fire department that does plan reviews for fire protection systems. We are reviewing a project that requires 40,000 gallons of stored water. They are proposing using multiple fire water tanks and eight 5,000-gallon tanks.

While NFPA
does not restrict the use of multiple tanks, I would like to see fewer tanks than eight. I am more inclined to allow two separate tanks at the most.

However, I wanted to see what others thought and if there was a standard understanding or practice to number or size of tanks to the total needed water demand. Thanks for any help.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
17 Comments

Can Non-Sprinklered F-2 Use Fire Flow Reduction?

12/10/2024

13 Comments

 
A 40,000 sqft, F-2 Occupancy, single-story metalworking facility of IBC Type II-B construction is not required to be provided with automatic sprinkler protection due to the lack of sufficient combustible loading in the IBC.

However, the same 40,000 sqft single-story facility of IBC Type II-B construction of a Mercantile (M) occupancy must be provided with automatic sprinkler protection due to sufficient combustible loading to warrant sprinkler protection.

Unfortunately, IFC Appendix B does not distinguish between these different occupancies with regard to Fire Flow except that a 75% reduction is offered to the M occupancy for sprinkler protection.

Since no sprinkler protection is required for the F-2 occupancy, can't it be treated the same as occupancies requiring sprinkler protection and provided with sprinkler protection - allowing for the 75% reduction?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments

Fire Hydrant Max Spacing and Distance to Bldgs?

8/16/2024

8 Comments

 
I have a bunch of new houses going in. Some are along an existing street, and some are around a newly formed cul-de-sac.

How do I determine the number of hydrants, how far apart they are, and the maximum distance to any of the homes?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

A Separate Second Storage Tank for Firefighting?

7/17/2024

5 Comments

 
Suppose on-site water storage for firefighting is required, and an existing tank is on-site sized for the existing building.

Can I add a second tank on site (not connected to the first tank) and just size it for the additional water required for the second building?

Ex.
A larger building requires a 10,000-gallon tank, while a smaller building requires a 5,000-gallon tank. Can I just install one new 5,000-gallon tank (10,000-5,000 = 5,000 gallons)?

Or would the tanks need to be connected so there is no shortage of water?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Limit for Length and Size for Underground Loops?

4/26/2024

11 Comments

 
Typically when I work on campus/multi-building systems, I am using a single underground main and splitting off to each building. Since you don't have to consider a multiple building fire problem, we have typically worked on the hydraulically most-remote building for underground sizing and use wall PIVs to offer individual building shutoffs, with FDCs on the individual buildings.

I'm getting challenged on "what allows this in code?" It's mostly a question of - where is the limit on how long a loop can be?

I'm looking at this from a sprinkler design perspective and whether each individual building's sprinkler system is able to perform hydraulically.

Is the limit for the length/layout/sizing of a campus underground loop simply the more demanding of Fire Flow or sprinkler system feeds?

Is there a code basis for this?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Tank Size for Simultaneous Sprinkler & Fire Flow?

8/29/2023

6 Comments

 
Long question - in essence - is Fire Flow considered on top of a flowing sprinkler system?

Recently there was a great discussion on the forum here about whether a water storage tank size needs to include Fire Flow in addition to sprinkler demand. There were some great points made (www.meyerfire.com/daily/must-water-storage-tank-include-site-fire-flow).

I have just come upon a project where we do have a municipal water supply, but it tapers off very steeply. The flow test in the area was 52 psi static, 25 psi residual at only 650 gpm. This would put the available Fire Flow around 712 gpm at 20 psi for the site.

In order for the AHJ to reduce the required Fire Flow under the IFC, the building(s) nearby need to be sprinkler-protected. This would bring down the Fire Flow requirement to 1,000 gpm at 2-hours, for this setup. The sprinkler system isn't designed yet, but we'd estimate around a 550-650 gpm demand with a fire pump. This gets really interesting based on the prior discussion.


When the fire department shows up on site during a fire, and then starts to pull water, is this Fire Flow in addition to the flowing sprinkler system, or considered separate?

In other words, is the 1,000 gpm (for 2 hours) for Fire Flow on top of a 600 gpm demand for sprinkler (for 60 minutes)?


If the water storage tank needs to meet the demand of the sprinkler and Fire Flow separately, then the calculation comes down to ~300 gpm needed to fill the shortage on Fire Flow, multiplied by 2-hours. That's a tank in the ballpark of 35-40,000 gallons.

If the water storage tank needs to meet the Fire Flow as the sprinkler system is operating, that's a flow of around 1,600 gpm to fight a fire. That's as much as ~900 gpm x 2 hours to a ballpark of 100-115,000 gallons. Huge difference.


I can't find any relevant code that stipulates one way or another, only that the tank must supply the sources it is connected to. 

Am I looking at this correctly? I see sprinkler and Fire Flow needing to be met by a tank that they're connected to, but is the Fire Flow robbing the sprinkler system, or vice-versa?

Thanks so much for reading. This is obviously TLTHFR (too long, thank-you-for-reading).

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Allowed to Use Hydrant Across 2-Lane Highway?

3/9/2023

12 Comments

 
When a building is 84-feet from an existing public fire hydrant located across a 2-lane 45mph roadway, can we assume it is standard practice to use it in an event of a fire?

Or would the owner be required to add a personal-use fire hydrant or water storage device on their side of the road?

In the latter case, how far would the fire hydrant have to be placed from the building?​
Picture
Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

Maximum Allowable Pressure for Fire Hydrant?

8/1/2022

9 Comments

 
We have a proposed fire hydrant in our county that will have pressures ranging from 210 psi to 250 psi according to the engineer designing the underground line.

My Chief and I are looking into this in regards to NFPA standards/applicable code, and are concerned that the high pressure could injure firefighters or damage equipment.

Is there a maximum permitted pressure that a hydrant can be, per code?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Min. Distance from Transformer to Fire Hydrant?

7/19/2022

8 Comments

 
Is there an applicable code reference for minimum distance between a fire hydrant and a transformer?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Provide Fire Access for Narrow Mechanical Yard?

7/18/2022

2 Comments

 
Hoping to gain some insight from industry here:

Working on preliminary layouts for a large industrial facility that is comprised of tilt-up precast single-story building (~40' tall) and flanked on one side by an equipment yard (think generators, switchgears, mechanical equipment) configured in two levels (think mezzanine).

Question is on fire access to the main building: The mechanical yard runs the entire length of the main building and we are considering fire access as the depth of the equipment yard is ~100ft with a limited service corridor separating the two (~12ft) for maintenance and building egress. There will be periodic gaps (~6ft wide) between equipment located at grade, however the access will require passing through the yard on foot (underneath the second level of equipment on the mezzanine) to gain access to the main building.

Per IFC 503.1.1 our fire access roads must provide continuous access to the exterior within 150ft of the building.

Would passing "through" the mechanical yard at grade meet this requirement?

Would placing "driveways" through the yard to allow a truck to pull closer to the building (but being parked underneath the second level) be kosher?

A similar question exists regarding having hydrants located directly under the second level near the extents of the yard, is this OK?

Have been unsuccessful at locating any code references regarding fire access through a "tunnel" if you would. An AHJ perspective would be much appreciated, along with any other thoughts/feedback.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
2 Comments

Fire Alarm Required in Detached Cooler?

7/11/2022

7 Comments

 
We are designing a new/upgraded fire alarm system for a remodeled highrise (our local codes are 2012 IBC and 2018 NFPA 1) and there is a detached walk-in cooler for the restaurant, located relatively close to the main building (~3' away from the nearest exterior wall).

We received an RFI asking whether fire alarm devices are required in the coolers - good question(!). I'm not able to find anything specific for fire alarm devices in detached storage buildings.

Do you see fire alarm required for the detached cooler?

If anyone has any insight (or NFPA references that I've overlooked), it would be very much appreciated!

Thanks for a great community!

​
​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

What is Seen/Specified for Firestop ID Labels?

5/4/2022

9 Comments

 
What are you all seeing or specifying for firestop identification labels?

Masterspec calls for metal or plastic labels.

I found an FCIA (Firestop Contractors International Association) article that speaks to stamped metal tags or ceramic fiber tags (Google is failing on what that actually would look like).

It seems the firestop manufacturers all have stickers.

I have always specified the metal or plastic labels using the Masterspec language. If I get anything at all installed, it is the manufacturer stickers. I have concerns about the longevity of the stickers.

I’m curious what others are calling for, what your AHJs or clients ask for, and what is actually getting installed. Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Required Fire Hydrant Distance From Building?

8/19/2021

12 Comments

 
We have an project serving the textile manufacturing industry. We are looking to install a fire hydrant (500 gpm minimum) in proximity to the building.

What is the minimum and maximum distance these hydrant(s) should be located from the building?

The project is not under IBC / IFC criteria, only subject to the NFPA series of standards. 

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

Where to Locate Portable Fire Extinguishers?

8/11/2021

10 Comments

 
I am new to the fire engineering fraternity and I'm currently working with a small office building. It's a single-story, 5,800 sqft office use with a small battery room and small server room.

IBC (2021) Section 906 and IFC start with "where required". I cannot find where extinguishers are required for business occupancy.

What is the code path to determine if fire extinguishers are required?

Does the IBC/IFC not address where extinguishers are required?

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Proper Spacing for Private Fire Hydrants?

9/3/2020

7 Comments

 
Is there a standard spacing for private fire hydrants?

No applicable code for this project, but looking for guidance in what would be common under NFPA 24, NFPA 1 / 101, and/or the IBC. Thanks in advance.

​​​​​​​​​​​​​​Submitted anonymously and posted for discussion. Discuss This | Submit Your Question | Subscribe
7 Comments

Standpipes Not Req'd for Large Industrial Facility?

5/22/2020

3 Comments

 
NFPA 1 Section 13.2.2.2, a Class I standpipe is not required in buildings less than three stories or less than 50-ft high above grade. 

If we have a huge industrial complex or storage occupancy of 60,000 square meters (645,000 sqft), should we not require a standpipe system if it is only one floor above grade with a total height of 40-feet? Looks strange to me.

​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
3 Comments
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT