Updates to Free Remote Area Calculator Tool

7/17/2024

 
This week I've updated our Quick-Response Remote Area tool, which quickly takes a few considerations into play and reduces the size of a fire sprinkler design area based on the Quick-Response Reduction that's allowed in NFPA 13. This new free version incorporates references in NFPA 13, 2022 Edition.

Suppress Early, Suppress Less
The concept behind reducing the calculated hydraulically remote area in a fire sprinkler system is entirely based on fighting a more minor fire earlier in the development of the fire.

There are a handful of factors that contribute to the timing of sprinkler response (a good future discussion), which include the thermal sensitivity, sprinkler temperature rating, distance of sprinklers relative to the ceiling, sprinkler spacing, ceiling height, and dynamics of the fire itself.

The reduction in the hydraulically remote area is based upon comparative tests of quick-response spray sprinklers against standard-response spray sprinklers. According to the NFPA 13 handbook, the tests demonstrated that the earlier the water is applied to the fire, the smaller the fire and, ultimately, the fewer sprinklers needed to activate.

Not Universally Accepted
While the remote area reduction has been included in NFPA 13 for years, it is not universally accepted. Many engineer specifications don't allow the reduction, and design standards for significant organizations such as the Department of Defense (UFC 3-600-01) don't permit it either.

Why not accept the remote area reduction, if NFPA 13 includes it? Like other elements in hydraulic design for fire sprinkler systems, not using the remote area reduction provides an additional safety factor to the system.

Additionally, since the quantity of sprinklers relates to the quantity of water flowing in the system, main sizes are directly impacted by using or not using the quick response area reduction. Building owners may opt to not want to reduce the remote area to preserve reasonable (larger) main sizes and give themselves flexibility on building modifications and sprinkler system changes in the future.

Quick-Response Area Reduction Calculator
This quick calculator is in part a checklist of prerequisites to reduce the remote area on a fire sprinkler system, in part a method of showing your work, and in part a quick calculator on determining your final remote area size. Don't see it below? Give it a try here.

I hope you find these tools helpful. Free ones are available on the TOOLKIT dropdown at www.meyerfire.com. If you're a MeyerFire University member, you get all these right in your iOS or Android app too.

Thanks, and hope you have a great rest of your week!

- Joe
James Art, FPE
7/17/2024 01:01:19 pm

You should be aware that in California,
the reduction in area for quick response is limited by code to
Light Hazard ONLY.
See CaFC (2022) Chapter 80 NFPA.

This results in a higher safety factor for Ordinary Hazard,
and less impact if a sprinkler is obstructed or otherwise fails.


Comments are closed.
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET THE TOOLKIT

    SUBSCRIBE

    Get Free Articles via Email:
    + Get calculators, tools, resources and articles
    + Get our PDF Flowchart for Canopy & Overhang Requirements instantly
    Picture
    + No spam
    ​+ Unsubscribe anytime
    I'm Interested In:

    AUTHOR

    Joe Meyer, PE, is a Fire Protection Engineer out of St. Louis, Missouri who writes & develops resources for Fire Protection Professionals. See bio here: About


    FILTERS

    All
    AI
    Announcements
    Author Jocelyn Sarrantonio PE
    Book Review
    Calculators
    Career
    Course
    Delegated Design
    Design Challenge
    Detail Critique
    Fire Alarm
    Fire Events
    Fire Suppression
    Flammable & Combustible Liquids
    Flexible Drops
    Floor Control Valve
    Life Safety
    News
    NICET
    Opinion
    Passive Fire Protection
    PE Exam
    Perspective
    Pick A Part
    Pick-A-Part
    Products
    Site Updates
    Special Hazards
    Specifications
    Sprinkler Systems
    Standpipes
    Students
    Talks
    Tools
    Videos


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    January 2025
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    December 2020
    November 2020
    October 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    April 2018
    March 2018
    February 2018
    January 2018
    December 2017
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    May 2017
    April 2017
    September 2016
    August 2016
    July 2016
    June 2016
    July 2015
    June 2015
    May 2015

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT