MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Do Other Consultants Review Site Utility Plans?

12/30/2020

11 Comments

 
I've been seven years in the chair, and the most thankless job I encounter on every project is - reviewing the site utility plan and picking it apart.

I've now made my own rule that I will only point the civil engineer's mistakes once, early in the project, and when it comes time to stack the riser, pressure test, etc, all I can say is "I pointed that out to you on Aug 11 2020 email."

Am I going about this the wrong way? SHould I even be investing energy into correcting the engineer with the stamp?

Recent example is a two story building with concrete tees. We're adding third and fourth floors from new structural members. The underground man took the site utility and started digging. Check valve was exposed above ground (supposed to be in pit) and the FDC was connected to the underground on the system side of the backflow preventer. Now he has to dig it up, cap the tee after the backflow preventer, and run it around and inside the building. The job requires a small pump (CL1 manual wet standpipe), and the underground man wasn't happy. All I was doing was point out wrong installations before it was too late.

I'm always left thinking, "this isn't even in my scope of work, but it affects everything downstream."

​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
11 Comments

Need Antifreeze or Dry System at Dust Collector?

12/29/2020

5 Comments

 
I'm looking for guidance on protecting a bag house/dust collector at a sawmill facility.

The unit comes with outlets attached for nozzles/sprinklers. Some of the existing ones at the facility are protected with anit-freeze systems, some with dry systems. 

Is there a reason you would need to use anti-freeze in lieu of a dry system for this application?

​​​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe

​
5 Comments

Branch Pipe Always Perpendicular to Structure?

12/28/2020

5 Comments

 
Are there ever scenarios where fire sprinkler branch pipe would not be perpendicular to structure?

As I understand it, running perpendicular to structure affords installers the most flexibility in hanging locations and avoids having to use trapeze supports throughout a project where support from the floor/roof assembly isn't possible. 

Just curious if branch pipe perpendicular to structure is an always scenario or just a prevailing scenario. Thanks in advance, appreciate your all's input.

​​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments

Replace Recalled Sprinkler w/ Different K-Factor?

12/23/2020

8 Comments

 
I recently acquired a project where I'm replacing all sprinkler in a residential home. Apparently the original sprinkler heads were the OMEGA that were recalled some years ago on.

These specific heads had a K=factor of 3.9 and although I have found only one direct replacement with the 3.9 K=factor, they are not cheap!

My question is what would be an alternative replacement to these k-3.9 Omegas, and would replacements need to be the same k-factor?

​​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
8 Comments

Where to find OSHPD Hanging/Bracing Methods?

12/22/2020

4 Comments

 
I'm hoping somebody can point me in the right direction on this. I'm doing a VA Clinic in California. Somehow I didn't notice that there were OSHPD requirements but I am having trouble finding information that clearly identifies the different hanging and bracing requirements that we'd need to abide by.

I know in the past we had to use clevis hangers, rod stiffeners, use solid strut for all seismic bracing etc, but back then I was a fitter and it was on my plans already.

Where is there guidance on the acceptable hanging types to meet OSHPD requirements?

I appreciate your help.

​​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments

Dry Sprinkler System Life with Galvanized and/or Nitrogen Inertion?

12/21/2020

17 Comments

 
Any thoughts or experience in system life expectancy for dry sprinkler systems with galvanized versus black steel pipe, and compressed air versus nitrogen?

Our firm (MEP/FP consultants) typically recommends nitrogen and galvanized pipe for dry sprinkler systems, and we often get the value engineer requests to accepts compressed air and/or black steel.

Any studies or data that support your experience? Approximate cost savings you might expect from each?

Thanks in advance!

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe​
17 Comments

Are Looped Dry Sprinkler Systems Allowed?

12/18/2020

9 Comments

 
It's clear that gridded dry systems are no longer allowed by NFPA 13 (for the last 30-40 years or so), but what about a looped dry system?

If I understand it correctly, gridded dry systems are not allowed because water delivery time is typically hindered, and gridded systems may not be set up to drain particularly well.

Is that true of looped dry systems? If the total volume of a looped dry system is small (200-500 gallons), and water delivery time is not an issue, I could see major advantages to looping a dry system for areas like parking garages or attics. Thanks in advance.

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe​
9 Comments

Why Use Remote Area Other than 1,500 sqft?

12/17/2020

4 Comments

 
What would be reasons to use a hydraulic design point other than the lowest flow rate just over 1,500 sqft of remote area?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe​
4 Comments

Why Suction Pressure Doesn't Rise in Test Loop?

12/16/2020

8 Comments

 
Some fire pump assemblies have closed-test loops. When we circulate water through this closed test loop, why does the suction pressure not increase?

I'd be interested in understanding the physics of the situation a little better here.

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe​
8 Comments

How to Prevent Algae Growth in FP Water Tank?

12/15/2020

5 Comments

 
How can we prevent the formation of algae or microorganisms in water storage tanks for fire protection due to the water being stagnant?

​​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe​
5 Comments

Does Fire Sprinkler Riser Room Require Rating?

12/14/2020

11 Comments

 
I was looking through the International Building Code and have not found a requirement for a fire sprinkler riser room to be enclosed by a fire-rated wall.

Are there any requirements other than clearances to service the equipment for this room?

​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
11 Comments

Will High-Intensity Sound Activate Sprinklers?

12/11/2020

6 Comments

 
​Will high intensity sound, 200 dBP, activate either glass bulb or fusible link sprinklers?

Is there any documentation that supports either way?

Thank you.

​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments

Calculation to Determine if Pipe in Wall Freezes?

12/10/2020

5 Comments

 
We have a lot line sprinkler installation with sprinkler piping being recessed in a furred out wall. We are concerned about pipe freeze ups.

Since we are connected to the existing system that serves the entire floor it would not be feasible to do a dry pipe system or add anti freeze.

Does anyone have a good calculation to determine if the piping will freeze in the wall cavity?

​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
5 Comments

Prevent Water Through Pipe Sleeve Clearance?

12/9/2020

10 Comments

 
I have two questions on projects in areas that are seismic regions D or more restrictive and flood prone/high water table:

NFPA 13 (2016) Section 9.3.4.3 where clearance is provided by a pipe sleeve, 4 in. pipe & larger require 4 in. larger pipe sleeve. So if we are providing a below grade wall or floor penetration, that experiences high water tables and flooding.

What are the most common practices to prevent ground water intrusion through the pipe sleeve?

NFPA 13 Section 9.3.4.8 states - where required, the clearance shall be filled with flexible material that is compatible with the piping material. Is this most likely a water proofing or rated caulk?

My original thoughts lead me to something like a Metraflex Sliding MetraSeal or any pipe sleeve seal on the market, but think that would go against the internal pipe sleeve clearance requirements. Any suggestions on best practices?

​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments

When is a Storage Tank Req'd with a Fire Pump?

12/7/2020

10 Comments

 
I'm putting together design-build requirements for a new single-story construction building. The flow test pressure is borderline in my opinion so I'll be calling for a fire pump.

When is a water storage tank required with a pump?

I don't think the system needs one, but I just want to be sure.

​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
10 Comments

Software for Fire Alarm Door/Wall Audibility?

12/4/2020

6 Comments

 
Any good software resources out there for predicting fire alarm signal audibility across walls and doors based on their attenuation values and ambient sound pressure?

​Editors Note: Another fire alarm question today, love it. Keep 'em coming! You can post any fire protection-related question using the "Submit Your Question" link below at any time.

​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments

Detail Level to Provide for 120V Fire Alarm Power?

12/3/2020

6 Comments

 
As a consultant, what level of detail do you go into for the line voltage (120v) fire alarm plans and wiring?

The line voltage is affected by loads / fuse sizes and affects the disconnect switch size. I'm wondering about the level of detail that an engineer should be showing versus leaving the sizing to the fire alarm and electrical contractors based on their specific system layout requirements.

​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
6 Comments

Smoke Detectors Req'd Below Theater Balcony?

12/2/2020

4 Comments

 
We have an auditorium project with a walkway that is constructed beside the seating area at the first and second levels. The second level has been provided with beam-type smoke detectors. 

There is a suspended ceiling below the walkway which is approximately 6-feet (2 m) from the wall. Do we need smoke detectors below this suspended ceiling?
Picture
The design currently has smoke detectors only inside ceiling void spaces below the walkway - is this in compliance with NFPA 72?

The fire alarm contractor is arguing that if a fire originates at the floor level below this walkway, it will be easily detected by the beam detector at the second level due to the smoke buoyancy. 
​
​​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments

Required Clearance Around a Fire Pump Skid?

12/1/2020

4 Comments

 
Do you know of any specific guidelines for space around a fire pump skid to leave in a fire pump room?

I have always worked off the notion of "enough clearance to get around and work on a pump" but that is very subjective. So, I have a self-imposed 3-foot clearance around the edges of a skid. 

Is there anything more specific in generally adopted codes or standards?

​Posted anonymously for discussion. Discuss This | Submit Your Question | Subscribe
4 Comments

Thanks to Top November 2020 Contributors!

12/1/2020

 
​We're always thankful for the expertise and input shared with this collaborative community. The wide range of voices (from designers to AHJs, inspectors and engineers) is great. Here's a thank you to all our contributors, especially our Top Ten for November 2020:
1. Franck
2. Dan Wilder
3. Gary Lagnese
​4. I'm at Work
5. Fred
6. Glenn Berger
​7. Bruce Verhei
8. Jonathan Sullivan
9. Wayne Ammons
​10. Casey Milhorn
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT