Wire Brush or Rust Inhibitor on Sprinkler Pipe?

5/26/2023

7 Comments

 
Our condo units are 23 years old. A recent inspection of the sprinklers had some rust on the exterior of the pipes near the sprinklers.

Can we wire brush these areas and spray with a rust inhibitor, or do we need to replace all those pipes?

Are other inspections needed to see if any rust is inside the pipes or how thick the pipe steel remains?

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Glenn Berger
5/26/2023 08:04:47 am

My recommendation is to have a licensed contractor perform some non-destructive testing to determine the pipe condition. Wire brushing or spray painting will just hide the problem.

Reply
Anthony
5/26/2023 08:11:28 am

Agreed on the solution, call 1 or 2 contractors to take a look and give you an opinion.

Only 2 things cause rusting pipe water from inside the pipe or water from outside the pipe. AKA a leak or environmental factors like other leaking pipes or the like.

If the rust is caked on and 'foamy' near a joint where the pipe turns, then it's probably a leak and that portion of the pipe will need to be replaced. If all of the pipe and fittings are brown and you have a humid climate it's probably just normal exterior oxidation.

Reply
Dan Wilder
5/26/2023 08:14:41 am

Exterior rust (not from a pipe leak, just atmospheric moisture) is common and really not an issue if it's light, especially without an active leak on steel pipe. Anyone recommending replacement at that minimal level to you, I would get a second opinion (again, assuming this is not an active leak and it's limited to surface rust).

Yes, you can take a light pressure wire wheel, Brillo pad, or other abrasive means to remove surface rust from the PIPES if it's an eyesore and then paint as wanted. There are products out there that you can just spray over the rust spots as well. Any pipe, fitting, valve, and/or hanger/pipe stand can be painted, but maybe take a couple pics of the pipe stenciling to allow a future company to see the type, schedule, & MFG of the pipe before it gets covered. Do not, under any circumstance, paint any sprinkler, pressure gauge, name plate, or external moving part (reset handles, springs, and the like...ask your current inspection company when onsite next)

As for wall thickness testing, there are several options from hiring a company to perform Ultrasonic testing of the piping system (up to specific lengths), spot checks of wall thickness, and up to having sections of the pipe cut out and sent in for testing at an approved lab. (We use ECS & Dyne but there are others that are just as good)

Your current inspection company should be doing internal inspections of the piping and valves every 5 years, flowing water yearly, and external system inspections per NFPA 25 (linked below for reference). Nothing more is required but there are preventative measures available depending on your budget.

https://www.nfpa.org/codes-and-standards/all-codes-and-standards/list-of-codes-and-standards/detail?code=25

Reply
Jesse
5/26/2023 08:44:57 am

I concur with Dan, this is likely just surface rust from ambient moisture. All of the solutions posted above are sound ideas

Reply
Casey Milhorn
5/26/2023 09:34:29 am

It sounds like you are an owner of the building or condo, or at least the rep for the owner. If so, ultimately it is up to you on repair vs replacement. Two things: 1. Reliability and ability of the system to perform and 2. possible future water damage cost.

Not having any pictures, but going by the description, I would rate exterior corrosion at about a 2 out of 10 of affecting the system performance/dependability. Probably a 4 out of 10 on possible water damage concerns (depending on location of pipe: garage, in the unit, etc). If exterior corrosion is prevalent for your location, I would be even more concerned on the sprinkler heads themselves. As they say, an ounce of prevention is worth a pound of cure. Or in other words, a little $ now, or the possibility of a lot of $$$ later.

Reply
Franck
5/26/2023 03:34:14 pm

I agree with Dan and Jesse
If this is a wet system, outside corrosion might only be related to ambient humidity level (or maybe salty environment if you are near the Sea), and most of the time not a real concern for corrosion inside the pipes. Just clean it and it should be fine for another 10 years or even more.
If you have corrosion inside the pipes, this is another issue as it could expand being unnoticed until you have a failure. Or create “sediments” that may block your sprinkler orifices (especially if installed pendent).
If you have corroded sprinklers, then replace them (especially those with a fusible link).
If you have dry sprinkler system, then it is wise to inspect the inside of the piping.

Reply
Frank Savino link
6/2/2023 09:26:54 pm

The rust on the outside of a pipe is oxidized steel that provides a non reactive coating that actually inhibits further oxidation. Removing the rust will expose metal that has not been oxidized and which is susceptible to oxidation and further deterioration. Therefore, do not remove the rust. It is actually providing protection of the pipe.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT