MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Good Luck to Examinees Tomorrow

10/26/2017

0 Comments

 
Although I'm nowhere close to perfect in creating this prep material, I have thoroughly enjoyed constructing this year's set of daily practice problems and I sincerely hope they have been beneficial and helpful to you.

After the exam I'll send a brief survey to gather constructive feedback so I can improve our tools again for next year. Thank you to those who have already provided feedback about the prep guide and the website, it is greatly appreciated!

If you haven't already, consider subscribing to the weekly fire protection blog which covers takeaways on a range of fire protection subjects. 

Thanks and all the best to those taking the exam tomorrow!

​Joe
​
0 Comments

Good References for Sprinkler Stocklisting?

10/25/2017

3 Comments

 
Do you known of any good books, references, or tutorials on stocklisting for fire sprinkler systems?

Note: This is a Daily Discussion question submitted anonymously to us. Submit a Question or Discuss This Here.
3 Comments

Strobes in Restroom Stalls?

10/24/2017

3 Comments

 
A project has restroom stall walls that run floor to ceiling. There are gaps above and below the door for venting. Are strobes required in each stall? Audibility would be provided with a combination horn/strobe in the main restrooms space.

Note: This is a Daily Discussion question submitted anonymously to us. Submit a Question or Discuss This Here.
3 Comments

Seismic Restraining Strap for Seismic Clamps

10/18/2017

0 Comments

 
Question on seismic bracing for fire sprinkler:

NFPA 13
9.3.5.11 Sway Brace Installation
9.3.5.11.10 C-type clamps including beam and large flange clamps with or without restraining straps, shall not be used to attach braces to the building structure.

I typically see Cooper B-line fig.828 used, the universal seismic clamp on the beam flange. Do they have to be used with a retaining strap on the beam? Manufacturer's instructions is silent in this regard.

Note: This is a Daily Discussion question submitted anonymously to us. Submit a Question or Discuss This Here.
0 Comments

The Order of Valve Installation

10/17/2017

2 Comments

 
When reading NFPA 13 Handbook, 8.16.1.1. The figure shows several layout of valves installation. My question is what is the order to install the valves. Wet system figure shows control valve, then check valve; however the dry pipe system shows check valve first then control valve. So what is the right order to install valves? Or it doesn't matter as long as you have control and check valve?

Note: This is a Daily Discussion question submitted to us. Submit a Question or discuss this by clicking the title above.
2 Comments

Elevator Lobby Detector Requirements

10/16/2017

8 Comments

 
For an entry lobby area that is open to the floor above with a elevator on the second floor, and there is a pitched skylight for the roof. Where do you locate the smoke detector for elevator recall? I could not find any specific requirements for smoke detector location requirements in NFPA 72. 

What are the design/location requirements for a elevator recall smoke detector in this scenario?

​​​Note: This is a Daily Discussion question submitted anonymously to us. Submit a Question or Discuss This Here.
8 Comments

Logarithmic Flow Test Graph Spreadsheet

10/13/2017

1 Comment

 
Does anyone have a spreadsheet to plot a proper water flow test graph? I know it's difficult to get a semi log-semi log graph in excel. Thanks. (Email us at [email protected] and we can post it here)

Download: PDF of N1.85 Graph


Note: This is a Daily Discussion question submitted anonymously to us. Submit a Question or Discuss This Here.
1 Comment

Attach Sprinkler Pipe to Bottom Chord of Joist?

10/9/2017

0 Comments

 
For open-web steel joists systems I commonly see sprinkler hanger attachments to the top of the structural joists. When would it be permissible to attached to the bottom of the structural joist?

Note: This is a Daily Discussion question submitted anonymously to us. Submit a Question or Discuss This Here.
0 Comments

Egress Through Back-of-House Space

10/6/2017

1 Comment

 
Is there any scenario where egress is allowed through a back-of-house (storage and warehouse) space? This project has retail up front and is governed by NFPA 101.

​Note: This is a Daily Discussion question submitted anonymously to us. Submit a Question or Discuss This Here.
1 Comment

Urgent Care: Ambulatory or Healthcare

10/3/2017

2 Comments

 
Does an urgent care center fall under ambulatory occupancy or healthcare? This appeared in Weekly Exam 10 #8.

Note: This is a Daily Discussion question submitted anonymously to us. Submit a Question or Discuss This Here.
2 Comments

Air Compressor Noise for Sprinkler Systems

10/2/2017

1 Comment

 
What methods have you found to be successful to reduce the noise and frequency of air compressors for dry and preaction systems?

Note: This is a Daily Discussion question submitted anonymously to us. Submit a Question or Discuss This Here.​
1 Comment
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT