MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Typical Suppression Water Storage Tank Type?

3/31/2022

9 Comments

 
​We're looking at a fire protection system, Ordinary Hazard Group 2, that requires primary fire protection water from a storage tank.

We are looking at three options, (1) above ground insulated with a heater, (2) underground concrete and (3) underground fiberglass.

I am curious what the community here sees around the industry as being the most common choice here?

The job site already has substantial excavation going on and the job is located in the north east so freezing is a concern. There will be no private hydrant so we don't see the need to carry hose allowance in our tanks sizing.

​Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Layout Sprinklers to "Skip" Cloud Ceilings?

3/30/2022

8 Comments

 
The NFPA 13 sections on cloud ceilings continue concentrate on sprinklers above the cloud ceilings, not the sprinklers in the clouds themselves.

If the area above the cloud is sprinklered throughout, yet there are multiple clouds greater than 4-ft wide in the shortest direction (all at the same elevation plane), creating obstructions to the sprinklers above, does each cloud obstruction need to be treated independently for sprinkler coverage beneath, or can the designer “skip” clouds or portions of the clouds and gaps, as long as the overall pendent sprinkler spacing does not exceed the maximum spacing for the hazard?

I would think the opening width between the clouds would play a role in this as well, the heat's ability to skip the gap. And whether or not the sprinklers above are able to develop their spray pattern.

I often see designs with sprinklers in clouds spaced out 15' x 15' leaving some clouds without sprinklers. As far as I can tell, even the 2022 edition and handbooks are silent on this.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Ceiling Pockets with No Sprinklers in Skylight?

3/29/2022

3 Comments

 
We have a skylight scenario that's slightly different than a prior discussion here.

NFPA 13 Section 8.5.7.1.1 states:
"when a sprinkler is installed directly beneath a skylight not exceeding 32 sq.ft., the distance to the ceiling shall be measured to the plane of the ceiling as if the skylight was not present".

Two things I'm not understanding here:

1) "..sprinkler installed directly beneath..": does this mean a sprinkler in the opening, somewhere in the depth of the skylight, from the finished ceiling up to the clear glass?

2) "..as if the skylight was not present." : the way I'm interpreting this is the distance from where the sprinkler is installed (the deflector) at the lower ceiling level - or we could say at the ceiling level where the skylight opening is - can be measure as if the skylight isn't there, meaning the deflector should be placed a min. 1" down from the opening, even if from the opening to the skylight glass is say 5 feet?

If that is the case where a sprinkler is installed in this manner (so as to ignore the depth of the skylight), then here's one last proposal/query: a bulkhead is installed at a lower elevation than this ceiling level. So now, are we able to implement ceiling pocket requirements?

The total volume of ceiling pockets is less than 1000 cu.ft. in the compartment, and with the other requirements fulfilled from 8.6.7.2, we'd be able to get away with sprinklers only in the the lower bulkhead ceiling.

My issue with this though is the presence of the skylights. Hoping someone can help me out here. Thank you.


​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Diesel Pump Req' Relief Valve for Governor Fail?

3/28/2022

7 Comments

 
Does a diesel-powered fire pump require a full flow relief valve to prevent over pressurization due to a RPM governor failure?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Two Hose Valves at Top of Remote Standpipe?

3/25/2022

17 Comments

 
In Class I standpipes, I commonly see a pair of hose valves installed at the top landing (or intermediate landing) - One immediately below the other.

Is this an incorrect derivative of the requirement to calculate the two most remote outlets (at 500 gpm), or something that was required in a previous edition of NFPA #14, or is this merely a regional practice that is a result of the shared DNA of my regional contractors?

I thought I had seen an informal interpretation regarding this, but I cannot find it again. NFPA Figures do not appear to support this double-valve arrangement.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
17 Comments

Which Hydrant to Flow for Well-Gridded Supply?

3/24/2022

10 Comments

 
I'm quite familiar with conducting hydrant flow tests, NFPA 291, and have read articles such at the Sprinkler Age article from Feb. 2018. And I know the residual hydrant should be between the hydrant(s) to be flowed and the large source mains for the area.

But in terms of a specific project site (especially if the underground is well-gridded), would you chose the hydrant closest to your project to be the static/residual hydrant, or would you select the flowing hydrant to be closest to your project (and adjusting the static/residual for any elevation difference)?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Setting for Circulating Relief Valve on Fire Pump?

3/23/2022

5 Comments

 
Under NFPA 20, Section 4.20.7.1: 

The circulating relief valve shall actuate below the opening set point of the pressure relief valve to ensure cooling of the pump during churn operation.

NFPA 20 Handbook:
​
The pressure setting of the circulation relief valve should be well below the pressure relief valve setting but above the maximum suction pressure.

Based on this, how do I properly specify the circulation relief valve setting that is installed on the pressure relief valve discharge line if the pressure relief valve set point is 175 psi?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Nearby Lateral & Longitudinal Considered 4-Way?

3/22/2022

10 Comments

 
For seismic bracing, can one lateral and one longitudinal brace, attached within 2-foot of a drop to the floor below, be considered a 4-way brace?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Share & Discuss Fire Protection Drawings?

3/21/2022

13 Comments

 
This isn't really a question, but I wanted to see if anyone would be willing to share drawings they have done in the past with me?

I am looking to improve the look of our drawings, provide the AHJ with clear and concise information, and provide an all-around great end product. Thank you in advance!

If company information, logos, location, address, etc need to be removed or blocked in order to share the drawings, I understand.

Editor's note: We love this idea. If you're looking to share a sample (or set), email it to us at [email protected], and we'll update this post with images and links for discussion as they come in. Your images/drawings can be anonymous or credited, whichever you'd prefer. This could be a neat opportunity to discuss likes/improvement ideas.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
SUBMITTED DRAWINGS:
From ​Ignis Engineering:
veteran's home
TRANSFER STATION
From MeyerFire, LLC:
COFFEE HOUSE
BOWLING ALLEY
From QR3design:
NEWFOUND GOLD
13 Comments

Maximum and Minimum Pressures for FDC Sign?

3/18/2022

14 Comments

 
We have been asked to supply FDC signage for an existing building with combined sprinkler/standpipe system.

The AHJ has requested that both minimum and maximum operating pressure be included on the sign.

Can we use existing hydraulic data information or should it be recalculated including friction loss from the fire hose to pumper truck?

Also, what would constitute the maximum pressure in a combined sprinkler / Class III system?

Would it be max 175 psi at all 2-1/2” hose connections if there are pressure regulations devices on the 1-1/2” hose valves?

Thanks in advance in helping us sort this out.

​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments

Hanger Spacing for Temporary PVC Standpipe?

3/17/2022

6 Comments

 
During a recent life safety walk through of a popular boat show, I observed the installation of a temporary Class I wet standpipe system to supply various hose valves along the docks.

I noticed the 4-inch Silver-Line Schedule 40 PVC pipe was being supported randomly. I recorded distances ranging from 9 to 15 feet. I consulted with NFPA 14 then 13.

NFPA 13, Table 17.4.2.1 shows "NA" for 4 inch CPVC pipe. In viewing the cut sheets for the listed pipe, the support spacing is 7.7 feet at 73 degrees F.

My question is, is my methodology correct on how I went about getting the correct spacing in order to advise the the contractor?

Please advise. Thank you.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Cost of Sprinklers in Wood Floor/Ceiling Cavities?

3/16/2022

8 Comments

 
We have a project that is Type III-A, wood frame construction, with an NFPA 13 sprinkler system.

The client is weighing options of filling floor truss cavities with non-combustible insulation versus adding sprinkler coverage within these floor-ceiling cavities.

Does anyone have recent experience to know the relative cost impact of adding sprinklers within these floor cavities?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

An FDC Required with Dedicated Fire Water Tank?

3/15/2022

13 Comments

 
We have a project that has a dedicated fire water supply storage tank. Is an FDC required on this setup?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments

Steel Parts with 25-ft Rack Fall Under Chapter 16?

3/14/2022

5 Comments

 
We have a warehouse with all steel parts and materials. There are no pallets. 

If these parts and materials are stored on 25-foot high racks, does the design criteria of Chapter 16 in NFPA 13 (2016 Edition) apply for a commodity like this?

​Am I missing something critical here?

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Sprinkler Criteria for Small Class IB Control Area?

3/11/2022

9 Comments

 
We have a 300 sq ft control area (1 hour rated) for storage of Class IB flammable liquid. The 2018 IBC Table 307.1 permits 120 gallons (no sprinklers required), but this amount can be doubled if the building is equipped with an NFPA 13 automatic sprinkler system.

Our client would like to store about 165 gallons in the room (3 drums). The building is fully sprinklered.

What is the required sprinkler design density for this room?

We considered Ordinary Hazard Group 2 (same as lab area it supports) or Extra Hazard Group 2 (only occupancy in NFPA 13 that mentions flammable liquids).

If EH2, then the minimum water demand becomes quite large: 0.4 x 2500 + 500 gpm hose = 1500 gpm (Under the 2016 NFPA 13 - Section 23.4.4.2.5).

Could you help point us in the right direction? Thanks to all in advance for helping us hunt this down. 

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Mezzanine Stair Require Gypsum Underneath?

3/10/2022

8 Comments

 
I have an S-1 occupancy. It is a privately owned storage unit (no public access) used for the storage of exotic cars, maybe 3 vehicles in total. The space is about 1,400 square feet, and is fire sprinkler protected. There is a wood-framed mezzanine at the back of the unit as is about 300 square feet.

The question that has come up is if the underside of the open wood stairs to the mezzanine needs to be protected with fire-retardant gypsum board?

There is no sprinkler coverage under the stairs. The mezzanine may be built out by the owner to have a few chairs, a couch, a television, etc.

Digging into the code talks a lot about accessibility but not so much about the fire resistance requirements for the stairs. I have the found following in the 2015 IBC (code we are under):

1104.4 Multistory buildings and facilities. At least one accessible route shall connect each accessible story and mezzanine in multilevel buildings and facilities.

Exceptions
1. An accessible route is NOT required to stories and mezzanines that have an aggregate area of not more than 3,000 square feet (278.7 m2) and are located above and below accessible levels. This exception shall not apply to:

...and...

4. Where a two-story building or facility has one story or mezzanine with an occupant load of five or fewer persons that does not contain public use space, that story or mezzanine shall not be required to be connected by an accessible route to the story above or below.


So...the accessibility issue is covered but nothing about the rating of the stairs that I can find. Any help would be appreciated. Maybe I am not looking in the correct code section.

Thank you!

​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Software to Estimate Water Delivery Time?

3/9/2022

13 Comments

 
Is there a calculation program to estimate the water delivery time for a dry system, that works on AutoCAD?

Looking for options in this area. Thanks.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments

Advice About and When to Report Negligence?

3/8/2022

14 Comments

 
First - I really appreciate this forum. The discussions here are great - sometimes quick & easy and sometimes with a lot of depth. Also appreciate the variety of perspectives we each see the same industry. So thank you. Also - my question today isn't concerned about the people on this forum. It's clear that you care and are knowledgeable, so wanted to lay that out there.

At what point am I obligated to report negligence?

I've seen some projects out for bid that are five-story apartments with NFPA 13D issued on the drawings. I've seen hazard criteria that is (black and white) below code minimums out of NFPA 13. Underground pipe stretching 40 feet before stubbing up into a building. Not small things-big things. 

Not just missing the mark - but clearly unprofessional and probably considered to be gross negligence by some lawyers (I am not one). They're signed/sealed and put out to the world for bid.

I don't see this all the time, but it does come up. I'm not an AHJ but my guess is they'd have much worse horror stories. These things can all be corrected - RFIs or plan review or with inspections. But at what point is something so far off that it's not a mistake and is actually something that should be reported?

Are AHJs handling these things behind the scenes and I just don't know about it?

I don't want to be the bad guy and I don't feel like it's my personal fight to stand in front of each state board and state a case why someone else missed something. But at what point do I become part of the problem if I don't report it?

Do states have anonymous tips for the license boards?

Has anyone gone this route with any real effect?

Again I want to be part of the solution, not the problem, but I also don't quite feel like this is my life's crusade either. I am curious how others would go about addressing this issue and what advice you might offer to a younger person in the industry. Appreciate the conversation, thanks.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments

Recommendations with FM-200 Phase-Out?

3/7/2022

12 Comments

 
Given the HFC (hydrofluorocarbon) production phase-out, what are you currently recommending to your clients and customers regarding the installation of new FM-200 systems at this time?

Just curious to get a status check on how you approach this challenge. Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

Where is C900 Allowed for Underground Service?

3/4/2022

5 Comments

 
When is C900 PVC allowed below buildings before the transition to metallic pipe for spigot stub up?

I often see municipal rules to keep non-metallic pipe no closer than five feet from the building foundation. 

Where does this requirement come from?

I have no problem with this practice but would like some code justification to discuss this with contractors.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Calculate 3,000 sqft with Combustible Ceiling?

3/3/2022

9 Comments

 
I have a project that consists of a concrete deck and a solid decorative wooden ceiling suspended about 1-foot below the deck. I'm trying to determine if this condition would create a combustible concealed space per Section 8.15 of NFPA 13 (2013 edition). The section touches on the construction of structural elements, but not really the construction of the ceiling itself.

Unfortunately, I have not been able to verify the supporting structure of the ceiling as is difficult to access above due to its age and level of ornate detail. I also question the feasibility of being able to protect above this ceiling for those reasons.

If the space is considered a combustible concealed space and the preference is to omit sprinklers from the space, is the course of action at that point to increase the hydraulically remote area to 3,000 sf and omit protection?

​Thanks everyone!

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Hazardous Locker on Building or Separate?

3/2/2022

4 Comments

 
I wanted to pose the question on hazardous material storage lockers. We wish to protect the locker in accordance with Chapter 14 of NFPA 30 and have rated it for 4-hours to eliminate the need for fire separation distance to the immediately-adjacent main building as allowed.

The locker will not be structurally attached and will only have flashing connecting the two to keep out the elements, garbage, and animals. The locker will only have people in as necessary to get the liquids out.

The main building has a door on the "exterior wall" that opens and "reveals" the 3-hour rated hazardous material locker door, which you have to open to get inside the locker.

NFPA 30 2015 handbook Section 14.4.3 denotes that lockers over 1500 sqft should be protected permanent building such as attached buildings or warehouses. Our locker is under the 1500 sqft requirements so therefore I would say we are not a building but a "locker".

Therefore, the exterior wall openings allowances of IBC (2015) Table 705.8 would be to the lot line (over 10ft) and not the locker itself (0ft), allowing our client to access the locker from the inside of the main building and not having to go outside to access it from the exterior.

I was wondering if anyone has had a similar experience or if we should just call it part of the main building and protect it as such and lose the allowances of Chapter 14.

Thanks in advance!


​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Thanks to Top Contributors for February 2022

3/2/2022

 
Shout out to the top contributors for February 2022 - thanks for making the forum something special!
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture

Use Test Header Butterfly for Throttling Flow?

3/1/2022

7 Comments

 
When doing an annual test today for large fire pumps with a combined test header, I was told that most inspectors throttle and send water to the pitot gauges by using the butterfly valve inside the pump room and keeping the control valves wide open outside on the test header.

I disagreed with this approach, as my mentor in the industry taught me to first charge the test header and then get your pressures by opening each outside control valve individually to get your pressures. He said this is so that you don't burn up the rubber on the inside test header (normally-closed) butterfly valve. He said it happened to him in the past and then the building owner is left with a leaking test header control valve and the danger and costliness of a test header full of water.

Is there a correct way (by code) to get your pitot reading off the hose monsters outside (what I mainly using) or is charging water one way or the other simply a matter of preference?

I hope this makes sense.

I understand some test header control valves are OS&Y but most all the outside components I come across are the test hose connections that open and close via the gate valve.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT