Include Exhaust Sprinklers in Paint Booth Calc?

4/25/2025

10 Comments

 
NFPA 33, 2018 Section 9.6.2.1 reads "The sprinkler design area shall not be required to exceed the area of the booth or room in which spraying or resin application is conducted."

My project has a large downdraft paint booth for buses. There are two concrete pits (4-ft height, 3-ft width, 80-ft long) beneath the paint booth that are covered by open grate flooring.

(1) Does the above reference mean that the exhaust duct sprinklers do not need to be included in the booth hydraulic calculation?

I have a large paint booth, and it has 4 exhaust ducts.

(2) Is sprinkler protection required within the pit?

Do these heads have to be included in the booth calculation or can they be considered heads under obstruction?

If sprinkler protection was within the pit, the bags had to be regularly changed, which creates an issue for the end user and adds a large demand to the calculations. I think it would be unlikely that the sprinklers would operate in the concrete pit, as the overhead system should adequately protect the booth itself.

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Different K-Factors for Duct vs Paint Spray Booth?

9/19/2024

6 Comments

 
Can you use a different k-factor for sprinklers in a duct and plenum versus the k-factor for the booth sprinklers in a paint spray booth?

I was told I could not use different k-factors to calculate the hazard. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Same Sprinkler Cover for Inside the Exhaust Duct?

8/8/2024

9 Comments

 
We are providing sprinkler protecting inside a spray/paint booth and its associated exhaust ducts.

The question we have is if the sprinkler(s) inside the exhaust duct require the same protective covering as the heads inside the booth below.

​Thank you in advance for your input.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Design Criteria for Sprinklers in Industrial Oven?

8/6/2024

7 Comments

 
I am working on a design for a wet sprinkler system in an industrial oven. This oven has steel mandrils with fiberglass strands coated in epoxy rolled through them, heated to 350 degrees. Then, they are rolled through another machine that blows ambient-temperature air onto the mandrils to cool them down. This process forms fiberglass/epoxy-reinforced conduits.

There are (3) total exhaust ducts, one penetrating the roof and two extending 5'-0" above the top of the machine and into the open building. No dipping, flow coating, or spraying happens in this machine. Strictly heating and cooling.

I am guided by NFPA 13's rules on ducts, but I don't believe NFPA 33's design criteria would apply here. I am also guided to NFPA 13 2022 9.3.8 and A9.3.8, but I am unclear on whether 15 psi is required at each head based on the wording.

My thinking is
that a 0.2 over the whole oven would be the design criteria, protecting the hazard (OH2) in a non-FM building.
Picture
What would your design criteria for this be?

Would you calculate the heads in the exhaust ducts?

Would you put heads in the exhaust ducts that don't extend through the roof or say they're protected by the overhead system?

I have my thoughts, but a lot is left up to interpretation. Thank you for any information.

P.S. in the attached file, (2) ducts that don't extend through the roof are shown as actually extending through the roof. There is a revision drawing I am waiting on.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Foam Req'd for Diesel Generator Inside Building?

7/15/2024

8 Comments

 
The hot topic of AFFFs and PFOS. Where is the requirement stating foam must be used for fire protection for a diesel generator inside a building?

We're looking to eliminate the need for foam instead of replacing it with "fluorine" free foam.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Does Reference in a Standard Pull in Other Code?

11/28/2022

9 Comments

 
I have a project involving spray application of resin, and an exhaust system including multiple 60-ft tall exhaust stacks.

We are located in Ontario Canada, and the Ontario Building Code takes precedence. Any other codes cited need to be enacted by the OBC, or by a code enacted by OBC in order to be relevant. NFPA 13 is relevant here.

Chapter 26 (NFPA 13-2019) includes material from other codes. Section 26.4 relates to Spray Application Using Flammable or Combustible Materials, and references NFPA 33.

I have not found a reference in NFPA 13 that states that an in-duct sprinkler system SHALL be provided.

It appears to me that Section 26.4 states requirements for IF a system is provided.

Unless otherwise stated, are the requirements of Chapter 26 to be used in isolation, without enacting the full text of the other NFPA Code/Standard cited?

If another NFPA Code/Standard is cited in Chapter 26, is the full text of the cited document to be followed?

Where is the line drawn between the two documents?

I have the NFPA 13 Handbook, and the supplemental text does not clarify this for me. Thank you very much for taking the time to read through this one.

​
9 Comments

Difference Between Spray Room & Spray Booth?

7/4/2022

8 Comments

 
​Spray Room vs Spray Booth: When to use the requirements for one or the other?

I am working on a flammable spray application and was wondering if anyone has a any good metrics for when to determine if an enclosure is a "spray room" vs a "spray booth".

I am working on a 40-ft by 10-ft enclosure which I would argue is a room, but NFPA 33 provides discernable direction even with Annex sections, especially with "this definition is not intended to limit the term spray booth to any particular design." This shows up in A.3.3.19.

From NFPA 33 2021:

Spray Booth 3.3.19
"A power-ventilated enclosure for a spray application operation or process that confines and limits the escape of the material being sprayed, including vapors, mists, dusts, and residues that are produced by the spraying operation and conducts or directs these materials to an exhaust system."


Annex A.3.3.19:
"Spray booths are manufactured in a variety of forms, including automotive refinishing, downdraft, open-face, traveling, tunnel, and updraft booths. This definition is not intended to limit the term spray booth to any particular design. The entire spray booth is part of the spray area. A spray booth is not a spray room."

Spray Room 3.3.20
"A power-ventilated enclosure for a spray application operation or process that confines and limits the escape of the material being sprayed, including vapors, mists, dusts, and residues that are produced by the spraying operation and conducts or directs these materials to an exhaust system."


Annex A.3.3.20
"The entire spray room is considered part of the spray area. A spray booth is not a spray room."


Based on definitions there are no official metrics to determine when to use either definition.

Is this perhaps a constructed room vs a manufactured structure?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Is New Paint in Paint Booth Properly Protected?

1/19/2021

11 Comments

 
We have been asked if a 20+ year old wet pipe sprinkler system we installed into a paint application room is the correct method of protection for a specific paint product that is currently being used.

The MSDS sheets for a few of the products they now use indicate protection with dry chemical, foam, or water fog.

I have been told that the MSDS sheets typically refer to the product as its being stored and not necessarily as its being applied. The storage is not happening in this room of course, but in approved fire-rated storage cabinets outside the area. None of the typical requirements for alternate protection are met per NFPA 33.

Basically other than the product data sheets, this is a run of the mill paint application area. Nothing automated or fancy.

Anyone have any experience with a similar situation?

​​​​​​​​​​​​Sent in anonymously for discussion. Discuss This | Submit Your Question | Subscribe
11 Comments
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT