MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Use 4-ft Obstruction Rules for 2-ft Obstruction?

6/30/2023

8 Comments

 
I’m designing a wet system protecting storage utilizing 25.2K ESFR pendents.

I have some continuous obstructions greater than 2-ft wide (less than 4-ft wide) that require protection below the obstructions. It's under the 2018 IBC, and NFPA 13 2019 edition. The obstructions are mostly closely-spaced conduit groups.

I would like to place the ESFR pendents within 3-inches to the side of the group with the deflector 6-inches below and have listed water shields installed for intermediate level rack type protection.

Chapter 9 in NFPA 13 seems to allow this, but it is in a subsequent section dealing with obstructions greater than 4-ft wide. The verbiage and the annex figure do not clearly state the width of the obstruction.

This protection scheme will be clearly denoted and submitted to the AHJ, but I want to get input if there are any potential issues with this design.

​Any questions, comments, or concerns will be greatly appreciated!

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Hazard Classification for Gas Golf Cart Parking?

6/29/2023

6 Comments

 
I’m trying to find some back-up support for sprinkler protection hazard classification for propane (LPG) golf carts, stored at a Golf Course.

Judgement wise, I can go with OH2, as NFPA 13 says vehicle parking garages are OH1, and repair garages are OH2.

But.... is there anything included somewhere in any of the NFPA standards that addresses this specifically?

Any help is greatly appreciated.

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Does FDC Get Hydrostatic Tested Every 5 Years?

6/28/2023

7 Comments

 
Does an FDC have to be hydrostatically tested every five years?

Is that commonly done as part of a 5-year test?

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Any Ongoing AI Developments for Fire Sprinkler?

6/27/2023

14 Comments

 
Recently, my son introduced me to some examples of AI that affect my everyday routine, such as email automation and task management.

This got me wondering if there are any ongoing developments in AI specifically aimed at enhancing fire protection systems and fire sprinklers?

It seems like we are only scratching the surface of what this technology can achieve in this crucial area. Look forward to the discussion.

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments

When to Plan for 6-inch vs. 8-inch Fire Service?

6/26/2023

8 Comments

 
Is there a good dividing line for when to have a 6" vs 8" service main to a building?

Assuming light & ordinary hazard with 52,000 sf as an area limitation for a riser, is there a limit on number of risers to a 6" main?

What is the driver on how to predict that service main size?

​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Can All Fire Pump Suction Pull from One Tank?

6/23/2023

7 Comments

 
We have an underground water storage tank (concrete) with two compartments; Tank 1 and Tank 2. Our fire pumps are vertical turbine type: 1 duty and 1 back-up. Both suctions of each fire pump are located only at Tank 1.

Is this code compliant?

Or shall we relocate the suction of the back-up fire pump into the Tank 2?

Thanks in advance.

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Handrails Required on Roof Due to Standpipe?

6/22/2023

11 Comments

 
Is it a requirement to have a 42-inch handrail on the edge of the building, due to the standpipe hose connections and this needing to be accessible for the fire department use?

​If it's required, it seems that handrails could apply under IBC 2018 Section 1015.6.
Picture
Thanks in advance.

​​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Fire Alarm Pathway Survivability for K-12 Schools?

6/21/2023

7 Comments

 
Is a Pathway Survivability of Level 1 allowed for an elementary school and high school?

If not, what kind of protection would be required? Are there any performance alternatives?

Thanks in advance.

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Use Sprinklered Travel Distance with NFPA 13R?

6/20/2023

10 Comments

 
​I am in the process of bidding an existing building.

Here is the rundown: the ground level has parking. Above that is a 3-hour horizontal separation between the parking and the first floor. Then there are three stories of apartments above the separation.

I’m looking at this as two separate buildings and am proposing NFPA 13 for the parking and NFPA 13R for the apartments above.
Picture

It will also have two dry standpipes on the exterior stairwells.

My question comes to sprinkler protection on the outside exit corridors and the egress travel distance.

NFPA 13R Section 6.6.5 clearly states that the exit corridors are not required to be protected. Life Safety code allows a means of egress travel distance of 250' for a sprinklered building.

If the building is sprinklered per NFPA 13R with the above ommision, can the 250' egress travel distance be used?

Thought/Comments appreciated!

​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Why is My Air Compressor Running Frequently?

6/19/2023

12 Comments

 
Needing some help here to diagnose what might be the issue for frequent running of an air compressor for our dry sprinkler system.

Our dry system compressor runs every 5 minutes for about 15 seconds. The air gauges on the system never shows any change but the gauge on the compressor tank shows a loss of 15 pounds of air pressure on a 60 psi tank.

The compressor goes on when the tank gauge reaches 42 pounds and pumps up to 56 pounds; the compressor stays on for 15 seconds then kicks off. 

Any advice? Are the gauges reading normally? Where should I start here?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

Construction Type of Air-Supported Structure?

6/16/2023

8 Comments

 
We have a project with an air supported dome structure. It's serving around 430,000+ sqft of indoor sports.

However, I am a bit confused with the type of construction this would be clasified as.

As per NFPA 5000 and IBC, an air-supported structure can be Type II-B (000), but wouldn't we be limited on allowable floor area restrictions for the site of the building?

Are there any exceptions to sprinkler protection for a building like this?

I would really appreciate your point of view, thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Appropriate Sprinkler Height from Tall Roof?

6/15/2023

9 Comments

 
We have a production facility with a roof height of 55-ft. Someone has decided that storage sprinklers would be more appropriate.

How far from the roof would it be acceptable to install K11.2 (K160) spray sprinklers?

Is this approach even acceptable? Does the extreme height of the roof affect the best sprinkler height?

I vaguely remember Russ Fleming did a paper on the hottest point in the fire plume being some 10 % (?) of the ceiling height from the roof. Must have been 20 years ago or more.

Hopefully someone can help me with information or views on this subject on an appropriate height from the roof.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Does EIFS Trigger Sprinklers on Exterior Corridor?

6/14/2023

8 Comments

 
We have a multistory hotel building with the rooms opening to an exterior corridor. There is Exterior Insulation Finish System (EIFS) along the walls of the exterior corridor.

NFPA 13 (2022), Section 9.2.3.3 allows omission of sprinklers from exterior exit corridors where the exterior wall of the corridor is at least 50% open and where the corridor is entirely of noncombustible construction.

It seems from research that EIFS is considered combustible and would require sprinkler protection along the exterior corridor.

Has anyone done more research on this or has this come up before for other projects with EIFS in the exterior corridors and ultimately required sprinkler protection?

​Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Hydraulic Placards Required for NFPA 13D?

6/13/2023

6 Comments

 
Are hydraulic placards required for NFPA 13D systems?

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

How to Best Regulate Pressure on Combo Riser?

6/12/2023

7 Comments

 
I'd appreciate some advice.

What's the best way to regulate pressures on a combined sprinkler (OH2) and Class 3 standpipe system?

Obviously the pressures required vary between sprinklers, 2-1/2" standpipe outlets and 1-1/2" hose rack connections.

Pressure regulating valves are expensive to put in on all connections, but I was thinking about using pressure regulating valves for the 2-1/2" standpipe outlets.

I think it's great that we can all share our combined experience on this great website - thanks in advance!

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Reduce Pressure to Site Loop when FD Arrives?

6/9/2023

10 Comments

 
My community has a number of fire pump pressurized fire loop systems that include private fire hydrants.

These facilities are large industrial structures and require pressures in excess of 200 psi for their sprinkler systems. The hydrants are needed to provide water access within code required distances.

To avoid injury to fire personnel and damage to our pumper trucks, is it possible to decrease the fire pump pressure to a manageable pressure once we have arrived on site and assessed the situation?

This would allow us to operate normally while the existing sprinklers, though not at full discharge, are still adding water to the situation.

I am looking for solutions that don't involve millions of dollars or running hose for a quarter mile or more.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Does Stair Structure Have to be Fire-Rated?

6/8/2023

7 Comments

 
If a stair structure is supporting the fire barriers that enclose the exit enclosure, does the stair structure have to be fire rated as well?

Looking specifically at IBC 2018 Section 707.5.1 and NFPA 101 (2018) Section 7.1.3.2.

If there is a fire inside a stair, the means of egress is no longer usable and at that point are you protecting the interior of the building from the fire inside the exit enclosure?

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Second Valve Required on a Fire Service Main?

6/7/2023

13 Comments

 
I'm working with a city inspector who is adamant that we add a second non-rising stem valve (NRS) in the fire sprinkler service main just before the building. The first valve being in the street at the live-tap location with the roadway box.

Is a valve required on the service main before the building?

The requested location would place the valve under the sidewalk, accessible by T-handle wrench only, prohibiting reliable supervision of any kind.

I can't seem to find any language in NFPA 24 that I can use to argue against the second unsupervised valve. I don't see any value in the position the inspector has taken and requested a copy of the city ordinance requiring the additional valve.

Installing the second valve wouldn't be a huge deal but certainly seems like an unnecessary opportunity for an unsupervised valve to get closed or fail. I would like to hear what others in this community think and if anyone has something to offer.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments

Approved Pipe Material for Pier/Dock Standpipe?

6/6/2023

14 Comments

 
Has anyone designed a dry manual standpipe for a pier or dock standpipe system in the past?

My question is in regards to materials used for the pipe.

With the tides rising and falling my client is struggling to find an approved material that will allow for enough flexibility.

I walked an adjacent marina to our project and it looked like they used 4" heavy-duty rubber tubing to run out the standpipe lines and transitioned to steel only for the vertical 2 1/2" up to the hose valves on the dock.

Any information to point us in the right direction would be helpful. Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments

How to Calculate Refill from Existing Well?

6/5/2023

6 Comments

 
We have a Fire Marshal that is asking us to "show how the fill line can refill the [water supply] tank in a maximum of 8-hours, per NFPA 22 Section 14.4.2". 

The tank we're proposing will be supplied by an existing well, but we do not have information on well capacity.

What parameters should we be looking for on well capacity? Do we have to test for both flow and time? 

Is the computation on refill as simple as the flow rate (gpm) x time (8-hours) to get the contribution from the well?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Does Ceiling Rating Affect Protection Above?

6/2/2023

6 Comments

 
We have a project that is a 100,000 sqft building with an ESFR system that will be built out as offices with ceilings throughout the building.

The building and construction will all be non-combustible with no clouds or open areas. We don't know yet if all the ceilings will be rated.

Does the ceiling rating have any bearing on whether upright ESFR sprinklers will have to remain at the roof?

Thanks in advance.​

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Thanks to Top Contributors for May 2023

6/1/2023

 
Thanks to the Top Contributors that make the discussions here exceptional. Here are the Top Contributors for May:
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture
Picture

How Much Flow/Pressure for Storz Hose Line?

6/1/2023

9 Comments

 
From a firefighting perspective, how do do I calculate losses through hose lines?

How much water can flow through a 6-inch Yellow Storz hose line? What about an 8-inch? Is there a pressure associated with the calculation?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT