Door Egress Width: Deduct the Full Projection?

11/11/2026

4 Comments

 
When measuring door egress capacity width (not door clear width), projections up to 3.5 inches wide and 38 inches high are ignored in the measurement of egress capacity width.

If there is a 4.5-inch projection on one side of the door opening, how is the egress width measured?

Is it 1 inch less because the projection exceeds the allowable projection width by 1 inch, or is the measured width reduced by 4.5 inches because the entire projection is considered?

What if there is a projection that is 40 inches high on one side of the door? Is the measured egress capacity reduced by the entire width of the projection?

​Thanks in advance!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Fire Pump Req'd to Be on Backup Generator?

11/10/2026

15 Comments

 
We are on a Type IIIA, R-2, 377-unit, 5-story wood-framed project over a 6-story CIP (cast-in-place) Type IB garage, under IFC 2018, NFPA 101-2024, IBC 2024, and NEC 2023.

The sprinkler system did not require a fire pump when performing the original flow test, but now it is necessary. There is no generator in the design.

Do any of the codes above require the fire pump (and other items in the riser room associated with the sprinkler system) to be on a backup generator?

​Thanks in advance!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
15 Comments

How is Egress Width Measured for Stair?

10/16/2026

7 Comments

 
For a stairwell, is the egress width measured in-between toe-kicks, from inside of the handrails, or outside of the toe-kicks/walls?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

How Do Tire Storage Rules Apply to Aisle Width?

9/28/2026

7 Comments

 
We've been having trouble interpreting tire storage requirements regarding enforcement for our inspectors for both indoor and outdoor existing buildings within our district.

The code path: The scope of Chapter 34 - Tire Rebuilding and Tire Storage of the IFC states that tire storage facilities shall comply with Chapter 34 as well as NFPA 13, and that, particularly, storage in buildings shall also comply with Chapter 32 - High-Piled Combustible Storage.

For the Indoor Storage case: According to NFPA 13 Section 3.3.136, tire storage is considered miscellaneous and incidental to the occupancy if they don't exceed the thresholds denoted in that section.

In this case, from an egress perspective, are we correct in assuming aisle widths would be governed by IFC § 1018.5—giving a minimum of 28 inches if nonpublicly accessed and the occupant load is less than 50?

Otherwise, wouldn't the width have to be no less than that of a corridor maintained at 44 inches or greater as determined by the occupant load?

Conversely, say the area of storage outlined by NFPA 13 is exceeded, then both Chapters 34 and 32 (if storage height exceeds 6 ft as it's considered a high hazard commodity) of the IFC apply. Chapter 34 gives thresholds for on-tread vs. other storage arrangements and wheel hole alignment as they pertain to storage alongside/against adjacent walls.

Once the storage height exceeds 6 feet, does Chapter 32 trigger the full suite of fire protection requirements in Table 3206.2 based on public vs. non-public access and total storage area?

For non-rack storage arrangements, would aisle widths and egress considerations then fall to whether the building is sprinklered or non-sprinklered per IFC §3206.10.1.1 & 3206.10.1.2?

Finally, for storage that exceeds the miscellaneous tire thresholds per NFPA 13 but stays under the 6-foot height cap (meaning Chapter 32 high-piled rules don't apply), we still have to watch the total volume.

Once storage volume exceeds 20,000 cubic feet, is it automatically considered "bulk storage of tires," classified as a Group S-1, and would egress then default back to Chapter 10 aisle widths in that scenario?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Above-Ceiling Smoke Detectors for Highrise?

7/10/2026

3 Comments

 
In a highrise building with a sprinkler system designed under NFPA 13, are above-ceiling smoke detectors required?

There are limited combustible materials (wiring, steel pipe, steel ductwork) and in other areas PVC pipe.

Are smoke detectors required for the above ceiling spaces?

Should they be considered if not?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Exterior Window Allowed on Fire-Rated Stair?

7/8/2026

9 Comments

 
Is a window allowed in the exterior wall of a fire rated egress stair enclosure?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Travel Distance Right Angles vs. Natural Path?

6/16/2026

5 Comments

 
Some AHJs require travel distance to be measured orthogonally, meaning all changes in direction are made at right angles. This does result in a worst-case travel distance, but the IBC specifically says it should be measured using the natural walking path.

Generally, walking occupants do not make turns at 90-degree angles.

How do you work through this code/interpretation with AHJs?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

Do Condo Unit Doors Need Self-Closing Hinges?

12/22/2025

7 Comments

 
I have a 10-story condo building with 70 units. Each floor has 7 units, and the unit doors open to an open-atmosphere walkway with two exit stairwells at each end.

Do each unit door that swings into the unit need self-closing hinges?

​Thanks in advance for your help or guidance with this.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Tie Tenant Duct-Detectors to Building Fire Alarm?

10/27/2025

6 Comments

 
Good morning, I am in Florida and use the Florida Fire Prevention Code 8th Edition, which references NFPA 1 and 101 (2021), NFPA 72 (2019), NFPA 96 (2021), and NFPA 17A (2021).

I have a mixed occupancy strip mall that is fully sprinklered and has a fire alarm that was initially installed to monitor the sprinklers only.

One tenant upgraded the panel to accommodate a full fire alarm for their unit.

A different tenant, mercantile class C, in the strip mall has installed a hood and hood suppression system along with duct detectors for their upgraded AC system. The ducts serve only their unit and do not cross demising walls or serve other units.

My interpretation is that the duct detectors and hood suppression systems must be tied into the building's fire alarm.

Is this correct?

Another question, would this tenant then need to upgrade their unit to include pulls and notification appliances?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

FA & Occupancy Type for a Trailer Near Building?

7/28/2025

4 Comments

 
We have a project where there is one large building that has many different activities throughout. There is also a trailer that is not connected to the building by walkway or anything except some plumbing for what I believe is a restroom.

This trailer is maybe 2-4 feet away from the larger main building, and the activity being done in the area closest to this trailer is woodworking/carpentry.

I am trying to determine how the trailer should be classified to determine the requirements for a fire alarm system. I have gone back and forth between NFPA 101 and the IBC, but I am either overthinking or underthinking the scenario.

I would just like to ensure I understand the criteria correctly because these two buildings do not share exit access or an exit, but may share an exit discharge.

Would it be correct to classify the trailer as an existing business occupancy and look at Chapter 39 of NFPA 101?

If I arrive there and look at Section 39.3.4.1, it appears that the three criteria listed there, which the trailer would not meet, result in a fire alarm system not being required.

This does not sound correct but I could not piece together why. A

ny help would be much appreciated! Thanks!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Standpipe Hose Connection Allowed in Corridor?

7/16/2025

8 Comments

 
Looking for clarification on NFPA 101 Section 30.2.5.1.2, which provides an exemption for exit staircase remoteness. NFPA 14, however, requires a standpipe system in all exit staircases.

We are working on an 18-floor high-rise apartment building that has two exit staircases eligible for the remoteness exemption outlined in 30.2.5.1.2.

I would like to install a standpipe riser in the exit access corridor leading to exit staircases instead of within the exit staircase, as NFPA 14 specifies.

Is locating the hose valves in the corridor in-between allowed rather than within the exit enclosure?

Picture
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Egress Speed for NFPA 2001 Egress Time Study?

4/9/2025

6 Comments

 
NFPA 2001, Standard on Clean Agent Fire Extinguishing Systems now require an egress time study to show that the design limits exposure to halocarbon agents is no longer than 5 minutes, like FK-5-1-12 (NOVEC 1230), HFC-227ea (FM 200).

This comes from 2018 Edition Section 1.5.14, 2020 Edition Section 4.3.4, and 2022 Edition Section 4.3.4.

Exposure time for inert gas agents will depend on the oxygen levels within the space or room. Concentration below 43 percent shall be permitted where exposure is no longer than 5 minutes. Concentration between 43 and 52 percent shall be permitted where exposure is no longer than 3 minutes.

The annex of NFPA 2001 tells us to review the NFPA Handbook and the SFPE Handbook for more information.

Is anyone doing these calculations, and if so, what exit flow, movement speed, and reaction time would you consider appropriate for spaces using these systems?

​Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Can "Refuge Area" Include Area Open to Outside?

3/27/2025

3 Comments

 
We're looking at "refuge areas" per 2024 IBC (not to be confused with "areas of refuge" in NFPA 101) within smoke compartments to satisfy the requirements for smoke barriers in Group I-1, Condition 2 in the IBC.

Can the "refuge area" be calculated to include portions of the floor/smoke compartment that are open to the exterior of the building?

For example, an occupant load of 80 persons receiving care on the fifth floor of a Group I-1, Condition 2 occupancy would require a minimum of two (2) smoke compartments to be provided (420.6).

Each smoke compartment must be provided with a refuge area sized to accommodate 15 sqft/care recipient plus 6 sqft/other occupant and "areas or spaces permitted to be included in the calculation of the refuge area are corridors, lounge or dining areas and other low-hazard areas" (420.6.1).

If each side of the smoke compartment is provided with an exterior lounge/amenity area, may this be used as the "refuge area" to meet the minimum required square footage?

Picture
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments

Is Large Circulation Space a 'Corridor' in NFPA 101?

2/13/2025

6 Comments

 
Subject: Two story convenience opening separation from corridors.

NFPA 101 (2021 edition) Section 8.6.9.1 permits convenience openings for two adjacent stories. But, these convenience openings shall be separated from corridors (requirement #3) and
further states that separation should be by a smoke partition (requirement #5).

How do you define a corridor versus an open floor area or lobby per NFPA 101, since no definitions are given within the code?

Jurisdiction is required to follow NFPA 1 and NFPA 101.

For example, a building has a large assembly space on the second floor. All doors from the assembly space lead to a ~40'-0" wide circulation space (+200'-0" long in the other direction). To reach the building exit stair, occupants from the assembly room must traverse the 40'-0" wide circulation space. Within this circulation space is a ~20'-0" x 40'-0" vertical opening that connects the 1st and 2nd floor.

Should this circulation space be considered a corridor
, and should the vertical opening be prohibited from being classified as a convenience opening without a smoke partition separating from the corridor?

Or is the 2nd floor space to be considered an open floor area, with exits immediately accessible in different directions (NFPA 101 7.5.1.1.1) and not consider it a corridor?

​The width of the circulation space seems too wide to be defined as a corridor but NFPA only provides minimum width requirements for corridors, and no maximum width for a space to be considered a corridor as far as I can determine.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
6 Comments

NFPA 101 (1-hr) or NFPA 90A (2-hr) in 4-Story Shaft?

1/21/2025

11 Comments

 
NFPA references are based on current editions. While NFPA 101, Section 30.3.1.1.4 (New Apartments) allows vertical penetrations to be protected with a 1-hour rating when sprinklered, NFPA 101, Section 30.5.2 requires HVAC equipment to comply with NFPA 90A.

According to NFPA 90A, Sections 9.1.3 and 6.8.3, a higher level of protection is required for shafts that penetrate more than four floors (2-hr fire rated and fire dampers).

Does the exception provided in NFPA 101 permit reducing the required fire rating to 1-hour for duct shafts, or does NFPA 90A take precedence?

I'm curious to hear different perspectives on this.

I can understand both sides of the issue but find it challenging to justify allowing a 1-hour fire rating for a vertical exit within a New Apartment while requiring a 2-hour fire rating for the duct shafts.


Thanks in advance.
​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Smoke Purge for DoD Buildings Over 2 Stories?

11/21/2024

6 Comments

 
UFC 3-600-01 (with change 6, 2021), Section 4-29.2.1 requires a manually activated smoke exhaust system for Limited-Access Structures three stories or more in height, with 6 air changes per hour throughout the entire building.

NFPA 101 (2024), Section 11.7.3.1.2 and 11.7.3.2 outlines that if there are
no unobstructed operable openings, openable from both the exterior and interior of the building, the building is defined as a Limited-Access Structure.

Most DoD buildings have security requirements that do not permit operable windows, especially not from the exterior
or the interior. Therefore, most DoD structures over two stories in height would require these post-fire smoke purge systems; however, I have not seen them actually being implemented on projects.

Is there an alternative code path I am missing, or have you designed and installed these systems in UFC projects?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

When Does Common Path Stop for Wide Areas?

10/3/2024

6 Comments

 
I understand the definition of the "Common Path" from Section 3.3.49 in NFPA 101, but within the examples it is up to the point when you reach a corridor and have the two exit alternatives.

In a case like the one in the image shown below, the orange area is very wide, or open space, up to where they would measure the common travel distance.

At what point does the path of common travel stop in a scenario like this?

​What is that threshold?

Picture
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Exit Stair Required to Have Solid Treads/Risers?

8/22/2024

8 Comments

 
In NFPA 101, is a solid riser and a solid tread required for an Exit Stair?

See the image below that is metal tread but wouldn't have solid risers. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
8 Comments

Corridor with a Non-Exit Door at End a Dead-End?

6/18/2024

7 Comments

 
We have a sprinkler protected facility where we have a corridor that exceeds 50-ft in length.

At the end of the corridor is a door that leads to the apparatus bay. It's not a means of egress leading to an exit (higher hazard on the other side). The required means of egress are at other locations in the facility.

Is this considered a dead end corridor under NFPA 101?

In all the examples I've found on the topic, the end is truly dead-end with no means of exiting.

What's your take on this? 

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Difference Between "Permitted" and "Required"?

5/10/2024

5 Comments

 
What is the difference between the terms "permitted" and "required" in NFPA standards?

For example, a later chapter will say that "Smokeproof enclosures complying with 7.2.3 shall be permitted.", which will point you back to:

7.2.3.1 General. "Where smokeproof enclosures are required in other sections of this Code, they shall comply with 7.2.3, unless they are approved existing smokeproof enclosures."

The "parent" section uses the phrase "where 'required' elsewhere", while the occupancy-specific section uses "permitted", as in allowed to be required, without specifically requiring it.

This feels very cyclic.

Am I directed back to the separation requirements of Chapter 6, or is there something buried in the occupancy chapter that I am not seeing?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

When is Deluge System Required for Stages?

4/3/2024

12 Comments

 
What are the deciding factors or requirements on when a deluge system would be required on a stage to separate the stage from the audience?

This would be for the proscenium opening protection.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
12 Comments

Use Sprinklered Travel Distance with NFPA 13R?

6/20/2023

10 Comments

 
​I am in the process of bidding an existing building.

Here is the rundown: the ground level has parking. Above that is a 3-hour horizontal separation between the parking and the first floor. Then there are three stories of apartments above the separation.

I’m looking at this as two separate buildings and am proposing NFPA 13 for the parking and NFPA 13R for the apartments above.
Picture

It will also have two dry standpipes on the exterior stairwells.

My question comes to sprinkler protection on the outside exit corridors and the egress travel distance.

NFPA 13R Section 6.6.5 clearly states that the exit corridors are not required to be protected. Life Safety code allows a means of egress travel distance of 250' for a sprinklered building.

If the building is sprinklered per NFPA 13R with the above ommision, can the 250' egress travel distance be used?

Thought/Comments appreciated!

​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Does Stair Structure Have to be Fire-Rated?

6/8/2023

7 Comments

 
If a stair structure is supporting the fire barriers that enclose the exit enclosure, does the stair structure have to be fire rated as well?

Looking specifically at IBC 2018 Section 707.5.1 and NFPA 101 (2018) Section 7.1.3.2.

If there is a fire inside a stair, the means of egress is no longer usable and at that point are you protecting the interior of the building from the fire inside the exit enclosure?

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Water Curtain vs. Rated Door on a Loading Dock?

5/31/2023

10 Comments

 
Water curtain using automatic sprinklers to avoid providing opening protectives - there's a lot of confusion on this.

Exception stated under Section 705.8.2 of 2021 International Building Code (OBC) states that Opening protectives are not required where the building is equipped through an automatic sprinkler system in accordance with Section 903.1.1 and the exterior openings are protected by a water curtain using automatic sprinkler systems approved for that use.

Can we use this exception and provide a water curtain using automatic sprinklers to avoid fire rated doors in the loading dock of a building?

Is there anything else that I need to be concerned about while designing these sprinklers for the water curtain?

Need more clarity here before recommending an approach. Thanks in advance. 

​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

What Drives Detection for Chemical Plant?

5/4/2023

8 Comments

 
What code or standard prescribes the location and/or number of heat / smoke / gas detectors needed for an industrial / chemical plant?

We have an open steel structure with processing equipment on most floors, which are essentially grating – no roof and no walls – containing flammable and toxic chemicals. 

We’ve planned to place some detection in strategic spots downwind of the flare (southmost) and tankfarm (same flammables) and there are some single-story buildings and other outside equipment like a cooling tower, nitrogen generation, boiler – all downwind of the tankfarm and open structure mentioned. 

So, some of all types where personnel could be in any area especially the lab/control room and electrical building mentioned above.  The modular building supplier may have those taken care of but I need to check behind them. 

The majority are outside and in the nine-story structure.  I plan to have flame and gas detectors throughout depending on the correct guidance.  Thanks in advance for your take!

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
<<Previous
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT