I have observed forward-flow tests of backflow preventers, and fire pumps tests, that are conducted through 2.5-inch nozzles identical to the image below, but without the playpipe tip screwed onto the end of the nozzle.
Image Link The pitot reading was taken off the 1-3/4" threaded end of the nozzle where the playpipe tip gets screwed on. Is this approach acceptable, and would the GPM table for the 1-3/4" butt for converting the pitot pressure to flow be acceptable? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Dan Wilder
10/10/2023 08:46:06 am
As long as the measurements are taken from the correct location per NFPA 291 for the discharge orifice size and the corrected Coefficient is used, this is acceptable. Just make sure that the hose between the two points isn't too long and creates excessive friction loss and skewing results.
Reply
Eric R
10/10/2023 08:53:25 am
I think it would depend on what kind of test you are performing, and what level of precision is needed.
Reply
Anthony
10/10/2023 08:58:31 am
NFPA 291 will say the reading from the hydrant should come from:
Reply
David Kendrick
10/10/2023 09:22:02 am
Curious, I've read this comment several times about hose length.
Reply
DAVE
10/10/2023 01:33:46 pm
That has been my belief as well, and have argued the same. I think we purched 3" diameter hose material just to have the ability to crank the gpm to #11.
Reply
Ivan Humberson
10/11/2023 07:31:39 am
David, I totally agree. As long as the static and residual pressures are taken at the source, where the flow characteristics need to be determined, the length of hose will have no effect on the characteristic flow curve, other than the data point while flowing water may be a lower gpm due to the friction loss in the hose.
Reply
Glenn Berger
10/10/2023 04:03:38 pm
As long as the calculations are based upon the true flowing orifice the test results should be acceptable.
Reply
James Art. FPE
10/21/2023 08:59:38 pm
Using a Playpipe is fine! Great Idea.