Sprinklers for Generator in Detached Building?

9/4/2026

8 Comments

 
Is there an NFPA requirement that mandates sprinkler protection of a generator room that is in a separate technical service building? 

If so, what is the hazard classification for the generator room? Is there an equivalent of a 6.5 L/min.m² foam-water system under NFPA-specific requirements?

Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Ground Wire on Secure or Unsecure Side of SCIF?

9/2/2026

11 Comments

 
For a SCIF, where should the ground wire be bonded?

We have a project where #4 AWG ground wire is to be bonded to sprinkler (water) piping of the penetration
, but does that need to occur on the secure side or the unsecured​ side of a SCIF?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments

Forward Flow Test: Flow & Pressure, or Just Flow?

8/31/2026

14 Comments

 
We are having a debate between our office and the field.

What numbers are we looking for at the initial forward flow test?

The office claims we are looking for the full flow possible from the riser testing arrangement, with a minimum flow rate equal to system demand. Pressure is to be noted but not have a requirement. (The pressure is to be noted for future tests to assess system degradation.)

The field claims we are looking for Flow and Pressure of the demand of the sprinkler system. Achieve flow and throttle the discharge to achieve the sprinkler system minimum required pressure for system acceptance.

NFPA 13, 2019 Edition, Section 16.14.5.1 and A.16.14.5.1 address this "tests at a minimum flow rate of system demand including hose allowance where applicable" and the appendix "this test is only concerned with testing at the proper flow rate."

What are your thoughts?
​
Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments

Reason for Differences in Flow Test Results?

8/25/2026

13 Comments

 
We are working on a school project that needed a 1,000 gpm fire pump due to three standpipes.

We initially did a hydrant flow test and had a flow of 425 gpm with a static of 55 psi and residual of 50 psi when we started the design
. By the time it went out to bid and the contractor performed their own test,​ they flowed 354 gpm with a static of 55 and a residual of 50.

In the first test, we got 1215 gpm at 20 psi, and 1012 gpm in the second test. They went to turn on the pump and were only getting 368 gpm when the building inlet pressure was at 20 psi.

We re-did the flow test to see what changed so drastically and again got a static of 51 with residual of 46 at 375 gpm, which would give us 1004 gpm at 20 psi.

We have confirmed the two valves between the street and
the building are fully open, and we only have about 50 feet of 8” pipe, so the pressure drop to the building is negligible, especially at 368 gpm.

We are at a loss for what could be causing such a difference in pressure to the building and such a low flow.

​Has anyone ever run into an issue like this or have any suggestions of what else we could check out?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments

Physical Separation Between Different Hazards?

8/24/2026

4 Comments

 
We have a project under NFPA 13 with different hazard classifications on the same floor. I’m designing a sprinkler system using the density/area method.

If different areas on the same floor have different occupancies and contents, for example, an OH1 workshop adjacent to an OH2 storage area, can the boundary between the two hazards be based simply on the different use/occupancy and materials present?

Or does NFPA 13 require a specific physical separation or fire-rated compartmentation between them in order to use different hazard classifications?

How stringent are these separation requirements?

​I’m not referring to the Room Design Method. Thanks in advance


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Estimate Sprinkler Count Above Coverage Area?

8/19/2026

6 Comments

 
For those of you who have designed sprinkler systems in old or existing buildings, is there any common rule of thumb for how much the sprinkler count tends to increase because of irregular geometry, existing walls, small rooms, etc.?

In my case, I’m ending up with roughly 20–30% more sprinklers than what I would get from simply dividing the total protected area by the maximum allowable coverage per sprinkler.

Does that sound normal for an existing building, or would you consider that excessive?

​Thanks in advance!


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Percent Polyethylene in Container to be Group A?

8/18/2026

1 Comment

 
Regarding NFPA 13 2025, how much polyethylene can you have in a composite container without classifying it as a Group A plastic?

Is it a maximum of 15% of the total weight?

This container will store non-combustibles, also on a plastic pallet. I guess if you can
classify the container/product as a Class IV, then the classification of the total storage unit will be Cartoned Group A Plastic?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
1 Comment

Pendent Sprinklers for Basement with 10" Joists?

8/17/2026

10 Comments

 
We installed a basement with pendent sprinklers where the deflector is 1” below the bottom of the wood joist that is 10 inches deep, and the AHJ says that pendent sprinkler heads are not acceptable because heat goes into the bay and delays sprinkler activation.

If the sprinkler is installed 1” below the timber joist, can we consider it as unobstructed construction?

If the deflector is installed 11 inches below
the roof ceiling and NFPA 13 2019 edition establishes that the distance between the deflector and the ceiling is between 1 and 12 inches for upright and pendent sprinklers, why can we not use pendent sprinklers?​

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Sprinklers in Any Lower Ceiling Over 48" Wide?

8/14/2026

6 Comments

 
Is my understanding of NFPA 13 (all recent editions) correct in that any ceiling projection down that is over 48" wide must have sprinklers in the lower ceiling/soffit?

The specific scenario: a 5-foot-wide x 25-ft-long gyp board ceiling above a nurses station. The vertical distance between the 2 ceilings is 0'-3".

Even with the pendent sprinklers installed in the higher ceiling more than 12" away from the vertical face (which meets other obstruction rules), code tells me sprinklers shall be installed in the 5 ft wide lower ceiling (because it exceeds the 4 ft wide threshold) even though the sprinklers in the higher ceiling are not obstructed.

What's your take on this?

Thanks in advance.

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Non-Expanded Plastic as Class IV or Group A?

8/13/2026

9 Comments

 
I've got a question regarding commodity classification in a facility with a sprinkler system designed for Cartoned non-expanded Group A Plastics.

The owner wants to store high-weight non-combustibles inside plastic containers, see picture. 
Picture
The total weight of plastics will not exceed 15% of the total weight.

Is there any chance the storage unit can be treated as a Class 4 commodity and raised to Cartoned Group A Plastics due to the plastic pallet?

Or is it necessary to treat the commodity as Exposed Group A Plastics because of the plastic container? 

Thanks in advance.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Prevent FD from Drafting Too Much Tank Water?

8/12/2026

8 Comments

 
I have a project right now that the sprinkler system is being supplied from a tank and pump because the only water available is 25 gpm from a well. The AHJ refuses to allow NFPA 1142 for mobile apparatus to supply fire flow, saying it has to be a "fixed" system. However, he does let me use NFPA 1142 for fire flow rate.

I've added an additional 30,000 gallons to the tank for the 250 gpm fire flow for 2 hours. The AHJ just says to add a connection to the tank so the fire department can pull directly from the tank.

The problem I'm running into is how can I be sure the fire department only uses 250 gpm so they don't rob the sprinkler system of any water?

​I don't have any experience doing this. Any advice or guidance you could provide would be greatly appreciated.

​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Sprinklers Required with Combustible Insulation?

8/11/2026

9 Comments

 
Are sprinklers required in a noncombustible concealed space that contains combustible insulation?

I have a contractor who is trying to use polyurethane spray foam insulation in a noncombustible concealed space above a ceiling. It is an NFPA 13 system and they do not want to sprinkler it.

To my knowledge, this spray foam insulation is combustible, and by filling a noncombustible space with it, it will need sprinklers. They are trying to propose intumescent paint, but I don't believe that changes anything for them.

Do you all know of any applicable exceptions in this situation or if they don't need sprinklers?

I think 9.2.1.13 is the only relevant section from 13, but I am having trouble finding whether this foam exceeds the 1,000BTU per square foot. Thank you.

​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments

Way to Tell Flexible Coupling vs. Rigid Coupling?

8/10/2026

10 Comments

 
Is there an easy way for AHJ inspectors to tell the difference between a flexible coupling and a regular coupling?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments

Pump & Storage Tank for Sprinklers & Hydrants?

8/6/2026

6 Comments

 
A project we're looking at has a hydrant network that connects to fire sprinkler systems and hydrants. 

What would be the process we'd need to consider for the water supply (fire pump and tank capacities)?

How does the greatest sprinkler system demand (possibly with hose allowance) relate to the hydrant demand? Are they additive? 

Not all buildings could have sprinkler systems in the future, so we're questioning the relationship between sprinklered building system demands and the fire hydrant demand.

Thanks for your input.
​

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Can Check Valve Be Removed from Zone Control?

8/5/2026

8 Comments

 
When would we be permitted to remove a check valve from a zone control valve?

Like, what are the requirements for needing it one way or another? 

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

How to Arrive at 2,000 sqft CMDA Design Area?

8/4/2026

8 Comments

 
I have a CMDA wet system, protecting solid-piled Group A Plastics storage. The storage height will be under 12 feet.

Under Section 21.3.3(a), I have been led to the density of 0.60 gpm/sqft in Column C, over a remote area of 2,500 sqft. The 2,500 sqft remote area is what's getting me; it seems cut and dry that in my situation, I am stuck there unless I have a closed storage array.

I wanted to verify against other people's interpretations: are there any other ways I am missing that would allow the area to be brought down to 2,000 sqft?

I primarily ask because I have seen other systems in the field with areas of 2,000 with densities 0.40, 0.50, 0.60, and I'm unsure of how those systems have gotten to that point with the current codes.

​For clarity, I am using the 2022 edition of NFPA 13. Any input would be appreciated. Thanks.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments

Why Did FM Data Sheet 8-1, Table 1 Change?

8/3/2026

4 Comments

 
Does anyone know any background on the changes to Factory Mutual Data Sheet 8-9, Table 1?

The table used to use a set of formulas for all designs, which would apply a shape factor of 1.2 or 1.4 depending on ceiling construction/slope. It appears to have been updated in July of 2025, with changes being brought in that would allow 12 sprinkler designs to be calculated on the basis of 3 heads on 4 branch lines rather than using the old formulas, which, based on minimum spacing, was not possible for this to occur.

There
are no comments in the back or anything on FM’s website linked to testing that supports that change; any help would be appreciated.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Wet Sprinkler Zone Next to Pre-Action Zone?

7/31/2026

7 Comments

 
In an open, fully sprinklered building, can 50% of the floor area be protected by an automatic wet system, while the remaining 50% is protected by a pre-action system?

There is no wall separating the two areas. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments

Insulation, Protection for Exterior Sprinkler Riser?

7/28/2026

6 Comments

 
For an exposed exterior riser on a wet system, is insulation or mechanical protection required?

If so, what type of insulation is best?

​This is in the Orlando, FL area.

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
6 Comments

Connect Offices to Nearby ESFR System Main?

7/22/2026

5 Comments

 
There's an existing system in a warehouse with a pump. It's a grid system with an 8" main and 1" 17k ESFR sprinklers.

The main is in a 3' wide inaccessible "hallway". They added office space that will require 15 heads. There's a 4" floater main nearby.

Can I connect to the 4" main to feed the added sprinklers? What do I need to consider in doing so?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
5 Comments

How to Address Edge Beam Pocket with ESFRs?

7/21/2026

10 Comments

 
I am designing a 25.2k ESFR system in warehouse with purlins set on tapered beams with about 8" wide flanges spaced 20' on center. The last beam in the project area runs 1'-5" off the wall creating a small beam pocket along the length of the wall.

Current head spacing is 10'x10', and 18" below ceiling. The sprinklers adjacent to the beam are 3'-10" from centerline, or 5'-3" from the wall. This would require heads within the beam pocket, but the clearance between the wall and beam would obstruct sprinkler discharge.

Are there any special exceptions that would allow heads to be omitted from the pocket?

Or how could I approach this condition differently to meet code?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
Picture
Picture
Picture
10 Comments

How to Hang Sprinkler Pipe from Pyro-Bloc?

7/17/2026

6 Comments

 
I have a retrofit application where the sprinkler system needs to be supported from Pyro-Bloc, as that is what is making up the structure of the floor above. NFPA-13 (2022) does not allow the use of toggles (that's what the plumbers and mechanical contractors are using), and the material is too brittle to use drop-ins or expanding anchors.

Any recommendations on how to support the piping?

This is specifically 2" and larger. Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Code that Limits Flex Drops Above Hard Ceilings?

7/14/2026

6 Comments

 
Is there any relevant code or standard that restricts the use of flexible sprinkler armovers above hard ceilings?

Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
6 Comments

Equivalent NFPA 13 "Grouped Obstructions" Calc?

7/7/2026

4 Comments

 
Hello, Following FM DS 2-0 §2.5.4.5.3.3 - if two or more objects are considered a “grouped object”, their overall width is the collective sum of each of the objects that make-up the grouped object; the open spaces between them do not need to be included in the calculation.

Is there an equivalent in NFPA or do I need to take into account the open spaces if my project is in NFPA 13?

Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
4 Comments

Treat (3x) Tires On Tread as Portable Racks?

7/6/2026

3 Comments

 
We have a car dealership with tire storage on rolling racks on fixed rails similar to file storage systems. The tires are on tread and stacked 3 tires high.

​Would this be designed as open portable racks or should I be considering a higher density for when the racks are all pushed together?


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
3 Comments
<<Previous
    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT