Advice About and When to Report Negligence?

3/8/2022

14 Comments

 
First - I really appreciate this forum. The discussions here are great - sometimes quick & easy and sometimes with a lot of depth. Also appreciate the variety of perspectives we each see the same industry. So thank you. Also - my question today isn't concerned about the people on this forum. It's clear that you care and are knowledgeable, so wanted to lay that out there.

At what point am I obligated to report negligence?

I've seen some projects out for bid that are five-story apartments with NFPA 13D issued on the drawings. I've seen hazard criteria that is (black and white) below code minimums out of NFPA 13. Underground pipe stretching 40 feet before stubbing up into a building. Not small things-big things. 

Not just missing the mark - but clearly unprofessional and probably considered to be gross negligence by some lawyers (I am not one). They're signed/sealed and put out to the world for bid.

I don't see this all the time, but it does come up. I'm not an AHJ but my guess is they'd have much worse horror stories. These things can all be corrected - RFIs or plan review or with inspections. But at what point is something so far off that it's not a mistake and is actually something that should be reported?

Are AHJs handling these things behind the scenes and I just don't know about it?

I don't want to be the bad guy and I don't feel like it's my personal fight to stand in front of each state board and state a case why someone else missed something. But at what point do I become part of the problem if I don't report it?

Do states have anonymous tips for the license boards?

Has anyone gone this route with any real effect?

Again I want to be part of the solution, not the problem, but I also don't quite feel like this is my life's crusade either. I am curious how others would go about addressing this issue and what advice you might offer to a younger person in the industry. Appreciate the conversation, thanks.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
14 Comments
schulman
3/8/2022 08:09:07 am

The responses here should be an interesting read ....

As someone whose job it is to do Preliminary System Drawings that are then turned into actual Shop Drawings and Hydraulic Calculations (... product data), I can tell you that I see a lot of problems come back to me for review. I also often see practices in the field that are questionable. I try not to leave it to the AHJ .. I try to help ... at the end of the day I'm glad I'm not the "signer" on some of these jobs.

Also, if anyone ever sees something wrong with my drawings, I would hope they would tell me.

Reply
Todd Wyatt
3/8/2022 08:24:24 am

Report possible Code deficiencies to the "building official" (AHJ) and/or the building department that issued the Building Permit.

If the project is in the Construction phase, the automatic sprinkler system (ASPS) design submitted for review for permitting was checked for general conformance (e.g. "where an automatic sprinkler system is provided ... whether the sprinkler system is required") but the actual design of the ASPS (including calculations) is typically a "deferred submittal" (see 2021 IBC 107.3.4.1 Deferred Submittal https://codes.iccsafe.org/content/IBC2021P1/chapter-1-scope-and-administration#IBC2021P1_Ch01_Sec107.3).

The professional responsible for the ASPS is required to submit the deferred submittal to the AHJ for review. The ASPS is not permitted to be installed until the AHJ approves the deferred submittal.

Most building departments have websites that permit the public to confer with building officials including reporting possible Code violations. Here's a list of American State Building Codes :
https://www.buildingsguide.com/blog/resources-building-codes-state/

Good luck ...fight the good fight.

Reply
Jon
3/8/2022 08:29:43 am

The answer depends. Are all of the example mistakes you mentioned committed all by a single engineer? Or are you noticing mistakes from several different engineers? Licensed engineers are required to comply with ethics rules and that usually requires that they practice within their areas of expertise.

Unfortunately, fire protection falls under the responsibility of a mechanical engineer in smaller firms. Not that mechanical engineers don't know what they're doing, but it could be argued that fire protection is not within their area of expertise if they don't have enough experience with it.

Speaking overall, you have highlighted an issue that is known by many people and its a symptom of not enough qualified people in the fire protection industry.

I don't think what you are describing is true negligence, but rather mistakes or human error. I would continue to point out mistakes where you see them, and follow the proper channels (RFI's, etc.) to point them out. Include solid references from codes and standards in the RFI's to hopefully grab someone's attention and get the problem fixed.

Reply
Anthony
3/8/2022 08:41:55 am

I think there is a difference between code deficiencies and criminal negligence. At the end of the day you want to go home knowing you didn't put anyone in danger.

This site has tons of free resources to make every one better. Share some of the material!!

Reply
Dan Wilder
3/8/2022 08:45:50 am

For bids, preconstruction RFI's (this also provides insight to others that we are bidding against) or we address things in our inclusions/exclusions once we send the bid over.

If the job is ours and drawings are provided after the fact (depending on the working relationship with the EoR), we may ask for a short meeting to discuss items and give them the chance to revise their drawings and possibly save some face....issue with that is either they make changes and we get a change order or they don't change and we issue RFI's with cost impacts but in both cases, there is typically a monetary issue that causes some heartache.

There are some EoR's that just don't want to work with process and we just go the GC route and let things fall. It typically involves calling out very specific items out of NFPA to justify our position or to define why their drawings are incorrect. Most of our work is design/build anyway so we are ultimately responsible for the end product but if the direction is incorrect, the paperwork trail begins.

Reply
Ralph Foster link
3/8/2022 08:48:39 am

Your question does not have an easy answer.

If you are a licensed engineer, then you have a responsibility to report incompetence practice or gross negligence to the licensing board. This is problematic because incompetency practice takes a patter to establish - inn simple terms you need to refer multiple projects showing the engineer is incompetent. The issues should be black and white like your example of an NFPA 13D system for a n apartment building.

Gross negligence involves something that will involve loss of life. Like the building will collapse because the structure was not designed to support the load in the building. In our world, an example of this would be a manual standpipe for a high-rise building.

Another wrinkle is when the issue was an Alternative Method of Design the code official approved. There are specific procedures for this, but because of training or experience, I've seen some horrible Alternative Method code official have approve. And yes a code official can be referred to their licensing board too.

If/When if you make a referral to a licensing board (Engineer, Architect, Code Official, or Contractor) be sure you explain the issue in black and white terms because the person investigating is likely not to understand the code related issue.

Referral usually lead to blow back from the person you refer. Loss of future work, animosity, and getting a reputation for referring people. I have experienced all of these for referral I have made. I am OK with all of this garbage because I did the right thing protecting the public. As someone else said - Fight the Good Fight!

Reply
Jesse
3/8/2022 08:52:09 am

My state, Texas has a pretty organized state licensing board through the State Fire Marshal's Office with is a law enforcement agency. They investigate administrative and criminal matters.

However, I often see a lot of just completely wrong information in specification documents. I have one project right now a year behind because the architect indicated on sealed drawings the project would have a Class I Automatic Wet Standpipe. The project doesn't even require a manual standpipe by IBC or 14, much less an automatic. Suffice to say the architect doesn't know what any of that means.

In our world, words have meaning and being precise is important. Words like "storage, racks, flammable, etc" all have very clear yet narrow definitions to us, but those outside our world use in a utilitarian way. I've had automatic sprinkler plans rejected for OH2 designs because the building set referenced "storage".

I think its often that those not in our field don't know what they don't know. They don't know the difference between 13, 13R, 13D.

While negligence is out there for sure.. I think there is a lot more ignorance. Thankfully, we can help fix ignorance.

Reply
martin m
3/8/2022 09:19:00 am

"See something say something" we are professionals and have an ethical duty to protect the public

Reply
chad
3/8/2022 09:19:45 am

I emphasize with your situation as an AHJ. The PE licensing board's (in general) see this is a non-issue. Until it isn't. Like there is a long history and pattern of complaints. Or something was built wrong and it collapses or someone dies.

Otherwise... Oh its just a mistake, no harm no foul. They do not see it as negligence, at least not gross.

There are some RDP's/PE's that will stamp anything they can get paid for. Its sad. Unfortunately, unless we all harp on the really bad ones, nothing will change. I want to be clear, no one is perfect, mistakes happen and we shouldn't down on everyone. But call a spade a spade

Reply
Karsten Smith
3/8/2022 09:26:30 am

In the state where I live we are required by law to report anything that is incorrect to the AHJ. See something, say something. Which we do, often. That being said we do try to work with everyone to effectively communicate the issues before reporting to the AHJ. Most of the time it is ignorance like Jesse said not negligence. Notifying the AHJ clears the conscious and reaching out to the person who may or may not have made the mistake builds a great network of helping people in the industry. I always appreciate someone telling me I am wrong. That is how we learn.

Reply
Glenn Berger
3/8/2022 09:38:50 am

Be careful on the difference between gross negligence and just an error/omission.

Reply
Alex
3/9/2022 08:13:23 am

The last thing you want to do is call someone out for a simple error/omission. We all make mistakes and are on the same team, if you ask me. If its a one off case, I would just jump on the phone to discus with the engineer/designer.

If its repeated and gross negligence, I would notify the AHJ.

Reply
Manny Rios
3/8/2022 10:20:38 am

In our jurisdiction the AHJ is the State Fire Marshal. All plans for life safety systems are reviewed/plan checked by them, and any discrepancies are/will be addressed to prior to the release of said plans for construction. They have an open line of communication for questions/issues however minor they might seem. See something, say something!!

Reply
Pete H
3/8/2022 11:56:49 am

Depends your jurisdiction.

If you're in a jurisdiction that pins code compliance on the installing contractor as opposed to the bid plans engineer-of-record... then you don't report it. It's the duty of the installing contractor to catch these errors, RFI their bids, or adjust their prices for a code compliant system (and to suggest just letting their in-house guys VE the project.)

If you're in a jurisdiction that pins code compliance on the initial bid set... then report to whoever the initial bid set is submitted to as the AHJ if it somehow got past them with one of the scenarios you described.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Aug '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT