Mezzanine Stair Require Gypsum Underneath?

3/10/2022

8 Comments

 
I have an S-1 occupancy. It is a privately owned storage unit (no public access) used for the storage of exotic cars, maybe 3 vehicles in total. The space is about 1,400 square feet, and is fire sprinkler protected. There is a wood-framed mezzanine at the back of the unit as is about 300 square feet.

The question that has come up is if the underside of the open wood stairs to the mezzanine needs to be protected with fire-retardant gypsum board?

There is no sprinkler coverage under the stairs. The mezzanine may be built out by the owner to have a few chairs, a couch, a television, etc.

Digging into the code talks a lot about accessibility but not so much about the fire resistance requirements for the stairs. I have the found following in the 2015 IBC (code we are under):

1104.4 Multistory buildings and facilities. At least one accessible route shall connect each accessible story and mezzanine in multilevel buildings and facilities.

Exceptions
1. An accessible route is NOT required to stories and mezzanines that have an aggregate area of not more than 3,000 square feet (278.7 m2) and are located above and below accessible levels. This exception shall not apply to:

...and...

4. Where a two-story building or facility has one story or mezzanine with an occupant load of five or fewer persons that does not contain public use space, that story or mezzanine shall not be required to be connected by an accessible route to the story above or below.


So...the accessibility issue is covered but nothing about the rating of the stairs that I can find. Any help would be appreciated. Maybe I am not looking in the correct code section.

Thank you!

​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H.
3/10/2022 07:13:38 am

Okay, beyond IBC, what nfpa standard were the sprinklers in the building installed? I'm assuming NFPA 13 (I'm using 2016 edition, but I think you might be in 2013 due to your edition of IBC being 2015, so you may want to check that). because despite being private, this hasn't been described as residential.

(If residential sprinklers are used in NFPA 13, please refer to 8.10.6.3.2 and 8.10.7.3.2 in the 2016 edition which call for sprinklers under all fixed obstructions over 4'-0" wide, such as stairways)

NFPA 13 also guides for 8.15.3.1 (the section on combustible construction, assuming the wood is combustible) that sprinklers shall be installed beneath all stairways of combustible construction.

Reply
Jesse
3/10/2022 09:05:40 am

The lack of protection under the stairs combined with the lack of a fire barrier is concerning. I would imagine the stair way creates a shielded area to ceiling level sprinklers - and would continue to do so even if gypsum was installed.

Reply
Alex
3/10/2022 09:06:02 am

Hi,

From the question, there is not enough information to answer if you're permitted to have a combustible stairwell according to the IBC. That will drive your primary question regarding adding gypsum to the bottom side of the stairwell.

Although, I wanted to point out the following:

NFPA 13 (2013) 8.15.3.1 states that sprinklers must be installed beneath stairways of combustible construction.

NFPA 13 (2013) 8.10.6.3.2 states that sprinklers must be installed under fixed objects over 4'-0", such as stairs.

Either way, depending on the overall width, you may need to install sprinklers beneath the stairwell.

Reply
Todd Wyatt
3/10/2022 09:36:30 am

The adopted IBC (or IRC) is the starting point to determine the scoping requirements of the automatic sprinkler system (ASPS) per the "addition" of the mezzanine. You referenced the 2015 IBC.

The first issue to address is whether the 2015 IBC or the IRC (International Residential Code) is applicable. Per the 2015 IRC, "Garages and Carports" are addressed in Section R309. R309.5 Fire Sprinklers includes requirements for "private garages". If the garage-in-question is an "accessory building" ("a structure that is accessory to and incidental to that of the dwelling(s) and that is located on the same lot") to a single-family dwelling, I would recommend you clarify with the building official IF the 2015 IRC should be used (instead of the 2015 IBC) to evaluate the ASPS requirements for this garage.

I will continue as if the garage is to be evaluated per the 2015 IBC.

The second issue to address is to verify the Occupancy Classification (OC) of the private garage. You state that it is a "Group S-1 Storage Moderate-hazard". The IBC classifies "private garages" as a "Group U Utility and Miscellaneous" OC. In addition, Section 406.3 Private garages and carports limits the area to 1000 sf. Perhaps the building official required the "S-1" classification since it exceeded this area limitation? Maybe the jurisdiction allows larger private garages? I would recommend you clarify with the building official the correct OC and if it meets their requirements. Determining the correct OC is crucial since automatic sprinkler system (ASPS) requirements are dictated by the IBC Chapter 9 while the referenced standard NFPA 13 (13R) determines HOW the ASPS is to be designed, installed, tested, and maintained.

Next, review the ASPS requirements for both S-1 and U Occupancy Classifications. 903.2.9 Group S-1 requires ASPS if the fire area exceeds areas (12K, 24K, 5K) or if the fire area exceeds a number of stories (3). Based on this section, an ASPS is not required by the IBC for this S-1 OC “private garage.” Group U buildings are not required to be sprinklered per IBC Ch 9. While an ASPS may not be required for this “private garage” based on its OC, the installation of the ASPS is required to be compliant if it is part of the design.

The planned “mezzanine” may includes a “change of use” since it is adding a non-storage use in this (existing) private garage. This may be considered a “Change of Occupancy” (e.g. nonseparated multiple OC) so I recommend verification from the building official on how they interpret this non-storage use from an OC standpoint. Since this use occurring on a mezzanine (300 sf) is more than 10% of the 1400 sf garage, it may not be considered “accessory”.

Requirements for mezzanines are per 505.2 which requires the mezzanine cannot be more than 1/3 the floor area (1300/3 = 433 > 300 = Compliant), the Means of Egress meet Ch 10 (see 1004.11.2 & 1009.1), and meets the “openness” requirements of 505.2.3 (compliant?).

You state that the mezzanine is “wood-framed” but you did not identify the Type of Construction (I-V?) for the rest of the garage (non-combustible vs combustible?). If the garage is of noncombustible construction (Type I or II), combustible materials are permitted per Section 603 but a wood-framed mezzanine and stairway is not listed. The stairway is required to be “consistent” with the Type of Construction of the building per 1011.7. The code official should also be conferred when determining the calculated Occupant Load for the mezzanine’s intended use. The “accessibility” requirements you cited for the mezzanine relates to “accessibility for individuals with disabilities” per the ICC A117 (and ADA).

I am sorry if this created more questions than answers but this pathway through the Codes and the associated building officials is recommended to determine compliance.


Reply
Gregg Peterson
3/10/2022 01:14:27 pm

Thank you (and other commentators) for your in-depth research.

To answer some of your questions:

A.) The building is concrete tilt-wall construction with a steel joisted roof and a metal roof deck.

B.) Building official classified the units as S-1 as they were permitted as storage units and they wanted to cover the higher hazard category. The units are being marketed to private owners as collectible car storage areas and anticipated that minor repairs and vehicle work may be done. Thus, any S-1 activity was approved. No residential use is authorized. The maximum occupant load allowed by code is 24, but in reality this number is going to much smaller than that.

C.) The sprinkler system (NFPA 13 -2013) is provided throughout with complete coverage at the roof deck as well as under the wood framed mezzanine, but not under the open, wood-framed mezzanine stairs.

D.) The mezzanine is less than 1/3 of the floor area and the occupant load of the mezzanine will be about 3 or 4 persons. The code only allows for 1, but the mezzanine is not a a permanently occupied space, only for occasional use.

E.) It seems at this point requiring the stairs to be enclosed (type-X gypsum board) with no storage allowed under them seems to be the best course of action, unless they provide sprinkler protection under the stairs.

F,) The owner of the center apparently installed the basic wood-framed mezzanine as a sales tool and is leaving it up to the individual owners if they want to finish out the mezzanine or not with upgraded materials.

Reply
Little Fire Squasher
3/10/2022 04:04:01 pm

Here are some things that might trigger sprinkler:

Per 2013 NFPA 13 section....

8.9.5.3.2 Sprinklers shall be installed under fixed obstructions over 4' wide.....

8.15.3.1 Sprinklers shall be installed beneath all stairway of combustible construction.

If they decide to make the stairs non-combustible then..

8.15.3.2.3 Sprinklers shall be installed beneath landings or stairways where the area beneath is used for storage.

Todd Wyatt
3/14/2022 09:14:14 am

A. Unless the steel joists include Sprayed Fire-Resistive Material (SFRM), the Type of Construction is probably Type IIB Noncombustible, Nonprotected.

B. The calculated Occupant Load based on the planned use of the space must be considered when evaluating the Means of Egress capacity for compliance. Owner frequenlty tell me that this space will "never have that many occupants" ... until I attend the ribbon-cutting ceremony where that calculated occupant load is met (and sometimes exceeded).

C & F. The owner cannot "install" a wood mezzanine & stairway without the required plan review and inspection by a building official since this alters the initial approved building. Adding a wood mezzanine and stairway into a noncombustible, nonprotected structure may alter the approved Type of Construction. Adding a mezzanine without a professional fire protection engineer's review is not permitted.

Gregg Peterson
3/14/2022 03:59:18 pm

Thank you to everyone for the well-though out responses. This forum is truly one of the web's best resources...and Todd, received some more information on Friday that any owner driven modifications will need to be reviewed and permitted, including any upgrades to the open wood framed stairs and mezzanine that were previously approved for the "shell" space.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT