Sprinkler Criteria for Small Class IB Control Area?

3/11/2022

9 Comments

 
We have a 300 sq ft control area (1 hour rated) for storage of Class IB flammable liquid. The 2018 IBC Table 307.1 permits 120 gallons (no sprinklers required), but this amount can be doubled if the building is equipped with an NFPA 13 automatic sprinkler system.

Our client would like to store about 165 gallons in the room (3 drums). The building is fully sprinklered.

What is the required sprinkler design density for this room?

We considered Ordinary Hazard Group 2 (same as lab area it supports) or Extra Hazard Group 2 (only occupancy in NFPA 13 that mentions flammable liquids).

If EH2, then the minimum water demand becomes quite large: 0.4 x 2500 + 500 gpm hose = 1500 gpm (Under the 2016 NFPA 13 - Section 23.4.4.2.5).

Could you help point us in the right direction? Thanks to all in advance for helping us hunt this down. 

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Eric D.
3/11/2022 08:19:50 am

I would recommend looking at NFPA 30, as it deals directly with flammable and combustible liquids. There are several factors to consider, such as miscibility of the material in water, container type, storage configuration, type of system (water, foam-water), etc.

Reply
Glenn S Berger
3/11/2022 08:29:19 am

Follow NFPA 30 the the storage room only. You do not need to apply the higher density over the entire remote area since you will have fire-rated separation.

Reply
Karen P.
3/11/2022 09:12:05 am

Thank you Glenn. We have reviewed 2016 NFPA 13 small room rule and, assuming our interpretation is correct, it seems we still need to calculate over entire remote area per 11.2.3.3.4. A smaller remote area would certainly help! Let me know if we've missed something.

Reply
COLIN LUSHER
3/11/2022 10:39:19 am

Karen, that is NOT a correct interpretation. The room design method is used BECAUSE the area of the room is usually less than the areas shown on table 11.2.3.1.1. Paragraph 11.2.3.3.4 only states that if the room is smaller than 1500 sq. ft. (for light or ordinary hazard), or smaller than 2500 sq. ft. (for extra hazard), that the design DENSITY from table 11.2.3.1.1 shall still apply. So no matter what size the room, the density cannot be less than the minimum design density of 11.2.3.1.1. T

Pete H.
3/11/2022 01:53:32 pm

Karen, is this mercantile or storage occupancy? Or something different?

NFPA 30 has different rules based on occupancy (I'm looking at 2015 edition. Chapter 9 is general (which based on what you have of drums less than 119 gallons each will result in NFPA 13 Extra Hazard 2 for your room with a full 1500 sq ft calc. seems correct, but follow at your own risk). Chapter 10 is mercantile, chapter 11 is industrial, and chapter 12 is storage. I haven't looked at any of those chapters recently enough to guess as to what they'd do for you.

Glenn Berger
3/14/2022 08:11:07 am

For the record, my response never included the NFPA 13 Small Room Exception. My response stated fire-rated boundary.

Jesse
3/11/2022 09:06:15 am

You'll find design criteria for this in NFPA 30

Reply
Joshua Freedman
3/11/2022 12:22:33 pm

You can design it to NFPA 30 requirements or FM 7-29. If you design to NFPA or FM criterion, you and your client wont run into trouble down the road as the local AHJ doing the sign off might accept something less but the client will have issues with their insurance provider or other agencies.

Reply
Alex Riley
3/11/2022 01:35:37 pm

Echoing above! Sorry I'm late to the punch today. NFPA 30!

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT