In Class I standpipes, I commonly see a pair of hose valves installed at the top landing (or intermediate landing) - One immediately below the other.
Is this an incorrect derivative of the requirement to calculate the two most remote outlets (at 500 gpm), or something that was required in a previous edition of NFPA #14, or is this merely a regional practice that is a result of the shared DNA of my regional contractors? I thought I had seen an informal interpretation regarding this, but I cannot find it again. NFPA Figures do not appear to support this double-valve arrangement. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
17 Comments
Alex Riley
3/25/2022 07:55:32 am
Hi,
Reply
NK
3/25/2022 08:06:37 am
2 hose valves at the top level is easier for ITM testing so you don't have to run hoses up through the stairwells and worry about leaking water in an occupied building. NFPA 14 does not require this and your interpretation that the calculations are based on 500gpm at the two most remote fire hose valves (one on each of the top two levels) is correct.
Reply
Wes
3/25/2022 08:13:56 am
I've seen this done a handful of times, and it was to help facilitate testing.
Reply
Anthony
3/25/2022 08:10:19 am
Alex got the code spot on and I too have never seen that arrangement.
Reply
Jack G
3/25/2022 08:10:45 am
I ve only done that when the stairs had access to the roof, and roof manifolds were required. Sometimes the AHJ will allow it inside the roof access door, with a sign, because of freezing winter conditions,
Reply
DS
3/25/2022 08:12:55 am
This also could be for ease of testing for the flow test and not having to use a hose valve inside the stairs as one of the two most remote valves. It is a common practice in both existing and new installations in the area I work in.
Reply
Jesse
3/25/2022 08:16:35 am
Our largest AHJ also requires this. and yeah its kinda weird to me too
Reply
Matt
3/25/2022 08:27:24 am
I agree that it is for ease of testing. It can be messy and time consuming to run a hose from the second most remote standpipe connection to a safe discharge location.
Reply
Dan Wilder
3/25/2022 09:05:23 am
The wording and interpretation of NFPA 14 over the cycles has created this issue in both the hydraulics and design/install that carried over from editions and reviewers.
Reply
Wes
3/25/2022 09:08:46 am
Thanks Dan, this makes much more sense. I didn't know the historical context for this, but around the time we saw this method used was very much when the 2007 Edition of NFPA 14 would have been adopted.
Reply
Anonymous
3/25/2022 11:49:04 am
Thanks Dan and everyone. I think testing and incosistencies in the figures in the standard going way back is why it has become a common practice locally.
Reply
Danny
3/25/2022 09:44:57 am
I have a hospital that has two of these at most remote standpipes that are two different roofs. Per NFPA 25 to perform a 5 year flow inspection for a fully sprinklered building I need to flow 500gpm then 250gpm out of each additional standpipe until I reach 1000 gpm. Would flowing 500gpm out of both “Siamese/double hose valves” be ok?
Reply
Wes
3/25/2022 09:49:29 am
No, not in my opinion. The test would need to be conducted as described - 500 gpm at the top of the most remote standpipe, then 250 gpm at each additional standpipe (top or bottom).
Reply
Danny
3/25/2022 09:53:15 am
Ok, thank you!
sean
3/25/2022 12:40:04 pm
this actually changed from the different versions of nfpa 14. it used to sawy you should have two valves at the most remote location (2 valves at the highest landing). Now it specifically says you can use the two hose valves in the locations they are required i.e. the top floor and the floor below.
Reply
Danny
3/25/2022 01:58:15 pm
So you think I would be ok to flow my 1000gpm out of the two standpipes/double hose valves?
Reply