Use Test Header Butterfly for Throttling Flow?

3/1/2022

7 Comments

 
When doing an annual test today for large fire pumps with a combined test header, I was told that most inspectors throttle and send water to the pitot gauges by using the butterfly valve inside the pump room and keeping the control valves wide open outside on the test header.

I disagreed with this approach, as my mentor in the industry taught me to first charge the test header and then get your pressures by opening each outside control valve individually to get your pressures. He said this is so that you don't burn up the rubber on the inside test header (normally-closed) butterfly valve. He said it happened to him in the past and then the building owner is left with a leaking test header control valve and the danger and costliness of a test header full of water.

Is there a correct way (by code) to get your pitot reading off the hose monsters outside (what I mainly using) or is charging water one way or the other simply a matter of preference?

I hope this makes sense.

I understand some test header control valves are OS&Y but most all the outside components I come across are the test hose connections that open and close via the gate valve.

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Travis Mack
3/1/2022 08:08:04 am

I've done tests both ways for years. I have never come across an issue by throttling via the butterfly valve. I don't believer there is a required procedure in NFPA 20 or 25 on how it should or shall be performed.

Reply
matthew mueller
3/1/2022 08:17:19 am

I lost count of the number of butterfly valves I've had to replace over the years due to using the butterfly to throttle flow. Turbulence tears up the rubber seat that is on the vane, and it will no longer seal even after some times just one test. While there's no prohibition that I know of for doing this, it is very bad practice.

Reply
Jesse
3/1/2022 08:27:23 am

Smart mentor.

I would avoid throttling using the BFV. It will create a lot of turbulence downstream of the valve as well as undue stress on the valve itself.

Reply
Glenn Berger
3/1/2022 09:10:34 am

If you are looking to perform the test(s) at 0%, 100%, and 150% flow, the it is easier to use the throttling valve. If you are running the test with one hose valve open, two hose valves, three hose valves open, then the butterfly valve provides no assistance in this manner.

Regardless on how you perform the tests, ensure that hoses are securely connected to the hose monster and the gate valve, and stay safe.

Reply
Dan Wilder
3/1/2022 01:08:47 pm

On pump commissioning, we leave the butterfly open and throttle via the hose valves. On yearly (or 3-year if a flow meter is installed), the inspections guys I have seen will use the butterfly valve. Doesn't help that these are normally closed valves (if order correctly and not wired backwards)

The installation literature for Victaulic has some specific language on this...

" When using Victaulic Butterfly Valves for throttling service, Victaulic recommends positioning the disc no less than 30 degrees open. For best results, the disc should
be between 30 and 70 degrees open; this is dependent on the flow requirements/characteristics for the piping system. High pipeline velocities and/ or throttling with the disc less than 30 degrees open may result in noise, vibration, cavitation, severe gasket erosion/abrasion, and/or loss of control. Contact Victaulic regarding throttling services."

It also recommends installation 5 diameters from irregular flows and limiting flow velocities to 20 ft/sec (probably not an issue with a NFPA 20 sized test header)

There is a "supply side" of a butterfly valve as an installation method (the tapped port sitting below the clapper), but it's only discussed as a good practice, not a requirement.

Reply
Chris Logan link
3/1/2022 01:36:35 pm

I have tested both ways. I will use the test header supply valve to throttle most times if its an OSY (older install) as opposed to the butterfly. I haven't had any issues with butterfly valves burning up, but I can see it being an issue.

Reply
James E. Art FPE, Ca
3/2/2022 11:59:54 am

Throttling using a butterfly va. is very difficult (and can be hard on the rubber parts.)
When I do the specs, I recommend:
- Provide at least one OS&Y on the test loop, and
- Install a 2" drain on the loop, past the meter.
This allows release of some flow and pressure to drain,
which makes it much easier to regulate the flows to get good test points,
and reduces the tendency to have the water flowing in a circle around the pump to heat up.
It can also help drain the pipe if the meter is removed for service.
Note flowing just around the test loop does NOT verify or test the water source. An actual discharge test is required at least every 3 years.
James E. Art, Pleasanton, CA.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT