Cost of Sprinklers in Wood Floor/Ceiling Cavities?

3/16/2022

8 Comments

 
We have a project that is Type III-A, wood frame construction, with an NFPA 13 sprinkler system.

The client is weighing options of filling floor truss cavities with non-combustible insulation versus adding sprinkler coverage within these floor-ceiling cavities.

Does anyone have recent experience to know the relative cost impact of adding sprinklers within these floor cavities?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
8 Comments
Pete H
3/16/2022 07:28:53 am

No one is really going to be able to answer that without knowing the square footage of the structure.

Similarly, costs of labor vary heavily by shop (is it a union shop, is it a nonunion shop) and location.

Costs can also vary based on type of sprinkler and proximity to the sprinkler manufacturer.

Unfortunately the only way to really get an answer on this (that my inexperienced butt can think of) is put the project out for bid, and instruct bidders in your area to have the cost of protecting the floor/ceiling truss cavities as a separate line item as an alternate. Then instruct structural bidders (or whatever trade would handle the insulation in your area, not my field) to do the same with the insulation costs. Make sure the insulation you're asking for is detailed for the right type and capacity to make it so you can omit sprinkler protection in the interstitial space.

Compare the separate line items. Come up with works best for your project.

Reply
Jesse
3/16/2022 08:09:40 am

Its really difficult to answer that. The combustible concealed space is a volume of space. If these cavities between the ceiling and floor are 1-ft high, the cost of insulation will be substantially less than if they are 4-ft.

The cost of automatic sprinkler protection would largely be consistent.

Reply
Anthony
3/16/2022 08:56:50 am

Generally its fairly easy to get a price for insulation. So start there and work that against a sq ft number for the rest of your building's sprinkler cost that should be a decent ballpark number.

I think its always a better idea to go the insulation rout. You improve the heat zoning in a building and insulation doesn't need to be serviced and does leak.

If pipe is already going to be in the truss cavity and the truss is 36+ inches deep then Its worth thinking sprinklers in the cavity due to the large volume of insulation required.

As others have stated there is no "rule of thumb" as each instance requires a V/E analysis for the particular geometry and local cost factors.

Reply
Alex
3/16/2022 11:11:13 am

I agree with Anthony here. You also need to be careful when your cavity size gets large. The code outlines limits on amount of insulation that can be installed.

Reply
Wendell
3/16/2022 11:07:38 am

Coming at this from the architectural side, contractors we've worked with have always preferred the "fill voids with insulation" solution, but that's for voids that are generally no deeper than 24" or so. Note that some floor/ceiling or roof/ceiling assemblies have limits on amount and type of insulation that can be added, and/or require an additional layer of gyp if fiberglass insulation is used, so check Gypsum Association or UL assembly notes before proceeding.

Reply
sean
3/16/2022 07:52:33 pm

I think you also have to consider that if you are already running branch lines the additional heads are a cost but significantly less than a new system

Reply
Rock
3/17/2022 09:34:12 am

Be sure to loop in your AHJ. The AHJ may require a third party inspection of the insulation in the interstitial space due to the difficulty of completely filling the cavity from the underside.

Note: NFPA 13 will only allow a small gap at the top of the insulation after the insulation settles.

Reply
Thomas A VonCannon link
3/17/2022 04:21:38 pm

Insulation filling a void, locally when this is done it is blown in above chicken wire to maintain a filled void. I would think that when the void is over 24" deep, I would think sprinkler protection would start to be competitive with insulation. In most cases where this takes place you have a branch line within the cavity anyway, so you are talking the cost of a weld-o-let a sprig and sprinkler head.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT