MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

An FDC Required with Dedicated Fire Water Tank?

3/15/2022

13 Comments

 
We have a project that has a dedicated fire water supply storage tank. Is an FDC required on this setup?

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
13 Comments
Alex
3/15/2022 07:34:11 am

Hi,

The purpose of an FDC is to allow the fire department to provide supplemental pressure upon arrival. FDCs should be installed on all buildings except [NFPA 13 (2013) 8.17.2.2] :

(1) Buildings located in remote areas that are inaccessible for fire department support
(2) large-capacity deluge systems exceeding the pumping capacity
(3) single-story buildings not exceeding 2000 SQFT in area

Installing an FDC, in my opinion, is a no brainer. If the fire inside is overwhelming the sprinkler system, adding more pressure to increase flow from the outside is the safest option for firefighters.

Thanks,
Alex


Reply
Justin P Milne link
3/15/2022 08:20:16 am

The answer to your question depends on the application.

Are you providing wildfire engineering? Then the fire water storage tank is your fire flow for your fire truck. Depending on how remote the site is, you might have an FDC at the building to pump into and augment the pressure of the fire pump.

Are you providing standpipe engineering? Standpipes require fire department connections as the exterior and interior connections are needed for fire department use.

Are you providing standpipe engineering? Standpipes require fire department connections as the exterior and interior connections are needed for fire department use.

Are you providing deluge system engineering? Deluge systems require fire department connections because these fixed-fire suppression systems are intended to replace the need for a fire department in a very high-hazard environment.

Are you doing high-rise engineering? Then the fire water storage tank supplies your fire pump, but you'll still require fire department connections exterior to the building to augment the fire water supply.

Are you doing industrial engineering? Then the fire water storage tank is probably remote from the building complex, and you are going to need a HUGE amount of fire department connections so that you can get the GPM required per code.

To sum up, you need an FDC basically everywhere, unless there's no way to get the water supply to a location if you have remote buildings with no access to underground utilities.

Reply
Barry Carr
3/15/2022 10:17:27 am

I agree with Justin. It depends upon the application. In my view the AHJ certainly has the right to recommend an FDC be placed at the location, and be able to interject the reason for this request. I'm a firm believer in the Fire Service working within the intent of the Fire Code and preventing fires. (Sometimes a request and a good explanation for asking what you're asking people to do goes a long ways verses forcing them.)

Jon
3/15/2022 08:17:34 am

Alex pulled the code language but think about it this way as well. Theres only a finite amount of water in that storage tank so how would the suppression system be supplemented once that stored water runs low? Even in (most) remote locations where there isn't municipal water close to building, the fire department will use tankers/tenders and pumper relays to bring water to the site. The FDC is the avenue to bring that water to the system.

Reply
Jesse
3/15/2022 08:46:13 am

Wearing the fire protection engineering hat - yes, and Alex provided the code language.

Dusting off the retired fire chief officer helmet - also yes. Whereas the tank supplies the AS system the FDC allows the FD to supplement it. The tank may be there because there is no city source, or because the city source is too far. The FD will secure a water supply either by laying large diameter hose to a hydrant a distance away, drafting from a static source if available, or bringing it on their responding engines and tender apparatus, and if necessary running water shuttles to establish a continued water supply for long durations.

Reply
Pete H
3/15/2022 09:18:01 am

Yes.

Even if there's no hydrant to connect to, Fire Departments still might have their own pumper truck which is “[a] fire apparatus with a permanently mounted fire pump of at least 750 gpm (3000 L/min) capacity, water tank, and hose body whose primary purpose is to combat structural and associated fires.” to supplement fire suppression and control of the sprinkler system.

Reply
Justin Phillip Milne link
3/15/2022 09:21:29 am

Excellent adder here, Mr. H.

Reply
Matt C
3/15/2022 10:35:33 am

If you would require an FDC anyway, then yes you can't just omit the FDC. Even if the tank wasn't required, water would be shuttled in (via tanker/shuttle run from some other source, be it pressurized, or static) and dumped into porta-tanks set up by the FD on either end of the run.

In addition, if this is a static source (no fire pump) ensure that a drafting port is provided, and protection from mechanical damage is installed (bollards, for example).
Note that this connection can vary jurisdictionally. Where I'm located we require a 6" NH because that's what our hard suction hoses on the trucks are and allow a direct connection. In older areas, I've seen a standard fire hydrant which can be super confusing for responding personnel (the assumption being that hydrants are always pressurized). This also usually requires an adapter of some sort to be fitted onto the length of hard suction hose that connects to the hydrant (4" Storz to 6" NH, in our area) which can kill time during an emergency response.

I strongly recommend consulting with the AHJ on what connections/thread types are best suited for them.

Reply
Glenn Berger
3/15/2022 11:21:35 am

There is no exception for not providing a FDC for a building fire suppression system per NFPA standards for a dedicated water supply.

Reply
Matt Cornell
3/15/2022 11:33:56 am

What I like to see in our area is a large diameter draft point on the tank and the FDC in line right after the fire pump. This allows a short suction line thru the fire apparatus and a short discharge to the FDC. This allows for the fire department to support the pressure provided by the fire pump or by pass the fire pump all together if it fails.

Reply
Manny Rios
3/15/2022 12:26:36 pm

In our jurisdiction we have two remote sites that are provided with storage tanks to supply the fire protection systems, the AHJ (State Fire Marshal) using the code language required fire department connections at both sites.

Reply
Mahendra Sheth link
3/16/2022 11:56:04 am

Yes, the Fire Department Connection should be provided.

Some local Fire Departments have trucks with water tank that can be used to pump into FDC.

However, in order to provide good design,
1. The capacity of the tank must include required hose allowance.
2. There should be a wall hydrant mounted on the pump house wall with an inside control valve (to prevent freezing).
3. The wall hydrant should be supplied from the pump suction piping (not flowing thru the pump).

Thus, when the fire truck arrives to the site, they have a wall hydrant and the FDC available to pump in more water in the sprinkler system without stealing any system flow from the tank.

Reply
Greg C
3/16/2022 12:37:40 pm

In accordance with NFPA 22 it could be an approved method of filling the tank.

It may also be a local FD standard or approved method. Many areas have fire flow requirements in land use standards.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT