|
If I have a PIV installed, is it required to be tied into a fire sprinkler system?
I work at a campus style facility with a fire water supply loop for fire sprinklers. We have a couple of buildings that do not have a fire sprinkler system, however, there is a PIV outside the buildings that are in the closed position. I am assuming they were installed for "future use" assuming a fire sprinkler system gets installed. Is there an NFPA code reference that requires the PIVs to be "in service" or used for their intended purpose, or are we code compliant with them being "for future use"? I do have a concern with responding fire units incorrectly assuming that there is a fire sprinkler system in these buildings due to the PIVs being installed. What are your thoughts? Thanks! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Chad
7/18/2023 07:29:38 am
Its connected to a FP main? Signage on all valves are required.... as an AHJ I would expect one stating what it is (or isn't in this case)
Reply
Anthony
7/18/2023 08:31:03 am
As Chad said, yes, label all your valves.
Reply
Glenn Berger
7/18/2023 08:33:58 am
Your comment uses the dangerous words "future use assuming."
Reply
Jon N
7/18/2023 08:41:38 am
Similar to hydrants, you could add a sign stating "Not in Service" or something similar.
Reply
SCHULMAN
7/18/2023 08:48:09 am
A better solution (IMO) would have been to provide a locked valve on a branch off the main in a ground box with a blind flange on the downside and install the PIV "in the future" when the new sprinkler service piping to the building is installed. Just saying.
Reply
Jesse
7/18/2023 09:54:06 am
Great comments thus far. I'm curious as to whether or not there are hydrants on this loop. And if so, if these are effectively sectional valves for the loop.
Reply
Alex
7/18/2023 10:09:47 am
I believe best practice would be to label the PIV as "For Future Use" to avoid misunderstandings.
Reply
Dan Wilder
7/18/2023 11:18:54 am
Technically this falls under NFPA 24 for underground, not 13, but many of the same requirements still apply. Is the PIV monitored and/or just locked?
Reply
JT
7/19/2023 01:15:53 pm
You could model LOTO in addition to NFPA requirements. In addition to signage have documentation which included as built drawings and response/maintenance procedures.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop Sept '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
October 2026
PE PREP SERIES |
RSS Feed
