MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Restrain Service Pipe by Bolt to Friction Clamps?

6/8/2022

7 Comments

 
I have a job where the plans have a detail of the underground fire service entry into the building that shows us bolting to friction clamps. I've always used the 90-degree I bolts on the flange to shields.

Looking for some detail on this - are there other methods I should be considering? Is this acceptable?

​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
David Kendrick
6/8/2022 08:46:19 am

I think we called them Star Bolts. A 3/4" rod with a bent eye on one end and bolt thread on the other.

There are details of using a friction clamp with threaded rod. I just can't seem to locate one at the moment.

The friction clamp has "ears" that extend past the gland and bell of the fitting. Rod is laid into the gap between the ears after securing the clamp bolts.

We would use a special cast iron washer that had a pointed pin on one side that when placed over the rod with the pin between the fitting hub and bolt would hold the restraining rod in position. A nut would then secure the washer in the assembly.

It does require an equal fastener at the other end of the rod such as a dead man or fitting assembly.

As you can tell from the description Star bolts have less parts and are simpler to install.

Remember coat exposed steel or bag the pipe and restraint to reduce future corrosion.

Also good resource is the Ductile Iron Pipe Research Association.

www.dipra.org

I'd recommend requesting an installation guide from them.

Reply
Paul Pinigis
6/8/2022 10:07:04 am

Are you referring to a ductile iron retaining gland like Mega-Lug?

Reply
David Kendrick
6/8/2022 10:55:28 am

Megalug is a whole different product. A good product for that is made for ductile and plastic pipe.

www.DIPRA.org discusses restraint methods and calculations. Really good resource.

As far as the cast iron washer:

www.empireindustries.com

Figure 599 Socket Clamp Washer

We also would fabricate these out of welded flat plate with a 1/2" square rod about 1 1/2" long welded on the end for restraint of the washer.

https://www.asc-es.com/products/599-socket-clamp-washer

This is a picture of the Fig 599 washer with a Fig 600 restraint clamp.

Lots of product choices.

Toothed push gaskets are very useful on straight runs.

Reply
Jack G
6/8/2022 10:16:07 am

I would use an accessory at each slip joint, a gland I called tiger teeth. Had little teeth imbedded in the gland that held the joint together. Eliminates thrust blocks if entire run / service has restrained joints. Was about 35 bucks for 8 inch gland.

Reply
DAVID
6/8/2022 11:10:20 am

My boss was the expert in UG, not me, but we did as the other David described above, always going for redundant restraint/blocking, Star-bolts, MegaLugs, etc. (For the actual entry into the building, a one-piece stainless AMES In-Building-RIser (IBR) sometimes makes sense, especially in a retrofit.) Is the detail you have been provided old and generic?

Check the starpipeproducts restraint catalog, or ebaa-dot-com

There are several sentences and requirements regarding the use of clamps in NFPA 24 starting with this (2020):

10.6.2* Restrained Joint Systems. Private fire service mains
using restrained joint systems shall include one or more of the
following:
(1) Locking mechanical or push-on joints
(2) Mechanical joints utilizing setscrew retainer glands
(3) Bolted flange joints
(4) Pipe clamps and tie rods
(5) Other approved methods or devices

Reply
Cliff Schulze
6/8/2022 01:11:04 pm

Here is the only link I could find. Years back, the old fitters used to install this way all the time.
https://www.trumbull-mfg.com/products/joint-restraint-products/socket-clamps/

Reply
KRowe
6/9/2022 08:23:41 am

The use of a friction clamp (Water Main Clamp) is very common.
A single water main clamp behind the hub of underground pipe with Dog Ear washer. You would rod both sides through dog ear and use a concrete anchor to the wall.
If the water main clamp is in the middle of pipe, not behind a hub, restraining a fitting, you would need two water main clamps. The term used is to Mutt & Jeff the clamps. That is two varying lentghs of rod, say 2'-6" & 3'-6", one rod to each clamp, so that the water main clamp is cutting the pipe or crooked on the pipe. A single water main clamp in the middle of the pipe slides, no matter how tight you think you can tighten it.
This is what we you do if someone specified using an older method.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT