What Mandates Ductile Iron Until the Backflow?

12/20/2022

18 Comments

 
We are doing the install for a new building. The fire sprinkler underground comes in the building and they are requiring ductile pipe be used inside the building up to the backflow preventer.

Can anyone cite literature for this?

I know NFPA does not require the use of back-flow prevention, but am interested in the code basis for the pipe type until the backflow preventer.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
18 Comments
Clayton B Tibbetts
12/20/2022 08:06:11 am

Reference your local/state plumbing code.

Reply
Glenn Warga
12/20/2022 08:06:16 am

It is generally good practice to install Ductile Iron under building foundations. The local municipality is the entity that can specify installation methods and materials and the rules differ across the country. Many west coast jurisdictions require one piece stainless steel spigots under the foundation and into the building.

Reply
Anthony
12/20/2022 08:08:06 am

It may not be a code requirement, but a judgment call by the engineer/designer. They might think that the ground may not be suitable for PVC/CPVC or have seen too many installations that have neglected to properly sleeve pipe through foundations. There may be soil conditions that make DI the best call.

On the code front I have seen some jurisdictions require it on city drawings that look like they date back from the year one. It could just be that simple.

Reply
Corey Eppinghaus
12/20/2022 08:12:43 am

In Ontario the OBC under Table 7.2.11.2. of Part 7 gives you the list of acceptable piping material for a water service or FSM but it's really up to the engineer or designer of the UG and how that joint will be connected

Reply
JI
12/20/2022 08:18:30 am

I am usually limited by the Design Specifications of the municipality I am working in. Usually there is a section for Watermain Pipe Material or something similar. They will typically reference the latest Standard of the American Waterworks Association (AWWA). Typically I will see the use of Brue Brute PVC piping stubbed into the building, and then Ductile Iron fittings and a uniflange for connecting to the backflow. Generally speaking, anything downstream of the backflow when connecting to a municipal water supply should be considered safe for potable water, which the AWWA standards enforce.

If you are trying to avoid a long run of ductile iron pipe within the building, I would connect the backflow to the water service as close as possible to where it comes into the building, and you can use your NFPA approved piping of choice upstream.

There may be NFPA codes that dictate the use of certain underground materials, but I have never had to dig that far since the AWWA standards will trump anything within NFPA anyways.

Reply
Glenn Berger
12/20/2022 08:19:45 am

I have not heard of a requirement that you need to use ductile to the backflow preventor.. Typically it is ductile iron underground and then carbon steel aboveground and then to the backflow preventor.

Reply
Eric R
12/20/2022 11:30:30 am

Glenn,

This approach is certainly incredibly prevalent, but I'd be concerned if this is something you are still doing today. We switched over to either concrete lined directly up to the backflow, or in situations where we can't make that work we will use victaulic grooved(not firelock) glavanized fittings that come with the NSF61 approval and A53 galvanized pipe. This should keep you in conformance with the IPC regs for water service piping per 605.3 and 605.5. A lot of water purveyors don't pay attention to sprinkler connections at this time, but sooner or later this will catch up with everybody so better to get ahead of it if you can.

The cost change can be negligible once you get your SOP set. One product we are really enjoying use of lately is a cement lined ductile iron MJ x Flanged elbow to slap on the bald stub-in pipe. Having the MJ connection allows you to align the elbow parallel with the wall (as opposed to spool flanges that are always wrong) and then flange connect directly to the backflow. All NSF, all UL listed.

Reply
Glenn Berger
12/22/2022 08:40:12 am

OK I cheated, yes I use cement-lined ductile iron piping.

James Phifer
12/20/2022 08:30:14 am

Per the appendix of NFPA 13, you should consider the weight that nonmetallic pipe would be supporting. i personally would not feel comfortable supporting a heavy riser with a backflow preventer with PVC pipe for example.

A.10.1.4.1 Where nonmetallic underground piping is provided
above grade or inside a building, the following should
be considered:
(1) Exposure from direct rays of sunlight
(2) Compatibility with chemicals such as floor coatings and
termiticides/insecticides
(3) Support of piping and appurtenances attached thereto
(e.g., sprinkler risers, backflow preventers) [24:
A.10.1.4.1]

Reply
Todd E Wyatt
12/20/2022 08:36:43 am

2021 International Plumbing Code (IPC) references “ductile” (8) times in Chapter 6 Water Supply Distribution but none of the references are a requirement of use. Table 605.3 Water Service Pipe lists (18) acceptable materials, “ductile iron water pipe” as being one. Table 605.4 Water Distribution Pipe lists (14) acceptable materials, “ductile iron pipe” as being one. Table 605.5 Pipe Fittings lists (17) acceptable materials, “gray iron and ductile iron” as being one. Lastly, Table 605.7 Valves lists (6) acceptable materials, “ductile iron water pipe” as being one.

2022 NFPA 13 references “ductile” (21) times but none of the references are a requirement of use.

When an AHJ lists a “requirement” such as this, it is perfectly acceptable to request from the AHJ the applicable Code reference. Sometimes, the AHJ cannot give the reference and will revise their “requirement” language to “recommended.”

Reply
David Kendrick
12/20/2022 09:07:11 am

It is potable water up to the backflow preventer.

Reply
chad
12/20/2022 09:28:26 am

Typically, prior to the backflow is covered by a standard or code that is not referenced by the I-codes or NFPA, like a local water department regulations, that are enforceable through some state or local law. Although 13 may come into play in parallel, the other local or state code will win, no matter how much you want to argue with the water department.

Reply
DAVE
12/20/2022 11:12:10 am

In my area the water purveyors and fire departments also accept stainelss steel, so I see a lot of Ames In-Building Risers, especially in retrofit situations. Continuing to the backflow preventer, I often see stainless GxG spool pieces and grooved stainless 90's. But I have had one or two AHJ's not allow stainless. Historically, we never allow galvanized steel in our specs, however a few GxG galvanized fittings are now certified ANSI/NSF61 for potable water, e.g., some Victaulic grooved reducers and standard-radius 90's (see their 02.06 Potable Water Approvals).

Reply
Ryan Hinson
12/20/2022 11:21:39 am

Piping upstream of the backflow is potable and must be appropriate for contact with potable water. This is typically found in the adopted plumbing code. Where adopted, IPC (2015 referenced here) Section 605.3 includes minimum allowable "water service piping" which must conform to NSF 61 in compliance with Section 605.3 and Section 605.4 which is for "water distribution piping" in the context of potable water.

Table 605.3 includes allowable pipe types for potable piping systems. Both DI and Galv CS are allowed for this application along with SS, plastics, brass, and copper. Though I think this is a bad idea for obvious reasons; in lieu of their listings, plastics listed in Table 605.3 but NOT in Table 605.4 CAN stub up through the slab up to 2 ft inside a building per NFPA 13 (2022) Section 6.1.4 and NFPA 24 (2019) Section 10.1.4.

Section 605.3 also states the following for "water service piping" which is typically buried:
"Ductile Iron water service piping shall be cement mortar lined in accordance with AWWA C104."

This should not be confused with "water distribution piping", typically above grade, which has no cement mortar lining requirement per Section 605.4.

Reply
Casey Milhorn
12/21/2022 09:59:51 am

I think this got covered in several comments, but it's more about the fact that it's cement lined DI pipe. This will be enforced by your water purveyor. Some accept PVC (like C900) and others strictly want Cl. 350, 50, 51, or 52 cement lined pipe and fittings. Where I am, we actually have to install mechanical joint DI fittings above ground when we have more than 1 cement lined flanged fitting to get to the backflow. It makes for some ridiculous looking installs and tons of weight hanging in the building. They don't like cement lined flanged fittings probably because they can't verify it's cement lined after it's installed.

Reply
sean
12/31/2022 08:52:24 pm

NFPA 13 and NFPA 24 have a variety of materials that can be used more than just ductile

Reply
Welderinfo link
4/6/2023 10:24:41 am

I appreciate how you explained the pros and cons of different types of welding machines. Your expertise is evident, and it's really helpful for those of us who are just starting out."

Reply
rohandajohn link
5/10/2023 08:33:21 am

"I just wanted to let you know how much I appreciate the time and effort you put into creating this post. It's clear you're passionate about the topic and it shows."

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT