Seismic Req'd for Outside Pipe on Pipe Stands?

7/19/2023

10 Comments

 
I am running 8” and 4” water storage tank fill and suction lines above ground in an exterior utility yard. 

Is lateral and longitudinal bracing required for aboveground piping supported on pipe stands located outside of a building, in an exterior utility yard?

Due to underground conflicts with spread footing foundations the underground piping has to be routed above ground to the final location and connection points on the tank. The pipes are supported by 1’-6” non adjustable pipe stands attached to slab on grade.

This project is located in a seismic zone and the seismic force factor does not exceed 0.5Wᵖ and I am using ACI 355.2 qualified anchors as required by NFPA 13 2016 Edition. Sections 9.3.8, A9.3.8, 9.3.8.1, and 9.3.8.2. The pipe stands I am using are following the NFPA 13 2016 Edition prescriptive method detailed in sections 9.2.6.3.2, 9.2.6.4.2, 9.2.6.4.4.1, and 9.2.6.4.5.1, I’ve also attached a detail for clarification. Thanks in advance!
Picture
​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
10 Comments
Anthony
7/19/2023 08:14:33 am

You seem to satisfy all the requirements of 9.3.8. and 9.2.6. as I read them.

My next question would be are flexible couplings or rigid couplings be recommended between pipe segments?

Reply
Jesse
7/19/2023 08:45:25 am

I think you've covered the requirements.

Reply
Dan Wilder
7/19/2023 08:52:25 am

9.3.8 only requires a certified engineer to design the pipe stands when over 4' in a greater than .5 Wp. It does not say you can exclude seismic bracing if it's required on the system.

There is an EOD answer for this I need to look up and will post in a bit.

Reply
Dan Wilder
7/19/2023 11:12:51 am

It's an old answer...

Feb 2008 Ref NFPA 13/15 - 2007

No specific guidelines on how but references using the ground as the plane for brace angles vs the normal structure plane and check with Insurance Carrier for guidance.

NFPA 13-22 Annex A17.5.3.1 has some info on how the heights of pipe stands were calculated, but only refers to lateral loads, not longitudinal. This may be your best option to omit lateral bracing at least.

FM Global 2-8
Fig 2.2.1.1.2 for manifold risers indicates using 2x - 2-way braces within 2' of the end of a manifold when longer than 6' but really no other guidance.

Nothing new in NFPA 200 (draft-Section 6.8) on the matter.

NFPA 15-22' Section 6.3.2.2.4 says:
"Where pipe stands are used to support straight runs of piping or other configurations that are not looped or are not rigidly supported at the top of the pipe stand in a manner that will resist movement in all directions, the pipe stands shall be designed in accordance with the requirements of NFPA 13."

Reply
Jim Phifer
7/19/2023 09:03:42 am

I may be over thinking this, but...If lateral and longitudinal bracing is required, what would I attach it to?
concrete blocks? How big does the block need to be? How thick?
what strength does the concrete need to be?
I think this needs to be addressed more in NFPA 13.

Reply
BK
7/19/2023 09:15:57 am

I was thinking similarly, since bracing is designed and listed with structural building connections (e.g. to move with buildings)

Reply
AHJ
7/26/2023 11:41:50 am

I have this same question and am dealing with a similar installation. I agree, I wish there was more guidance provided in codes/standards.

Reply
SCHULMAN
7/19/2023 10:42:51 am

I'm no structural engineer but I think the forces from the pressure of the water would be far greater than any overturning moment forces on an 18" high 2" diameter steel pipe. Unless someone is asking for it, I would follow your detail and move happily on. Maybe laterally brace it at the changes of direction similar to underground thrust restraints?

Reply
Todd
7/19/2023 01:41:36 pm

What is the Seismic Design Category as defined on the Structural and/or FP plans?

https://www.meyerfire.com/blog/how-to-determine-if-sprinklers-require-seismic

Reply
Franck
7/22/2023 04:02:35 pm

NFPA 13 is for sprinkler systems only, not for the feed from the water supply to the sprinkler system.

You can apply the same reuirements as for a supply piping (outside a building) as for any water supply.
If you provide possible flexibility, that should be fine.
A possible solution (for large size piping), to allow lateral movements: listed flexible piping such as the solutions provided by (but not limited to...):
https://www.metraflex.com/seismic-applications/
https://kineticsnoise.com/kinflex/seismic-v-loops
https://www.victaulic.com/accommodating-seismic-movement/

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT