MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Limit for Length and Size for Underground Loops?

4/26/2024

11 Comments

 
Typically when I work on campus/multi-building systems, I am using a single underground main and splitting off to each building. Since you don't have to consider a multiple building fire problem, we have typically worked on the hydraulically most-remote building for underground sizing and use wall PIVs to offer individual building shutoffs, with FDCs on the individual buildings.

I'm getting challenged on "what allows this in code?" It's mostly a question of - where is the limit on how long a loop can be?

I'm looking at this from a sprinkler design perspective and whether each individual building's sprinkler system is able to perform hydraulically.

Is the limit for the length/layout/sizing of a campus underground loop simply the more demanding of Fire Flow or sprinkler system feeds?

Is there a code basis for this?

​Thanks in advance.


Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Glenn Berger
4/26/2024 08:10:06 am

A few questions requiring answers must be considered prior to a proper response to your question be given.

Is your single main dedicated to fire protection use only? Or is it for water needing systems on the campus?

Is there any expansion plans for the campus? Any potential more hazardous areas that can eventually pop-up on-site?

Are you considering any loss of performance as the underground system ages? NFPA standards do include a reduction in the Hazen-Williams C-factor.

Reply
Casey Milhorn
4/26/2024 08:39:42 am

No issue with it. Typically the issue has more to do with arrangement, placement of backflow, FDC placement strategy, fire pump placement (if required), and whether or not you have private hydrants on this line. If you have private hydrants, fire flow demand may be required to be met at these hydrants. Additionally I have ran into some local AHJs that have minimum size requirements on underground lines that feed hydrants based on number of hydrants and/or distance to hydrant.

Reply
Franck
4/26/2024 08:48:15 am

Limitation for size and length is directed by the hydraulic calculations. As long as you can supply all systems with a given pipe diameter and loop length, it is fine.
I survey many nuclear power plants with extensively long loop, but with large diameter to limit friction losses (generally above 8 in.).

As indicated above, check all parameters (fittings) and make regular loop tests to check internal integrity of your mains (every 5 years maximum).

Reply
Pete H
4/26/2024 09:00:00 am

None I can think of. Circulating street mains are typically gigantic compound loops or grids.

Casey's got a good point that you might have requirements for flow and size for feeding any hydrants.

Another concern I'd worry about is if your most remote building is your most demanding. Like if the most remote building is a light hazard office but you have a storage facility next to the source, the storage facility is still probably going to be the driver of your minimum flow.

Reply
Ricardo Gonzales Jr
4/26/2024 09:10:15 am

1st determine what the building needs for a proper system without and with a fire pump. Then direct the Civil folks to make that occur. Unless you're designing a private system, FPs usually don't get involved in water supplies.

That prompts the next set of questions from an FP point. What is the end game for our systems on a campus setting. Like the previous answers, there's a lot of questions before putting pen to paper.

Reply
Jeyson Ventura
4/26/2024 09:12:45 am

A different perspective on why the length of the loop system may be getting challenged.

NFPA 24 section 6.6 talks about sectional valves in looped systems. It states that sectional valves are required such that the number of fire protection connections between sectional valves does not exceed six, but it does not set a limit on the length of the loop. The intent is to limit impairments during a break or service of the underground pipe.

The only limit on the length of a system that I see is when a section of pipe splits off the loop or on a tree system. In my opinion, the intent to limit the number of connections to six would also apply in this case. NFPA defines fire protection connections as sprinkler system lead-ins, hydrants, or other fire protection connections.

Reply
Blaine
4/26/2024 12:36:37 pm

Might look into AWWA manual M31. Distribution System Requirements for Fire Protection.

Reply
Mark Harris
4/26/2024 02:17:50 pm

All great responses. May want to look at fire flow requirements in the appendix of the IFC IBC as well.

As Pete noted high hazard occupancy may make the sprinkler demand more than fire flow hydrant demand.

Reply
Jack G
4/26/2024 04:26:02 pm

Couple things.
Review Meyer fire 2020 hydrant distances, nfpa 24, ibc.
If installing underground for private water mains and hydrants, sometimes it efficient to loop the complex—- although the flow is to be calculated as dead end, Lead ins could be installed front, back or along a side was.
AHJ usually wants a minimum of 1500 gpm at 20 psi residual. Follow 24 for minimum size to fire hydrants.
Fire flow / sprinkler demand ( calculated hydraulicly, unless storage or high hazard , should be less than 1500 gpm.

Reply
Todd E Wyatt
4/30/2024 08:03:09 am

Scoping Codes (e.g. IBC-2024) and their referenced standards (e.g. NFPA 13-2022) include prescriptive requirements (e.g. shall) for the Design Professional to meet when designing a building and/or one of its systems. Some of these requirements include restrictions (e.g. "Sprinklers under walkways shall NOT be spaced more than 8 ft (2.4 m) apart horizontally.) but these are far less frequent than the use of "shall" without "not" following it.

Essentially, anything that meets the requirements (shall) and does not conflict with the restrictions (shall not) is acceptable. The Code and Standards cannot foresee all unique conditions so not all features are included in the requirements because they provide a baseline coverage that goes beyond the minimum requirements. For this reason, most Code & Standards permit equivalencies :

NFPA 13-2024
CHAPTER 1 Administration
1.5 Equivalency.
Nothing in this standard is intended to prevent the use of systems, methods, or devices of equivalent or superior quality, strength, fire resistance, effectiveness, durability, and safety over those prescribed by this standard.
1.5.1
Technical documentation shall be submitted to the authority having jurisdiction to demonstrate equivalency.
1.5.2
The system, method, or device shall be approved for the intended purpose by the authority having jurisdiction.

An equivalency statement is included in many NFPA documents to allow for products and system arrangements that are not specifically covered by the standard to be used. However, it must be demonstrated that the products or arrangements do not lower the level of safety provided by the standard or alter the standard’s intent. The AHJ is required to review the technical documentation and approve the equivalent system, method, or device.

I have experienced AHJs inquiring “Where does it state that this is permitted?” and my response (respectfully) is “Where does it state that this is NOT permitted?”.

The AHJ should not impose requirements beyond those specified in the adopted Code or Standard unless those requirements have been formally adopted in the jurisdiction.

Reply
J.H.
4/30/2024 02:10:58 pm

Generally, the governing Utilities Dept. will have guidelines regarding dead-end water mains, esp. those supplying hydrants and/or fire protection systems.

There is also some guidance in NFPA 1141. The 2017 edition is referenced below:

NFPA 1141:9.3.9 In residential areas, fire hydrants shall be supplied by not less than a 6 in. (150 mm) diameter main installed on a looped system or by not less than an 8 in. (200 mm) diameter
main if the system is not looped or the fire hydrant is installed
on a dead-end main exceeding 300 ft (91 m) in length.

NFPA 1141:9.3.11 Dead-end mains shall not exceed 600 ft (183 m) in length for main sizes less than 10 in. (250 mm) in diameter.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Oct '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 88A
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    November 2026
    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT