MeyerFire
  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT
Picture

Does a Private Fire Hydrant Require Backflow?

8/21/2023

11 Comments

 
In the NFPA series of standards, is there a requirement for a water line supplying private fire hydrants to have backflow protection?

I am working on a project where the fire marshal is requiring double check detector assemblies to be installed on six private fire hydrants. The line serving the hydrants has no other connections to it.

Thanks in advance.

​​​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
Chad
8/21/2023 07:10:45 am

Not in NFPA 24. Where I work, that's a water department decision, not fire. Perhaps the rationale is they are 'dead ends' that doesn't get flushed enough?

Never seen it anywhere else, the maintenance alone and possible failures does not make it the best idea.

Reply
Jesse
8/21/2023 08:05:42 am

Its not an NFPA thing, its from the plumbing code. If the "private system" will have 100-gallons or more of trapped water they will want a BFP.

Reply
JH
8/21/2023 08:19:49 am

Hydrants on dead end mains is a frequent occurrence in our JD. We reference NFPA 1141 in most cases, which only addresses dead ends over 600 ft long, and less than 10 inches in diameter.

Could you please share which plumbing code that requirement is from, and the code reference? Thank you.

Reply
Glenn Berger
8/21/2023 08:10:44 am

Is there not a backflow prevention assembly on the water main at the lot or property line?

If yes, then no requirement for device at each hydrant.

Reply
Todd E Wyatt
8/21/2023 08:11:38 am

Building Officials (AHJs) are required to enforce the adopted Codes and Standrards and to render interpretations as needed. They cannot require components above and beyond these requirements, however.

Respectfully request from the AHJ the Code/Standard section that requires "double check detector assemblies to be installed on six private fire hydrants."

Reply
Anthony
8/22/2023 07:37:29 am

This will probably be your fastest way to an answer.

If you're looking for the information without talking to an AHJ try the health department and permitting offices. Don't be afraid to sound uninformed and just start calling around. Public officials deal with odder questions than backflow requirements daily.

Reply
DS
8/21/2023 08:11:46 am

5.1* Connection to Waterworks Systems.
5.1.1
A connection to a reliable waterworks system shall be an acceptable water supply source.

5.1.2*

The volume and pressure of a public water supply shall be determined from waterflow test data or other approved method.
5.4* Connection from Waterworks Systems.
5.4.1
The requirements of the public health AHJ shall be determined and followed.

5.4.2
Where a backflow prevention device is installed to guard against possible cross-contamination of the public water system, it shall be listed for fire protection service.

5.4.2.1*
Where a check valve or alarm check valve is permitted by the AHJ in lieu of a backflow preventer, it shall be listed for fire protection service.

5.5 Connections to Public Water Systems.

Connections to public water systems shall be arranged to be isolated by one of the methods permitted in 6.2.9.
6.2.9
All connections to private fire service mains for fire protection systems shall be arranged in accordance with one of the following so that they can be isolated:
(1)*
A post indicator valve installed not less than 40 ft (12 m) from the building
(a)
For buildings less than 40 ft (12 m) in height, a post indicator valve shall be permitted to be installed closer than 40 ft (12 m) but at least as far from the building as the height of the wall facing the post indicator valve.


(2)
A wall post indicator valve

(3)
An indicating valve in a pit, installed in accordance with Section 6.4

(4)*
A backflow preventer with at least one indicating valve not less than 40 ft (12 m) from the building
(a)
For buildings less than 40 ft (12 m) in height, a backflow preventer with at least one indicating valve shall be permitted to be installed closer than 40 ft (12 m) but at least as far from the building as the height of the wall facing the backflow preventer.


(5)*
A nonindicating valve, such as an underground gate valve with an approved roadway box, complete with T-wrench, located not less than 40 ft (12 m) from the building
(a)
For buildings less than 40 ft (12 m) in height, a nonindicating valve, such as an underground gate valve with an approved roadway box, complete with T-wrench, shall be permitted to be installed closer than 40 ft (12 m) but at least as far from the building as the height of the wall facing the non-indicating valve.


(6)
Control valves installed in a fire-rated room accessible from the exterior

(7)
Control valves in a fire-rated stair enclosure accessible from the exterior as permitted by the AHJ

Reply
Dan Wilder
8/21/2023 09:04:54 am

NFPA 24 - 22' Ed.

Section 7.3.6 specifically says not to install a backflow between the hydrant and the control valve for that hydrant, not sure where you are being asked to provide the valve in your situation.

On top of keeping it warm and free of mechanical damage, putting it in a pit that will flood makes maintenance difficult.

Reply
RYAN HINSON
8/21/2023 09:43:10 am

And will void the listing of the BFP in most cases.

Reply
Thomas G. Kamprath
8/21/2023 11:47:29 am

Typically, backflow protection is specified by the local jurisdiction Cross Connection Control Ordinance. If you can't find a Cross Connection Control Ordinance, check with the local water purveyor. They would know if there is an ordinance in effect.

Reply
Mike Slaughter
8/23/2023 11:47:06 am

We are a Fire Code AHJ. It appears the AHJ is requiring a backflow at the point where the private water service connects to the public service. For buildings, cross-connection contamination is required by the International Plumbing Code (See Section 608 of the 2021 IPC). Also required for any underground connected to the public service which contains more than 100 gallons.

Hope this helps.

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top Sept '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 221
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    October 2026
    September 2026
    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT