HDPE ISO 4427, PE100 SDR Allowed Without FM?

3/29/2023

7 Comments

 
Can HDPE ISO 4427, PE100 SDR 9 PE be used for underground water service pipe (dedicated for fire water), even though it carries no FM Approval?

​​​​​​​​​​​​​​​​​​​​​​Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
7 Comments
Pete H
3/29/2023 06:44:07 am

Not on an FM designed job. But if the job is to be designed to UL or NFPA 13 standards, then it matters if HDPE PE100 meets the requirements found in AWWA C906 (Polyethylene Pressure Pipe and Fittings 4 in. Through 63 in. for Water Distribution.)

Barring being able to find the HDPE PE100 in those standards: check the actual manufacturer's listing. "Piping specifically listed for use in private fire service mains shall be permitted to be used." (NFPA 13 2016 10.1.1.2 [24:10.1.12].)

Reply
Jesse
3/29/2023 08:10:20 am

The lack of an FM approval only means it can't be used on projects governed by FM, If the project is governed by NFPA 24 you're good to go

Reply
Alex
3/29/2023 08:13:15 am

As Jesse mentioned, if the project is not FM approved, you should be good to go. You will still need to confirm with all local amendments.

Reply
Glenn Berger
3/29/2023 08:19:40 am

As others have said, if the minimum compliance is NFPA 24 you are probably good to go. Be careful when using HDPE pressure pipe. The internal diameter is not the same as cement-lined ductile pipe or even PVC pipe.

Reply
Todd E Wyatt
3/29/2023 08:59:24 am

SUMMARY
If a piping material is “listed for use in private fire service mains” OR complies with the specified AWWA/ASTM standard, then it is permitted per NFPA 13 (& NFPA 24) to be used as an underground piping material supplying an automatic sprinkler system (ASPS).

EXPLANATION
The adopted Code (e.g. IBC) is the scoping source for the automatic sprinkler system (ASPS) requirements and its referenced standards (e.g. NFPA 13) identify the requirements for the ASPS’s design, installation, inspection, and maintenance ... including compliant underground piping materials supplying the ASPS. “NFPA 24 Standard for the Installation of Private Fire Service Mains and Their Appurtenances” is not an IBC “referenced standard” and it is not a “reference publication” in NFPA 13. NFPA 13 Chapter 6 Installation Underground Piping have the same requirements as NFPA 24 :
“... the wording in Chapter 6 of NFPA 13 is extracted directly from Chapter 10 of NFPA 24.”

HDPE is an acronym for “High Density Polyethylene”. Per NFPA 13 (2023), “HDPE” is not referenced but “HIGH DENSITY POLYENTHYLENE” is (6) times. These (6) references focus on the “Classification of Commodities” and not on underground piping.

NFPA 13 Chapter 6 Installation Underground Piping” “covers the requirements for underground piping, including piping materials ...”

Table 6.1.1.1 Manufacturing Standards for Underground Pipe includes “Plastic” category and includes “Polyethylene (PE) pressure pipe and fittings, 4 in. (100 mm) through 63 in. (1575 mm) for waterworks AWWA C906.”


REFERENCES
NFPA 13 (2023)

Chapter 6 Installation Underground Piping
ENHANCED CONTENT
Chapter 6 covers the requirements for underground piping, including piping materials, fittings, joining of pipe and fittings, depth of cover, protection against freezing, protection against damage, laying of pipe, joint restraint, backfilling, and testing and acceptance.
The use of private, underground piping leading from a municipal water supply or privately owned waterworks system is one of the most common methods of supply to automatic sprinkler systems. Exhibit 6.1 shows a municipal water supply (illustrated with black piping) connected to the private water supply piping (underground piping illustrated with red piping). The jurisdiction of NFPA 24, Standard for the Installation of Private Fire Service Mains and Their Appurtenances, begins at the connection to the municipal water supply piping and ends within 24 in. (600 mm) of the underground piping entering the building. All piping, valves, and system appurtenances located between these connection points fall under the jurisdiction of NFPA 24.

ENHANCED CONTENT - FAQ
Does 6.1.1 require that all piping utilized underground be listed for fire protection service?
Underground pipe must meet either of the following criteria:
1. Be listed for fire protection service
2. Comply with the American Water Works Association (AWWA) or ASTM International standards specified in Table 6.1.1.1

ENHANCED CONTENT
Are the underground requirements in NFPA 13 the same as in NFPA 24?
The wording in Chapter 6 of NFPA 13 is extracted directly from Chapter 10 of NFPA 24. As such, the two chapters are identical, including the text numbering (other than the chapter prefixes), the tables, and the figures. The inclusion of this material in NFPA 13 makes it easier for the reader to find the requirements for fire main piping supplying sprinkler systems, allows for better coordination between the two standards, and ensures uniformity in the requirements for underground piping serving water-based fire protection systems.

6.1.1*
All piping used in private fire service mains shall be in accordance with 6.1.1.1, 6.1.1.2, or 6.1.1.3. [24:10.1.1]
A.6.1.1
The type and class of pipe for a particular underground installation should be determined through consideration of the following factors:
1) Maximum system working pressure
2) Maximum pressure from pressure surges and anticipated frequency of surges
3) Depth at which the pipe is to be installed
4) Soil conditions
5) Corrosion
6) Susceptibility of pipe to external loads, including earth loads, installation beneath buildings, and traffic or vehicle loads
The following pipe design manuals and standards can be used as guides:
1) AWWA C150/A21.50, Thickness Design of Ductile-Iron Pipe
2) AWWA M23, PVC Pipe — Design and Installation
3) AWWA M55, PE Pipe — Design and Installation
4) AWWA M41, Ductile-Iron Pipe and Fittings
5) Concrete Pipe Handbook, American Concrete Pipe Association
6.1.1.1 Use.
Piping manufactured in accordance with Table 6.1.1.1 shall be permitted to be used. [24:10.1.1.1]
Table 6.1.1.1 Manufacturing Standards for Underground Pipe
Plastic
Polyethylene (PE) pressure pipe and fittings, 4 in. (100 mm) through 63 in. (1575 mm) for waterworks AWWA C906
6.1

Reply
Todd E Wyatt
3/29/2023 09:38:30 am

REFERENCES continued ...

6.1.1.2
Piping specifically listed for use in private fire service mains shall be permitted to be used. [24:10.1.1.2]
6.1.1.2.1
Where listed pipe is used, it shall be installed in accordance with the listing limitations including installation instructions. [24:10.1.1.2.1]
6.1.1.3
Steel piping manufactured in accordance with Table 6.1.1.3 that is externally coated and wrapped and internally galvanized shall be permitted to be used between the hose coupling(s) on the fire department connection and the check valve installed in the fire department connection piping. [24:10.1.1.3]

NFPA 13 (2023) : HDPE

20.3* Classification of Commodities.
20.3.2 Pallet Types.
20.3.2.4 Plastic Pallets Other Than Polypropylene or HIGH DENSITY POLYENTHYLENE.
...plastic pallets when other than wood, metal, or polypropylene or HIGH DENSITY POLYENTHYLENE plastic pallets are used, the classification of ...
20.3.2.4.1
...III commodities stored on plastic pallets other than polypropylene or HIGH DENSITY POLYENTHYLENE, the classification of the commodity unit ...
20.3.2.4.2
...IV commodities stored on plastic pallets other than polypropylene or HIGH DENSITY POLYENTHYLENE, the classification shall be increased to ...
20.3.2.2.1.1
...I through Class IV commodities, when unreinforced polypropylene or unreinforced HIGH DENSITY POLYENTHYLENE plastic pallets are used, the classification of ...
20.3.2.2.2.1*
...I through Class IV commodities, when reinforced polypropylene or reinforced HIGH DENSITY POLYENTHYLENE plastic pallets are used, the classification of ...
20.3.2.2.1.2
Unreinforced polypropylene or unreinforced HIGH DENSITY POLYENTHYLENE plastic pallets shall be marked with a permanent symbol to indicate that the pallet is unreinforced.

Reply
Dave
3/29/2023 08:52:48 pm

We have spec'd UL-listed HDPE pipe for a few sprinkler projects such as piers, where some physical flexibility, protection, and corrosion resistance is desired. Specs including material requirements and joining methods, but no FM requirement.
Found this:
https://thecodecoach.blogspot.com/2011/07/what-in-hdpe-is-going-on.html
https://blog.unitedpolysystems.com/blog/hdpe-for-fire-prevention

Reply



Leave a Reply.

    SUBMIT A QUESTION
    Picture
    Why Sponsor?

    ALL-ACCESS

    Picture
    GET ALL OUR TOOLS

    SUBSCRIBE

    Subscribe and learn something new each day:
    I'm Interested In:

    COMMUNITY

    Top July '26 Contributors
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    Picture
    SEE LEADERBOARD

    YOUR POST

    SUBMIT A QUESTION

    PE EXAM

    Get 100 Days of Free Sample Questions right to you!
    SIGN ME UP!

    FILTERS

    All
    A1171
    ABA
    ADA
    ASCE 7
    ASME A17.1
    ASTM E1354
    Blog Thread
    Daily Discussion
    Design-documents
    EN 12259-1
    EN 12845
    Explosion Protection
    Explosion-protection-prevention
    Fire Detection And Alarm Systems
    Fire Dynamics
    Flammable And Combustible Liquids
    Flammable-combustible-liquids
    FM Global
    Human-behavior
    IBC
    ICC 500
    IEBC
    IFC
    IMC
    IPC
    IRC
    ISO
    Means Of Egress
    NBC
    NFPA 1
    NFPA 10
    NFPA 101
    NFPA 11
    NFPA 110
    NFPA 1142
    NFPA 1221
    NFPA 13
    NFPA 13D
    NFPA 13R
    NFPA 14
    NFPA 15
    NFPA 16
    NFPA 17A
    NFPA 20
    NFPA 2001
    NFPA 214
    NFPA 22
    NFPA 220
    NFPA 24
    NFPA 241
    NFPA 25
    NFPA 291
    NFPA 30
    NFPA 307
    NFPA 30B
    NFPA 31
    NFPA 33
    NFPA 37
    NFPA 400
    NFPA 409
    Nfpa-415
    Nfpa-45
    Nfpa-495
    NFPA 497
    NFPA 5000
    NFPA 502
    NFPA 54
    NFPA 55
    NFPA 654
    NFPA 68
    NFPA 70
    NFPA 701
    NFPA 72
    NFPA 75
    NFPA 770
    NFPA 82
    NFPA 850
    NFPA 855
    NFPA 90A
    NFPA 92
    NFPA 96
    NICET
    OBC
    OSHA
    Passive Building Systems
    PE Prep Guide
    PE Prep Series
    PE Sample Problems
    Poll
    Smoke Management
    Special Hazard Systems
    UFC 3-600-01
    UFC 3-601-02
    UFC 4-021-01
    UFC 4-211-01
    UPC
    Updates
    Water Based Fire Suppression
    Weekly Exams


    ARCHIVES

    August 2026
    July 2026
    June 2026
    May 2026
    April 2026
    March 2026
    February 2026
    January 2026
    December 2025
    November 2025
    October 2025
    September 2025
    August 2025
    July 2025
    June 2025
    May 2025
    April 2025
    March 2025
    February 2025
    January 2025
    December 2024
    November 2024
    October 2024
    September 2024
    August 2024
    July 2024
    June 2024
    May 2024
    April 2024
    March 2024
    February 2024
    January 2024
    December 2023
    November 2023
    October 2023
    September 2023
    August 2023
    July 2023
    June 2023
    May 2023
    April 2023
    March 2023
    February 2023
    January 2023
    December 2022
    November 2022
    October 2022
    September 2022
    August 2022
    July 2022
    June 2022
    May 2022
    April 2022
    March 2022
    February 2022
    January 2022
    December 2021
    November 2021
    October 2021
    September 2021
    August 2021
    July 2021
    June 2021
    May 2021
    April 2021
    March 2021
    February 2021
    January 2021
    December 2020
    November 2020
    October 2020
    September 2020
    August 2020
    July 2020
    June 2020
    May 2020
    April 2020
    March 2020
    February 2020
    January 2020
    December 2019
    November 2019
    October 2019
    September 2019
    August 2019
    July 2019
    June 2019
    May 2019
    April 2019
    March 2019
    February 2019
    January 2019
    December 2018
    November 2018
    October 2018
    September 2018
    August 2018
    July 2018
    June 2018
    May 2018
    November 2017
    October 2017
    September 2017
    August 2017
    July 2017
    June 2017
    November 2016
    October 2016
    July 2016
    June 2016


    PE PREP SERIES

    SEE LEADERBOARD

    SEARCH THE FORUM

    RSS Feed

Picture
​Home
Our Cause
The Blog
The Forum
PE Exam Prep
The Toolkit

MeyerFire University
​Pricing
Login
​Support
Contact Us
Picture

MeyerFire.com is a startup community built to help fire protection professionals shine.
Our goal is to improve fire protection practices worldwide. We promote the industry by creating helpful tools and resources, and by bringing together industry professionals to share their expertise.

​MeyerFire, LLC is a NICET Recognized Training Provider and International Code Council Preferred Education Provider.

All text, images, and media ​Copyright © 2016-2025 MeyerFire, LLC

We respect your privacy and personal data. See our Privacy Policy and Terms of Service. 
The views, opinions, and information found on this site represent solely the author and do not represent the opinions of any other party, nor does the presented material assume responsibility for its use. Fire protection and life safety systems constitute a critical component for public health and safety and you should consult with a licensed professional for proper design and code adherence.

Discussions are solely for the purpose of peer review and the exchange of ideas. All comments are reviewed. Comments which do not contribute, are not relevant, are spam, or are disrespectful in nature may be removed. Information presented and opinions expressed should not be relied upon as a replacement for consulting services. Some (not all) outbound links on this website, such as Amazon links, are affiliate-based where we receive a small commission for orders placed elsewhere.

  • Blog
  • Forum
  • TOOLKIT
    • ALL TOOLS
    • BUY THE TOOLKIT
  • UNIVERSITY
    • ALL COURSES
    • JOIN THE UNIVERSITY
  • PE Exam
    • PE Forum & Errata
    • PE Store
    • PE Tools
    • PE PREP SERIES
    • PE Old Questions
  • STUDENTS
    • LAND JOB/INTERNSHIPS
    • STUDENT CONNECTOR
  • LOGIN
    • TOOLKIT-ONLY LOGIN
    • UNIVERSITY LOGIN
  • STORE
  • OUR CAUSE
    • ABOUT MEYERFIRE
    • JOB OPENINGS
    • BECOME AN INSTRUCTOR
    • HELP/SUPPORT