|
Is an alarm check valve required in a sprinkler system?
Is there an alternative to an alarm check valve? Are there any restrictions on where the alarm check valve is required to be (i.e., inside or outside of a fire pump room)? Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Pete H
7/16/2024 07:55:19 am
FROM:
Reply
Anthony
7/16/2024 08:11:59 am
An alarm check is required when there is no electrical waterflow detection and signaling. Basically in any system that would require a water motor gong due to lack of a building alarm system.
Reply
Jesse
7/16/2024 08:40:19 am
Great answers above. To add, its also not uncommon to see alarm check valves even when there is a riser monitoring panel also.
Reply
Casey Milhorn
7/16/2024 08:55:40 am
From a practical perspective, alarm valves are antiquated and used a lot less frequently than they used to be. The only purpose to use an alarm check valve over a "riser check valve" in my opinion, is for the ability to add a water motor gong, as others have said, the advantage of a water motor gong is that they don't require power to operate a local audible alarm.
Reply
Jon N
7/16/2024 10:31:13 am
In almost 40 years as an AHJ, I have never seen an alarm check valve installed on a new wet-pipe sprinkler system. I have seen several on older, existing wet-pipe systems to activate a water motor gong.
Reply
Mark Harris
7/16/2024 02:07:25 pm
Some great and valid comments but my opinion the backflow prevention requirements (which go back about 40 years) replaced the alarm valve as the system check valve.
Reply
Glenn Berger
7/16/2024 08:23:53 pm
The antiqued Alarm Check Valve!
Reply
Jack G
7/16/2024 10:18:47 pm
As indicated above it is used for a local alarm when electrical supervision is not available.
Reply
Pete D.
7/17/2024 12:05:54 pm
The alarm check equivalent with an electric bell is called a Riser Check Valve. You want some kind of check valve, because when flowing water on adjacent systems connected to the same supply (say during the inspection), without the check valve you can siphon water out of the system not flowed. Then when the adjacent system ceases to flow, your system fills back up and you can get a false alarm. The modern vane-type or paddle flow switches have 2 sets of normally open contacts. One gets wired into an addressable monitor module to signal the authorities when water flows on a system. The other can have voltage landed on it to activate an electric bell local to the riser on the exterior of wall. They come in 120 vac or 24 vdc varieties. Alternately, an existing Alarm check valve can have the alarm port to the water motor gong cut and capped, and an electric bell can be added to the system in the same was as one would install it for a riser check valve.
Reply
Leave a Reply. |
ALL-ACCESSSUBSCRIBESubscribe and learn something new each day:
COMMUNITYTop July '26 Contributors
YOUR POSTPE EXAMGet 100 Days of Free Sample Questions right to you!
FILTERS
All
ARCHIVES
September 2026
PE PREP SERIES |
RSS Feed
