We have a building with an Extra Hazard Group 1 in a fairly rural location. We have an Electric, Diesel and Jockey (electric) pump system.
We had our diesel go out, sent away for repairs. What are the requirements for just having just electric in place? My concern is is the fire department cuts power if they come on site for industrial fire, or lose power due to weather, then we would have no suppression in service. The fire department can provide 1,500 gpm at 100 psi from a Type 1 engine through the FDC, (so 750 gallons). We have a pond to draft from. What would be the considerations? Amount of water available? In the event of power loss, the size of the FDC versus the size of the riser (a 6-8" dry pipe valve)? What would realistic attack line demand be for a hydrant/hose line? Can you think of anything else I'm not thinking of? Thanks in advance for the help! Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
11 Comments
JI
2/23/2024 08:19:45 am
My first thought is a back up generator should be on site which is able to supply the fire pump for the NFPA required water demand. The generator sizing should be for the duration of the water supply at the horsepower requirements for the sprinkler system demand. Depending on the types of systems, there might be varying durations and sprinkler demands that would need to be compared to see what the generator sizing should be. There are many factors that go into generator selection such as fuels readily available in the area, but in some cases the cost of a generator is not prohibitive when compared to a diesel fire pump install. However some facilities already require a generator so it is not a big deal to add the extra demand of a fire pump.
Reply
Glenn Berger
2/23/2024 08:28:59 am
Just having a single electric fire pump is satisfactory per the codes IF you have reliable power and IF your client doesn't want back-up equipment.
Reply
Jack G
2/23/2024 08:31:40 am
Keep the diesel. Em generator would cost a couple hundred thousand.
Reply
Franck
2/23/2024 08:35:17 am
Another concern might come from the Insurance Company.
Reply
Anthony
2/23/2024 08:38:49 am
Fire pump back up is one of the more difficult parts of the job for 'sprinkler guys' like me. The easiest options are always diesel back up or a generator with automatic transfer switch. The back up power or source of water only comes into play in section 9.3 where the fire department can't supply the required water to tall buildings.
Reply
Greg
2/23/2024 08:46:21 am
Good question. I've recently evaluated the same choice for diesel fire pump keep, or remove.
Reply
Jesse
2/23/2024 09:01:31 am
The electric pump is sufficient presuming the electric utility is reliable.
Reply
Kimberly Olivas
2/23/2024 09:47:10 am
By Code, electric fire pumps can only be used exclusively if the AHJ has deemed the power supply to be reliable enough. You cannot set your electric fire pump up with any shut off switches before the controller either. It has its own feed. If the fire pumps were the electric and a diesel pump back-up, then it could be possible to get rid of the diesel. But that's up to the AHJ, I would think. I am just talking off the cuff; I was excited to see a question I might be able to help answer. :)
Reply
Dan Wilder
2/23/2024 12:02:17 pm
As with everyone else, Reliable power as determined by the AHJ/Insurance. If the pump is on site backup gens and has the appropriate switches/panels to make that transition
Reply
Pete
2/23/2024 03:13:06 pm
Someone please sell me a diesel jockey pump. The reason is with all my 2-pump electric/diesel installations, when there's a site-wide power outage, the diesel doesn't function as a back-up pump. The electric jockey pump always fails with the power outage, same as the electric fire pump. The diesel pump comes on due to normal system pressure drops over a couple hours without a jockey pump. Then a tech gets a call from the central station and must respond to shut the diesel pump off. The set-up is hardly a substitution for reliable power.
Reply
sean
2/26/2024 01:24:40 pm
I think your biggest issue is right now the original design included both pumps. The code requires to maintain the system and equipment as first designed.