Can a flow meter be installed in test header piping?
This is the first time I've ever seen this installation. Thanks. Sent in anonymously for discussion. Click Title to View | Submit Your Question | Subscribe
9 Comments
Dan Wilder
2/21/2024 07:02:01 am
Is it against NFPA, no, however it defeats the purpose of having one to avoid flowing water annually if it only feeds to the test header. It "could" be used to just flow from the test header without the use of any pitot readings however they still need to be calibrated so it's not a 100% resolution and an expensive alternate with no real added value (IMO).
Reply
Jesse
2/21/2024 10:36:49 am
Yep it can indeed. Just think of it a really expensive pitot tube in that arrangement though.
Reply
WES
2/21/2024 10:44:07 am
While it seems like a logical idea - we've been told from the flowmeter manufacturer themselves (the #1 brand) that a flowmeter will NOT accurately read when flow happens out through the test header.
Reply
Franck
2/21/2024 11:46:53 am
Looks pretty strange to me.
Reply
Thomas Duross
9/8/2024 03:35:40 pm
Whenever I've been involved in installing, replacing or repiping, I've always advocated for a flowmeter. FM is 5 diameters (min) after the test valve (between pump check and discharge valve) but I valve it 2 ways. 1 to the header and 1 back to suction. This way I always flow through the meter to check, even though it has to be calibrated yearly and be within 1%. Closed loop FM numbers are good, but open loop FM goes awry. I'm told due to backpressure or the lack thereof. I really learned my lesson this year as I installed the digital version along with a new FPC/TS with the modbus communication to read suction, system and flow, and plot a curve on the FPC screen. Things are still a mess.
Reply
Glenn Berger
2/21/2024 11:46:59 am
I have been asked by clients to include the flow meter, whether the flow goes to exterior hose valves, back to a storage tank, or a return to suction side of fire pump with no objections except by contractors that failed to follow the design documents.
Reply
Jack G
2/21/2024 11:55:30 am
Basically the above is correct. I disagree with putting 2 hose valves in a valve room and running the hoses to the exterior. Hoses burst or leak.
Reply
Mark Harris
2/21/2024 04:04:01 pm
Some great comments about being expensive pitot. But as Glenn notes routing to a ground suction storage tank is common and saves water verses hose valve test. But sounds like Wes has documentation that is not right with the flow test meter manufacturer?
Reply
Megan Asbrock
3/21/2024 06:50:37 pm
sure can. the meter and pipng arrangement can be found in NFPA 20.